What does it all mean?
#1
What does it all mean?
What do all the ratings mean on my boiler? The net I-B-R, the DOE, and the Input rating? So far I have been told the DOE is what you match to your heat loss. The input, I assume, would be the amount of energy in gas it consumes to get he output. So what would the I-B-R be used for?
#2
You are right the Input is the amount of fuel inputthe boiler is certified for.
The DOE (Department of Energy) is a combustion test, a specific gas at a determined temperature is passed through the boiler and the exit temperature is obtained. After some other data is gathered it is applied to a formula and determined what the standby losses are, chimney, jacket etc. The net output is just a standard formula for piping losses. The Net output normally is higher than the formula results.
The DOE (Department of Energy) is a combustion test, a specific gas at a determined temperature is passed through the boiler and the exit temperature is obtained. After some other data is gathered it is applied to a formula and determined what the standby losses are, chimney, jacket etc. The net output is just a standard formula for piping losses. The Net output normally is higher than the formula results.
#3
When you say "net ouput" do you mean net I-B-R? I'm still not sure how I would use that number. Should I just not be concerned with it for what I am doing?
My current boiler is:
Input - 164,000
DOE - 135,000
Net I-B-R - 117400
My current boiler is:
Input - 164,000
DOE - 135,000
Net I-B-R - 117400
#5
Member
Join Date: Dec 2007
Location: A Galaxy From Afar
Posts: 337
Upvotes: 0
Received 0 Upvotes
on
0 Posts
With the Buderus boilers there is a:
"Heating capacity (gross output)"
and a
"Thermal output (net IBR output)" listed.
Would the "Heating capacity (gross output)" be the equivalent to the DOE rating? I too thought that DOE should be used to match against heat loss, but was surprised to see that it wasn't listed as such on the Buderus. Which is why I mentioned IBR on the heat loss thread.
The Burnham MPO I&O lists both IBR and DOE.
Al.
"Heating capacity (gross output)"
and a
"Thermal output (net IBR output)" listed.
Would the "Heating capacity (gross output)" be the equivalent to the DOE rating? I too thought that DOE should be used to match against heat loss, but was surprised to see that it wasn't listed as such on the Buderus. Which is why I mentioned IBR on the heat loss thread.
The Burnham MPO I&O lists both IBR and DOE.
Al.