Gas control valve issue???
#1
Member
Thread Starter
Join Date: Oct 2009
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Gas control valve issue???
Can anyone help. My peerless gas furnace started out with a failed transformer. After replacing the L8148E aquastat, the relay for the pump chatters alot. I shut it down and have chacked all components in the loop. I have a pilot and I have 24 V to the gas valve and the system runs OK with the gas control disconnected for the aquastat but as soon as I hook up the gas control vale, the relay chaters and the transformer is in overload. How do I tell if the gas control valve is bad (model V8200A)
PS, no resistance across gas control terminals.
PS, no resistance across gas control terminals.
#2
When you say "no resistance", do you mean that the meter reads ZERO OHMS ? as in SHORT CIRCUIT?
In other words, if it's a digital meter, it reads 00.00 and not OL ?
or if analog meter, it swings all the way to the right ?
That valve should only draw around 300 milliamps, so that would put the resistance around 80 ohms or so if it was good.
In other words, if it's a digital meter, it reads 00.00 and not OL ?
or if analog meter, it swings all the way to the right ?
That valve should only draw around 300 milliamps, so that would put the resistance around 80 ohms or so if it was good.
#3
Member
Thread Starter
Join Date: Oct 2009
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Gas control
Thanks. The old control valve was a dead short, 0 ohms. The new one was ~500 and works great. This must be what cooked the transformer in the aquastat.