wiring zone valves and taco sr501

Hi, I have added a third zone off of my current boiler. The third zone is radiant in my basement. I added a third zone valve (Honeywell V8043) and taco 501 controller with second circulator. zone valaves all work fine, but trouble with the 501 either always being on or not working even with 24 volts there. I have posted the diagrams here:

http://66.132.176.32/index2.html

Help please!!
 
  #2  
Old 11-16-09, 04:09 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,394
Upvotes: 0
Received 61 Upvotes on 51 Posts
The thermostat would be wired as normal but the zone valve end switch should be wired to the SR501 terminals R&W and not daisy chained to the other zone valves. The way you are showing it the SR501 has a 24v power supply and you are attached into the 24V side of the other transformer twice. All else stays the same.
See revised drawing
Radiant wiring picture by rbeck1953 - Photobucket
 

Last edited by rbeck; 11-16-09 at 04:29 PM.
  #3  
Old 11-16-09, 04:45 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
For the 'visual thinkers' among us, this is what rbeck is describing:



Sequence of operation:

T'stat opens zone valve, when valve opens, endswitch operates and triggers 501 to turn on pump and fire boiler.
 
  #4  
Old 11-17-09, 03:54 AM
K
Member
Thread Starter
Join Date: Nov 2006
Location: mass
Posts: 17
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you

Thanks folks! I really appreciate it!
 
 