Valve on radiator shut off then probelm with heating
#1
Member
Thread Starter
Join Date: Jan 2010
Location: PA
Posts: 33
Upvotes: 0
Received 0 Upvotes
on
0 Posts

Hello Gentleman,
If someone can please explain what is going on. My wife closed the valve of one of the radiators on the second floor of my house and we started having problems with the heat in one of the upstairs room. It's a hot water system that has no bypass and it has a steel compression tank and nothing to get the air out of the system automatically. The pressure at the boiler when I first checked was approximately 17 PSI. The first thing that came to mind was bleeding the air out of the system. I started at the 2nd floor radiators and worked my way down to the 1st floor. The room that was not heating had a lot of air in the radiator. I added more water to the boiler and continued to bleed the radiators. The pressure went down as I bled the radiators and I continued to supply water to the boiler until I got all the air out and got approximately 17 PSI @ the boiler again. I know the compression tank has some water in it, but when the water expands as it gets hotter it needs somewhere to go, but why did so much air get into the system and why was it fine before? Is it possible that I had the air in the system before and never noticed it until the valve was shut off?
Thanks in advance
If someone can please explain what is going on. My wife closed the valve of one of the radiators on the second floor of my house and we started having problems with the heat in one of the upstairs room. It's a hot water system that has no bypass and it has a steel compression tank and nothing to get the air out of the system automatically. The pressure at the boiler when I first checked was approximately 17 PSI. The first thing that came to mind was bleeding the air out of the system. I started at the 2nd floor radiators and worked my way down to the 1st floor. The room that was not heating had a lot of air in the radiator. I added more water to the boiler and continued to bleed the radiators. The pressure went down as I bled the radiators and I continued to supply water to the boiler until I got all the air out and got approximately 17 PSI @ the boiler again. I know the compression tank has some water in it, but when the water expands as it gets hotter it needs somewhere to go, but why did so much air get into the system and why was it fine before? Is it possible that I had the air in the system before and never noticed it until the valve was shut off?
Thanks in advance
#3
Not without asking more questions...
Did you try opening the valve on the radiator again?
How is the system piped? Monoflo? Series? Home runs?
My only thought as to what happened is that perhaps when the radiator valve was closed, the velocity increased in that pipe run enough to push a small bubble down the line where it met up with another small bubble and formed a big bubble.
When you say radiators, what do you mean?
Did you try opening the valve on the radiator again?
How is the system piped? Monoflo? Series? Home runs?
My only thought as to what happened is that perhaps when the radiator valve was closed, the velocity increased in that pipe run enough to push a small bubble down the line where it met up with another small bubble and formed a big bubble.
When you say radiators, what do you mean?
#4
Member
Thread Starter
Join Date: Jan 2010
Location: PA
Posts: 33
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Fair enough.
Yes, I opened the valve again and I still had the problem with the one room not warming up. I proceeded to the check the boiler and it had about 10psi @ 140 deg. I proceeded to bleed the system, beginning at the 2nd floor radiators. There was a lot of air in the 2nd floor radiators. I purged the air and supplied more water to the system. I had to do this a couple of times before I got all the air out. After all the air was out I was getting around 17psi @ 140 deg.
When I say radiator I mean cast iron radiators. Think they are in series.
I have been getting a little less heat at the room I had no heat before, but it's a big difference from the 68 deg. I was getting 73 before, now it's from 71-72. That's with the thermostat set to 69 and it's in the first floor. We can't set it back because we have a 6 month old, my wife is always cold and the room sits over a garage with no insulation in the garage ceiling.
The system takes forever to warm up since it has no bypass, no valves at all. None on the circulator or the any of the return or supply lines. I tried to help the system a little by installing an aquastat (L6006c) on the supply line, so it keeps the circulator off until the water temp at the boiler reaches around 165 and then cycles it on and off. I thought this was a good idea since condensation is a problem when there is a cold start. I don't know if this was a good idea but it has helped some.
Yes, I opened the valve again and I still had the problem with the one room not warming up. I proceeded to the check the boiler and it had about 10psi @ 140 deg. I proceeded to bleed the system, beginning at the 2nd floor radiators. There was a lot of air in the 2nd floor radiators. I purged the air and supplied more water to the system. I had to do this a couple of times before I got all the air out. After all the air was out I was getting around 17psi @ 140 deg.
When I say radiator I mean cast iron radiators. Think they are in series.
I have been getting a little less heat at the room I had no heat before, but it's a big difference from the 68 deg. I was getting 73 before, now it's from 71-72. That's with the thermostat set to 69 and it's in the first floor. We can't set it back because we have a 6 month old, my wife is always cold and the room sits over a garage with no insulation in the garage ceiling.
The system takes forever to warm up since it has no bypass, no valves at all. None on the circulator or the any of the return or supply lines. I tried to help the system a little by installing an aquastat (L6006c) on the supply line, so it keeps the circulator off until the water temp at the boiler reaches around 165 and then cycles it on and off. I thought this was a good idea since condensation is a problem when there is a cold start. I don't know if this was a good idea but it has helped some.
#5
Sounds like you did the bleeding just right. I might suggest letting the system sit without the pump running for a few hours and then temporarily raising the pressure in the system as high as possible without the relief valve popping... say 25 PSI, and then bleed. Let them bubbles float up out of the water, and the extra pressure might give a little more 'oomph' to move that air.
That might be a tad on the high side... but as long as it doesn't get up to like 25 when the boiler is at 180, you should be OK.
Sure it does, it should. What's important is that it doesn't have 'not enough air' to provide that expansion 'cushion' you talked about... Have you serviced the tank lately? i.e. draining it completely, and then re-pressurizing it. In normal operation, the tank will be at least 1/2 full of water at 12 PSI.
Of course you know now that you can't close the valve on one series connected radiator and expect the others in series with it to still heat. But, they may be monoflo? Can you see the piping to/from the rads on the lower level at the ceiling in the basement? Can you describe how they are piped? Example: Is there one big pipe going around the perimeter with the in/out of each rad tee'd into the single big pipe? or does the pipe loop in and out of each rad (series), or, maybe there are two big pipes running around, with the in coming from one, and the out going to the other... what you see downstairs is _probably_ the same as upstairs.
I'm sure you also know that insulating that ceiling will go a LONG way toward making that room more comfortable...
Where have I heard THAT before? 
I think the 'stat on the circ is a good idea... one thing kinda bothers me though... if the system were cool... and called for heat, boiler fires, no circ... now the boiler is hot, and the pump kicks in and dumps a lot of cool water in a hot boiler...
How much differential you have set on that 'stat?
I might experiment with that stat setting a little... because the lower you can set it, the better for the boiler. Try knocking it down a few pegs... maybe mmmmm... 150 or so? Or have you already done the experiments? And if you can come up with an easy way to measure the return temps, that's what you need to keep an eye on. Of course a boiler bypass would be the way to go...
No valves anywhere? What were they thinking?
After all the air was out I was getting around 17psi @ 140 deg.
I know the compression tank has some water in it
Think they are in series
the room sits over a garage with no insulation in the garage ceiling.
my wife is always cold

I think the 'stat on the circ is a good idea... one thing kinda bothers me though... if the system were cool... and called for heat, boiler fires, no circ... now the boiler is hot, and the pump kicks in and dumps a lot of cool water in a hot boiler...
How much differential you have set on that 'stat?
I might experiment with that stat setting a little... because the lower you can set it, the better for the boiler. Try knocking it down a few pegs... maybe mmmmm... 150 or so? Or have you already done the experiments? And if you can come up with an easy way to measure the return temps, that's what you need to keep an eye on. Of course a boiler bypass would be the way to go...
No valves anywhere? What were they thinking?
#6
Member
Thread Starter
Join Date: Jan 2010
Location: PA
Posts: 33
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sounds like you did the bleeding just right. I might suggest letting the system sit without the pump running for a few hours and then temporarily raising the pressure in the system as high as possible without the relief valve popping... say 25 PSI, and then bleed. Let them bubbles float up out of the water, and the extra pressure might give a little more 'oomph' to move that air.
That might be a tad on the high side... but as long as it doesn't get up to like 25 when the boiler is at 180, you should be OK.
Sure it does, it should. What's important is that it doesn't have 'not enough air' to provide that expansion 'cushion' you talked about... Have you serviced the tank lately? i.e. draining it completely, and then re-pressurizing it. In normal operation, the tank will be at least 1/2 full of water at 12 PSI.
Of course you know now that you can't close the valve on one series connected radiator and expect the others in series with it to still heat. But, they may be monoflo? Can you see the piping to/from the rads on the lower level at the ceiling in the basement? Can you describe how they are piped? Example: Is there one big pipe going around the perimeter with the in/out of each rad tee'd into the single big pipe? or does the pipe loop in and out of each rad (series), or, maybe there are two big pipes running around, with the in coming from one, and the out going to the other... what you see downstairs is _probably_ the same as upstairs.
I'm sure you also know that insulating that ceiling will go a LONG way toward making that room more comfortable...
I think the 'stat on the circ is a good idea... one thing kinda bothers me though... if the system were cool... and called for heat, boiler fires, no circ... now the boiler is hot, and the pump kicks in and dumps a lot of cool water in a hot boiler...
How much differential you have set on that 'stat?
I might experiment with that stat setting a little... because the lower you can set it, the better for the boiler. Try knocking it down a few pegs... maybe mmmmm... 150 or so? Or have you already done the experiments? And if you can come up with an easy way to measure the return temps, that's what you need to keep an eye on. Of course a boiler bypass would be the way to go...
No valves anywhere? What were they thinking?
thanks again Trooper!
#7
So you have two main pipes and each radiator has one pipe going to one main and another pipe going to the other main? IF that is the case, then it is in parallel. Series would have the water flow through one radiator to get to the next radiator.
#8
what they recommended was giving the system a tune-up to the tune of $1500. Then they recommended a new system, which they thought was necessary after looking around a bit.
I'm not sure if you mentioned the fuel type either?
...from what I remember it's called "waterlogged"... I can knock on the tank and it doesn't sound full ... How can I repressurize a steel tank?
I'd like to see pics before you proceed, but you did mention that there is a valve in the line to the tank, with a drain valve on it? And that the valve is rusted... so let's have a look before you turn that valve... but basically, the procedure would be to isolate the tank from the system by closing that valve (if it's in the line to the tank?) and connecting a hose to the drain. It should be a hose that's only long enough to get to your drain point... it shouldn't be looped all around, because that won't allow air to travel back up the hose, and the end of the hose should be open, not submerged in a bucket, for the same reason.
You need to completely drain that tank. What happens most often is the 'drinking straw analogy'... finger on the end of the straw and the drink stays in the straw when you lift it out... same thing happens with those tanks. You open the drain, and gravity and pressure drain the tank until a 'suction' or 'vacuum' forms in the tank, and water stops draining. You need to break that suction by forcing some air into the hose.
Sometimes you can blow into the end of the hose, but think about the germs and whatnot ... I'm not a big fan of that method. If you have an air compressor, you can blow that into the end of the hose... sometimes just loosening the hose connection where it's connected to the drain will allow it to take a gulp of air... you may also have one of the 'specialty' drain valves that includes an air valve on it... pics will tell.
Once you are sure that the tank is empty (or full... of AIR), you would close the drain, and re-open the isolation valve. Water from the system will enter the tank, and it will fill to around 1/2 with water. That's normal... the air in the tank will compress to whatever pressure is on the system.
As the system heats and cools, the air 'bubble' will be compressed more or less depending on the system pressure.
Typically, you might expect say 8-10 PSI pressure change from a cold boiler to a high limit boiler. This is usually a better indicator of the status of the compression tank than tapping. If you have excessive swing in pressure it's a sure bet the tank is near waterlogged.
two big pipes running around, with the in coming from one, and the out going to the other.This would be considered in series?
It is possible that the upstairs is in series though... look some more... it might be that the supply and return for each upstairs rad is piped down to the basement, and also tees into the same pipes that the downstairs do. It could also be set up with another pair of two pipes going upstairs, and around, and those rads tee'd in up there.
With a two pipe system, and functioning shut off valves on each radiator (don't force them!

That moved air has to go somewhere... and that somewhere should be back to the expansion tank. Ideally, with a compression tank, it would be connected to an 'air scoop' which would collect the air from the system as it is caught, and pass it up to the expansion tank. All the piping to the tank should be sloping uphill in order for the air to make it's way back in... this is another reason I'd like to see pics if possible.
Yes, we are going to work on that [floor insulation] this spring/summer.
more later... chores...
#10
I know how much you distrust these temp/pressure gauges but that's all I have for now. I will try to get a infrared thermometer or is there anything else you can suggest.
If you do go with the infrared, pick up a small can of flat black paint. If you first paint all the points you intend to measure, you will get the best accuracy. Those thermometers are terribly inaccurate on copper pipe. Rusty old cast iron, reasonably accurate... anything shiny, not accurate. Flat black paint, about as good as yer gonna get (not perfect, but good) Google "EMISSIVITY" for more info on this.
I think your pump a'stat is the lesser of two evils. If you've done the experiments, and are happy with the settings, then leave it be. If you use some 'heat sink compound' between the pipe and the bulb, and INSULATE the bulb and pipe at least a foot in each direction, you will get better performance of the stat... but don't expect pinpoint precision on the dial calibration in any event.
#11
Member
Thread Starter
Join Date: Jan 2010
Location: PA
Posts: 33
Upvotes: 0
Received 0 Upvotes
on
0 Posts

Pictures by ezra18042 - Photobucket
Typical... I'm glad you didn't bite... what make/model is the boiler? appx age? Why not post a few pics and we'll look them over and evaluate / make suggestions... know how to do the photo bucket thing?
I'm not sure if you mentioned the fuel type either?
I'm not sure if you mentioned the fuel type either?
It is possible that the upstairs is in series though... look some more... it might be that the supply and return for each upstairs rad is piped down to the basement, and also tees into the same pipes that the downstairs do. It could also be set up with another pair of two pipes going upstairs, and around, and those rads tee'd in up there.
With a two pipe system, and functioning shut off valves on each radiator (don't force them! ) if you have a 'problem' radiator that seems to have an air blockage, you can increase the flow through the problem unit by closing the valves on some/all of the other radiators. This might help to move that air out... but this brings up another point.
If the ceiling in the garage is exposed, explore having it spray foamed... that stuff also acts as a vapor and infiltration barrier. (for a few hundred bucks, there are also DIY kits available, but know that BIG mistakes can be made, so if you decide to DIY with spray foam, do your homework!)
You noticed that, eh?
If you do go with the infrared, pick up a small can of flat black paint. If you first paint all the points you intend to measure, you will get the best accuracy. Those thermometers are terribly inaccurate on copper pipe. Rusty old cast iron, reasonably accurate... anything shiny, not accurate. Flat black paint, about as good as yer gonna get (not perfect, but good) Google "EMISSIVITY" for more info on this.
I think your pump a’ stat is the lesser of two evils. If you've done the experiments, and are happy with the settings, then leave it be. If you use some 'heat sink compound' between the pipe and the bulb, and INSULATE the bulb and pipe at least a foot in each direction, you will get better performance of the stat... but don't expect pinpoint precision on the dial calibration in any event.
Pete
#12
It is an H.B. Smith Series-8.
What's with the duct tape on the gas burner? That don't look right.
I am not sure about this, because I have zero experience with gas burner conversions, but I have to wonder if the baro damper maybe should have been replaced with an atmospheric hood... or maybe not, since the gas burner is pressure fired... anybody know?
That would still make it a parallel branch wouldn't it?
I actually have flat black paint that is used on grills. Is that any good?
I just tried to do the best I could with what I had.
Ultimately though, a bypass would be the way to go...
#13
Member
Thread Starter
Join Date: Jan 2010
Location: PA
Posts: 33
Upvotes: 0
Received 0 Upvotes
on
0 Posts
What's with the duct tape on the gas burner? That don't look right.
Ultimately though, a bypass would be the way to go...
Pete
#15
First let's make sure that it's needed...
If the tank is waterlogged, you will see large pressure swing from cold to hot. If the tank is OK, you probably wouldn't see more than 8-10 psi increase from C to H ... cold should be around 12 PSI or so. So first determine if you really need to drain the tank.
If you do need/want to drain, a few pointers will be helpful.
First, the valve... before you try to close that valve, take some fine emery paper, or a wire brush, or steel wool and clean the STEM... get all that gunk off there, because if you close the valve with that stuff on the stem, it may damage the 'packing' material that seals the stem.
That valve is a 'gate valve', and when you close it, you don't want to 'muscle' it closed. If you do, you may end up wedging the gate into the slot and not get it open again... so snug it reasonably tight, but not power tight.
Of course, before you do anything, you want to shut the boiler off, and maybe let it cool a bit before you start.
Hook a hose to the drain valve. Remember that AIR needs to travel up the hose to displace the water that is being drained. If you use a long hose, all looped and rolled around on the floor, the air won't get to the tank. In other words, the hose should only be long enough to reach the bucket, or floor drain, or laundry tub... and don't submerge the end of the hose in the bucket when you drain either, again, air needs to go up.
Even with all this about the hose, the tank will probably STILL get 'suction locked', just like when you put your finger over the end of a drinking straw and lift it from the drink... drink stays in the straw. You will need to break that vacuum that develops in the tank. If you have a small air compressor, you can blow that up the hose... or if you have good lungs and are not afraid of dirty nasty boiler water in your face, you can blow into the end of the hose... sometimes by loosening the hose at the drain fitting the tank will take a 'gulp' of air... but whatever you need to do to get ALL the water out of the tank is what you need to do. (of course, not every last drop, but enough that you know the tank is at atmospheric pressure.)
Close the drain, open the gate valve and the tank will refill under pressure from the boiler to about half way... that's normal. Check that the boiler has returned to 12-15 PSI and fire it up.
If the tank is waterlogged, you will see large pressure swing from cold to hot. If the tank is OK, you probably wouldn't see more than 8-10 psi increase from C to H ... cold should be around 12 PSI or so. So first determine if you really need to drain the tank.
If you do need/want to drain, a few pointers will be helpful.
First, the valve... before you try to close that valve, take some fine emery paper, or a wire brush, or steel wool and clean the STEM... get all that gunk off there, because if you close the valve with that stuff on the stem, it may damage the 'packing' material that seals the stem.
That valve is a 'gate valve', and when you close it, you don't want to 'muscle' it closed. If you do, you may end up wedging the gate into the slot and not get it open again... so snug it reasonably tight, but not power tight.
Of course, before you do anything, you want to shut the boiler off, and maybe let it cool a bit before you start.
Hook a hose to the drain valve. Remember that AIR needs to travel up the hose to displace the water that is being drained. If you use a long hose, all looped and rolled around on the floor, the air won't get to the tank. In other words, the hose should only be long enough to reach the bucket, or floor drain, or laundry tub... and don't submerge the end of the hose in the bucket when you drain either, again, air needs to go up.
Even with all this about the hose, the tank will probably STILL get 'suction locked', just like when you put your finger over the end of a drinking straw and lift it from the drink... drink stays in the straw. You will need to break that vacuum that develops in the tank. If you have a small air compressor, you can blow that up the hose... or if you have good lungs and are not afraid of dirty nasty boiler water in your face, you can blow into the end of the hose... sometimes by loosening the hose at the drain fitting the tank will take a 'gulp' of air... but whatever you need to do to get ALL the water out of the tank is what you need to do. (of course, not every last drop, but enough that you know the tank is at atmospheric pressure.)
Close the drain, open the gate valve and the tank will refill under pressure from the boiler to about half way... that's normal. Check that the boiler has returned to 12-15 PSI and fire it up.