I have an oil boiler with a Honeywell 8182 Aquastat. I want to add 3 Honeywell 8043E Zone Valves. How do I connect the wires? Do I need a transformer or the 8182 Aquastat by itself is good enough. There are 2 yellow wires and 2 red wires coming from each Zone Valves.
Old 10-15-09, 04:44 PM
Grady's Avatar
Received 35 Votes on 33 Posts
Wiring
There should be a wiring diagaram with each valve but in case there is not, here's a link: http://customer.honeywell.com/techli.../95C-10932.pdf
Old 10-15-09, 04:50 PM
NJT's Avatar
NJT
NJT is offline
Received 4 Votes on 3 Posts
Yes, you need a transformer.
See figure 9 in this PDF file. Note that there is a typo in this file and the captions for figures 9 and 10 are reversed, but 9 is the one you want.
http://customer.honeywell.com/techli...it/69-0599.pdf
Old 10-15-09, 04:57 PM
C
Thanks a lot Grady. I'll take a look. Can I get by with just the Aquastat or I need a transformer or relay? 3 Zone Valves.
Old 10-15-09, 05:43 PM
C
Thanks NJ Trooper. I guess I do need a relay. R845?
Old 10-15-09, 06:01 PM
NJT's Avatar
NJT
NJT is offline
No, you do not need a relay, you need a transformer.
See figure 9 in the PDF I posted.
And, in the PDF that Grady posted, figure 10.
Old 10-15-09, 06:19 PM
C
Once again, thanks. I think I'll be able to do it now. Having to use a transformer was my main concern.