Boiler not firing, problem with pilot relight control


  #1  
Old 12-16-09, 06:49 PM
HandyMark's Avatar
Member
Thread Starter
Join Date: Dec 2009
Location: New York City
Posts: 4
Received 0 Votes on 0 Posts
Arrow Boiler not firing, problem with pilot relight control

I have 23 years old steam boiler Weil-McLain EG-45.
From time to time boiler is not starting.
The spark from relight is weak and slow
My boiler has installed Pilot Relight Control made by White-Rodgers 5051-21. I consider to change it to Pilot Relight Control by White Rodgers 5059-23, but I am not so sure, that these models, are compatible I was trying to search the answer on White-Rodgers www., but I can't even find my old model 5059-21 to find cross refference to newer one, and as for bad, there is no number to call technical support. Only option is to write letter to them
Anyone can help
 

Last edited by HandyMark; 12-16-09 at 07:16 PM.
  #2  
Old 12-17-09, 01:35 PM
F
Member
Join Date: Dec 2008
Location: Virginia
Posts: 80
Received 0 Votes on 0 Posts
I have the same 5059-21 relite control on my Hytech Boiler. I went on the web and found information about them. The new model number is 5059-23. Hope this helps.
 
  #3  
Old 12-17-09, 04:01 PM
HandyMark's Avatar
Member
Thread Starter
Join Date: Dec 2009
Location: New York City
Posts: 4
Received 0 Votes on 0 Posts
Arrow White-Rodgers 5051-21 to White-Rodgers 5059-23 ???

My question should be: Can I change White-Rodgers Pilot Relight Control 5051-21 to 5059-23 ? I am sorry for mistake in my question from previous post
Model 5051-21 is so old, that I couldn't even find it on White-Rodgers web page site
 
  #4  
Old 12-17-09, 04:41 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
Mark, does your existing 5051 control resemble the 5059? Does it have one high voltage connection, a ground, and the 24VAC connections? If so, the 5059 will 'probably' work.

Before you change the control... check all the GROUND CONNECTIONS that they are clean, rust-free, and tight! These controls require a SOLID GROUND!

I found a tel number that you can try for White Rodgers:

314-577-1300

Maybe they can help you?
 
  #5  
Old 12-17-09, 06:27 PM
F
Member
Join Date: Dec 2008
Location: Virginia
Posts: 80
Received 0 Votes on 0 Posts
Sorry, I had your model and my model numbers mixed up. I hope that you get your questions answered.
 
  #6  
Old 12-18-09, 09:54 AM
HandyMark's Avatar
Member
Thread Starter
Join Date: Dec 2009
Location: New York City
Posts: 4
Received 0 Votes on 0 Posts
Thumbs up White-Rodgers Pilot Relight Control 5059-23

Thank you Moderator NJ Trooper. I called White-Rodgers division of Emerson and spoke to technician. REPLACEMENT should be: Pilot Relight Control by White-Rodgers 5059-23. Once again big thanx for your help and soon I will post another question about boilersBeer 4U2
 
 