Water pressure dropping to 0 in matter of hours
#1
Member
Thread Starter
Join Date: Nov 2009
Location: Ireland
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts

PLEASE CAN SOMEONE HELP ME ON THIS:
Been having so much hassle with my boiler lately - a Vokera mynute 13 e.
Firstly after bein on for bout 40 mins it wud cut out and NOT Re-ignite (ie.the red pilot light wud come on and i had to physicall restart it. So i decided after asking 2 plumbers that could not solve the prob, i went to Vokera themselves.
Straight away they fixed the prob (he told me all he had to do was top up the GAS PRESSURE. so obviously i was delighted but unfortunately from that day on i'v been having another prob - the water pressure on boiler drops rapidly (i'm having to top up the pressure twice a day as it goes to absolute 0 therefor not a kick out of the boiler)
I got the guy back from voker and he changed some part on the boiler (he said basically if im still loosing pressure to get a plumber as he replaced the only part on the boiler that cud leak) anyway this goin on few weeks now with me toppin up every day but just yesterday i noticed in my spare room the radiator stone cold even the 2 pipes leading to the radiator are stone cold. can anyone help is this all related?
Vokera were very expensive so i cant really afford to go n spend a fortune again
please - any advice wud be appreciated.
ps. there is no obvious leaks anywhere in the house

Been having so much hassle with my boiler lately - a Vokera mynute 13 e.
Firstly after bein on for bout 40 mins it wud cut out and NOT Re-ignite (ie.the red pilot light wud come on and i had to physicall restart it. So i decided after asking 2 plumbers that could not solve the prob, i went to Vokera themselves.
Straight away they fixed the prob (he told me all he had to do was top up the GAS PRESSURE. so obviously i was delighted but unfortunately from that day on i'v been having another prob - the water pressure on boiler drops rapidly (i'm having to top up the pressure twice a day as it goes to absolute 0 therefor not a kick out of the boiler)
I got the guy back from voker and he changed some part on the boiler (he said basically if im still loosing pressure to get a plumber as he replaced the only part on the boiler that cud leak) anyway this goin on few weeks now with me toppin up every day but just yesterday i noticed in my spare room the radiator stone cold even the 2 pipes leading to the radiator are stone cold. can anyone help is this all related?
Vokera were very expensive so i cant really afford to go n spend a fortune again
please - any advice wud be appreciated.
ps. there is no obvious leaks anywhere in the house



#2
I'm not sure you will find anyone here that knows anything about your boiler... it's an unknown brand here for most part... nearly all of us here are in the USA...
If the pressure in the boiler is going to zero, then I think there must be a leak, even if you can't see it... where else would the pressure go? Any pipes under the house that you can't see?
If the pressure in the boiler is going to zero, then I think there must be a leak, even if you can't see it... where else would the pressure go? Any pipes under the house that you can't see?
#3
Member
Thread Starter
Join Date: Nov 2009
Location: Ireland
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts

Thanks a lot for your quick reply. yes im sure there is some pipes under the ground that i cant see!!! the only thing is i just thought it a coincidence that the minute i get one problem fixed another problem arises. Do you know why one radiator in my house is not working n all the others are. even the 2 pipes leading to the radiator stone cold. Also someone told me to bleed all the radiators as there may be air in the system causing the pressure to drop. last question, is there any other way of fixing leaks without tearing my house up?
Thanks again for your help
Thanks again for your help
#4
If one radiator is cold, the problem is most likely that there is air in those pipes blocking the flow of water. This is where I would start to look for a leak...
But air in the system will not cause the pressure to drop like that.
I have heard of some fellows using air pressure on the system to find leaks. I think what they do is let all the water out and then pressurize the pipes with air and go around and LISTEN and see if they can hear the air coming out. I can't say if it works or not, and I have only heard this story one time...
Can you get under the house and see the pipes? Or are they out of view in the walls and floor? and you said 'under the ground'... are some pipes buried?
But air in the system will not cause the pressure to drop like that.
I have heard of some fellows using air pressure on the system to find leaks. I think what they do is let all the water out and then pressurize the pipes with air and go around and LISTEN and see if they can hear the air coming out. I can't say if it works or not, and I have only heard this story one time...
Can you get under the house and see the pipes? Or are they out of view in the walls and floor? and you said 'under the ground'... are some pipes buried?
#5
Member
Thread Starter
Join Date: Nov 2009
Location: Ireland
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
thanks again , no unfortunately, i cannot get under house n yea pipes in floor etc out of view!! i might get someone to look around this cold radiator, i did feel the connections around it and there is tiny drips (very tiny) when i rub its a bit wet! so maybe this is close to my problem.
Also did i mention, lets say the water pressure is at even 0.1 and i turn on the heating, it will within a few minutes be up at 2) - does this have any significance
god i wish i knew bout plumbing lol
thanks again
Also did i mention, lets say the water pressure is at even 0.1 and i turn on the heating, it will within a few minutes be up at 2) - does this have any significance
god i wish i knew bout plumbing lol
thanks again

#6
Member
Join Date: Oct 2008
Location: South Dakota
Posts: 327
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Well, the fact that you gain pressure when the boiler runs is normal. Water gets hot, then expands, therefore creating more pressure. How old is this boiler unit? I did a little research on this brand of boiler, and the pressure is measured in bar???? According to the research that I found, it states that "normal opereating pressure" would be anywhere between 0.5 and 1.5. Again, it should be at lower pressure when cold. Finally, these units look pretty nice, and not to mention they look like they could be quite expensive!
Last edited by cheinemann; 11-07-09 at 08:57 AM.
#7
Member
Thread Starter
Join Date: Nov 2009
Location: Ireland
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
my boiler is approx 9 yrs old! And yes they are pretty expensive (about 1300 euro)
Can you please tell me this, i noticed one of my radiators - the fitting that joins the top part of the radiator is leaking, now its not really bad, just tiny drips really, do u think this would cause the pressure on my boiler to drop. (mine can drop to zero in matter of 3 hours somettime!!!!! this pressure drop is driving me mad especially when there is no obvious leaks except for this little leak on one of my radiators.
thanks again
Can you please tell me this, i noticed one of my radiators - the fitting that joins the top part of the radiator is leaking, now its not really bad, just tiny drips really, do u think this would cause the pressure on my boiler to drop. (mine can drop to zero in matter of 3 hours somettime!!!!! this pressure drop is driving me mad especially when there is no obvious leaks except for this little leak on one of my radiators.
thanks again

#8
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
A large change in pressure is indicative of too little expansion room in the expansion tank. If you have a non-diaphragm expansion tank then it is probably waterlogged. If you have a diaphragm type expansion tank it has either lost its air cushion or the diaphragm is damaged. In either case a small leak may be all it takes to reduce the pressure to zero in a few hours.
#9
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If the gauge reads in bar, then 2 = 29 psig. More evidence that your expansion tank has lost its cushion.
#10
I didn't find the exact model, but the manual for the 14e says that the relief valve is set up for THREE bar, which is almost 45 PSI I think... TWO bar might not be abnormal...
OK, read some more of the manual... your "Expansion Vessel" is to be precharged to 0.8 Bar, and the normal operating pressure should be 1.5 bar.
It does sound as though your expansion vessel has lost it's precharge. Looking at the manual, it seems that it is very difficult to get to, and that you may even have to remove the boiler from the wall in order to do so. They even suggest in the manual that since it is such a difficult job, instead of replacing the one that's in the boiler, to mount a separate one externally.
It is very possible that if your expansion tank has developed a problem it is the reason that you are losing water. It would be going down a drain from the pressure relief valve though, and not actually 'leaking' somewhere.
Even small leaks need to be fixed, whether or not they are the cause of the problem you are currently having. A constant influx of fresh water can cause mineral buildup and clog the heat exchanger passages, etc...
OK, read some more of the manual... your "Expansion Vessel" is to be precharged to 0.8 Bar, and the normal operating pressure should be 1.5 bar.
It does sound as though your expansion vessel has lost it's precharge. Looking at the manual, it seems that it is very difficult to get to, and that you may even have to remove the boiler from the wall in order to do so. They even suggest in the manual that since it is such a difficult job, instead of replacing the one that's in the boiler, to mount a separate one externally.
It is very possible that if your expansion tank has developed a problem it is the reason that you are losing water. It would be going down a drain from the pressure relief valve though, and not actually 'leaking' somewhere.
Even small leaks need to be fixed, whether or not they are the cause of the problem you are currently having. A constant influx of fresh water can cause mineral buildup and clog the heat exchanger passages, etc...
Last edited by NJT; 11-09-09 at 04:48 PM.
#11
Member
Join Date: Oct 2008
Location: South Dakota
Posts: 327
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Even small leaks need to be fixed, whether or not they are the cause of the problem you are currently having. A constant influx of fresh water can cause mineral buildup and clog the heat exchanger passages, etc...
#12
Member
Thread Starter
Join Date: Nov 2009
Location: Ireland
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts

Just an update on the above,
i had few people check the boiler, and also pulled up some floorboards and no sign of any leak, also the pressure relief valve outside shows no signs of any leaks either.
Anyway recently, while redecorating spare bedroom i had to remove the radiator (which i am goin to replace with a new one) anyway we accidently bent the pipe when removing therefore caused a small leak, so we had to drain whole system, cut pipe n put a stop valve on it.
anyway since then my pressure is no longer dropping to 0 overnight, it does still drop a bit but not to 0 (in fact i have not had to top up at all in the last week whereas i was doing it daily.
can anyone explain this.
i will be adding the new radiator next week and am afraid now that it will change again and drop to 0 every night.
any feedback would be grately appreciated -
i had few people check the boiler, and also pulled up some floorboards and no sign of any leak, also the pressure relief valve outside shows no signs of any leaks either.
Anyway recently, while redecorating spare bedroom i had to remove the radiator (which i am goin to replace with a new one) anyway we accidently bent the pipe when removing therefore caused a small leak, so we had to drain whole system, cut pipe n put a stop valve on it.
anyway since then my pressure is no longer dropping to 0 overnight, it does still drop a bit but not to 0 (in fact i have not had to top up at all in the last week whereas i was doing it daily.
can anyone explain this.
i will be adding the new radiator next week and am afraid now that it will change again and drop to 0 every night.
any feedback would be grately appreciated -
#13
It seemed the concensus here was that your problem was with your expansion vessel... it's been three months... has anyone checked it?
We also warned against a constant addition of fresh water being bad for the system...
I don't think you should have 'dropped the ball' three months ago.
We also warned against a constant addition of fresh water being bad for the system...
I don't think you should have 'dropped the ball' three months ago.