heat starts,works awhile, then stops

3 valve system

The valve calls, boilier starts, water flows.

Before reaching the temperature set the heat is turning off

I then shut off the electricity, turn the thermostats off. restart and everything is fine again.
 
  #2  
Old 11-29-09, 09:26 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
More info...

We need to know something about the boiler... make/model/fuel?
 
  #3  
Old 11-29-09, 04:46 PM
G
New Member
Thread Starter
Join Date: Mar 2002
Location: nj
Posts: 43
Received 0 Votes on 0 Posts
model

pennco

model 1505

natural gas


About a month ago one valve was not working so I disconnected the wires and fiddled with the manual valve and since then it has worked but now the start and stopping has begun
 
  #4  
Old 12-01-09, 07:05 PM
G
New Member
Thread Starter
Join Date: Mar 2002
Location: nj
Posts: 43
Received 0 Votes on 0 Posts
electrical housing

I literally touched the cover of the honeywell electrical housing (model l8148g 10301 2a therm) and everything has worked fine for 2 days.


If problems continue would replacing the electrical housing fix the problem
 
  #5  
Old 12-02-09, 02:26 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
I was going to suggest that perhaps one of your safety controls was cutting off the burner... most gas boilers have one,two,three of them... depending on the age of yours, you may not have these safeties... but,

It seems that you have accidentally narrowed down the problem area. There are solder connections inside the control boxes, and it sounds as though one or more of the solder connections has given up...

If you are handy with a soldering iron, you might be able to repair... if not, then most likely a new control will do the trick for ya.

Your model is obsolete, this is the FUNCTIONAL replacement for it.

L8148J1009
 
 