HydroStat 3150 LWCO Not Active
I installed a WGO-3 that has the 3150 controller. The LWCO showed active and was working as advertised after I fired up the boiler, but this morning I checked it and it no longer shows active. Boiler is operating fine and other aspects of the controller seem to work properly.
I played with the probe a little and recycled the power on it... no joy. Haven't called the manufacturer yet, but was wondering if anyone else has seen this happen on a new 3150 or even an older one and what the cause turned out to be. Not really much to the thing other than the board and probe.
I played with the probe a little and recycled the power on it... no joy. Haven't called the manufacturer yet, but was wondering if anyone else has seen this happen on a new 3150 or even an older one and what the cause turned out to be. Not really much to the thing other than the board and probe.
#2
Member
Thread Starter
Join Date: Sep 2009
Location: US
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Apparently the mystery is solved. According to the manufacturer this is a normal condition based on conductivity of the water, or lack thereof. They recommended pulling the probe completely out to see if the LW LED illuminates, which it does. So, they say the LWCO is operational, but I may or may not see the Active light come on depending on the water conductivity.