What does it all mean?

What do all the ratings mean on my boiler? The net I-B-R, the DOE, and the Input rating? So far I have been told the DOE is what you match to your heat loss. The input, I assume, would be the amount of energy in gas it consumes to get he output. So what would the I-B-R be used for?
 
  #2  
Old 09-04-09, 08:36 AM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,394
Upvotes: 0
Received 61 Upvotes on 51 Posts
You are right the Input is the amount of fuel inputthe boiler is certified for.
The DOE (Department of Energy) is a combustion test, a specific gas at a determined temperature is passed through the boiler and the exit temperature is obtained. After some other data is gathered it is applied to a formula and determined what the standby losses are, chimney, jacket etc. The net output is just a standard formula for piping losses. The Net output normally is higher than the formula results.
 
  #3  
Old 09-04-09, 08:52 AM
D
Member
Thread Starter
Join Date: Aug 2009
Location: USA
Posts: 4,345
Upvotes: 0
Received 1 Upvote on 1 Post
When you say "net ouput" do you mean net I-B-R? I'm still not sure how I would use that number. Should I just not be concerned with it for what I am doing?

My current boiler is:

Input - 164,000
DOE - 135,000
Net I-B-R - 117400
 
  #4  
Old 09-04-09, 08:55 AM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,394
Upvotes: 0
Received 61 Upvotes on 51 Posts
The only number you need to be concerned with is the DOE. This is what needs to match the heat loss. Net output and IBR are the same.
 
  #5  
Old 09-04-09, 09:30 AM
O
Member
Join Date: Dec 2007
Location: A Galaxy From Afar
Posts: 337
Upvotes: 0
Received 0 Upvotes on 0 Posts
With the Buderus boilers there is a:

"Heating capacity (gross output)"

and a

"Thermal output (net IBR output)" listed.

Would the "Heating capacity (gross output)" be the equivalent to the DOE rating? I too thought that DOE should be used to match against heat loss, but was surprised to see that it wasn't listed as such on the Buderus. Which is why I mentioned IBR on the heat loss thread.

The Burnham MPO I&O lists both IBR and DOE.

Al.
 
  #6  
Old 09-04-09, 01:31 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,394
Upvotes: 0
Received 61 Upvotes on 51 Posts
Gross output and DOE is the same rating. Years ago everybody had the gross output but I thought everyone switched to DOE now. Just not the Germans I guess.
 
 