24 volt transformer question
Old 10-29-09, 09:57 PM
K
I'm hooking up a taco zone valve and in the diagram in the directions it says L1(hot) then L2. I purchased a honeywell transformer and it is labeled C and R,which side is the hot or doesn't it matter when hooking up the valve. I was wondering if it will affect the valve from working because the #2 terminal says it needs to be hooked to the common.
Thanx
Kevin @
Last edited by NJT; 10-30-09 at 09:48 AM. Reason: please, no email addresses in public forum, thanks.
Old 10-30-09, 09:53 AM
NJT's Avatar
NJT
NJT is offline
Received 8 Upvotes on 6 Posts
Kevin, the L1 and L2 are the PRIMARY (120 VAC) side of the transformer. The C and R should be on the low voltage side.
Reality is that it doesn't much matter which 'polarity' you use, because it's A.C. which technically doesn't have a polarity. (of course it does have polarity, but it's changing 60 times a second! )
The only time it might matter is if you had a complicated whizz bang wiring scheme with multiple transformers, etc... then you would need to be careful of the transformer 'phasing'...
If you wanted to follow the 'convention', use the C as your 24VAC 'common' and the R as your 24 VAC 'hot', and generally the RED wire is the hot ... your other wire might be white... or some other color, depending on the thermostat wire you use.