can I plug orofice for vent on backflow preventer?

Hi folks,

I was going to sweat in a backflow preventer for my boiler system just after the shutoff (that is, closer to the boiler than the shutoff). This would put the preventer upstream of the auto-filler, the vent, and the pressure relief valve.

My question is whether I can just get a plug for the hole on the backflow preventer that's apparently for mounting a vent since I already have one installed a little closer to the boiler?

Thanks!
 
  #2  
Old 08-25-09, 06:41 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
No. That is NOT a vent but an integral part of the backflow prevention device. What you can do is pipe that opening to a floor drain or at least to no closer than six inches off the floor.
 
  #3  
Old 08-25-09, 07:50 PM
R
Member
Thread Starter
Join Date: Dec 2004
Posts: 89
Upvotes: 0
Received 0 Upvotes on 0 Posts
okay. Thanks a bunch, Furd!Beer 4U2
 
 