supply temp ver: return temp

I have a small staple up under floor radiant heating system.
Right now 8 zone manifold that I am using 5 zones, will be adding 3 more zones in the near future.
I am running supply temp of 140deg F (it actually runs at 137 / 138deg F)
The return temp is between 126 and 128deg F, so it runs between 8 to 10deg F cooler.
Is this a good ratio?

Thanks for any info.
 
  #2  
Old 04-10-10, 03:19 PM
P
Temporarily Suspended
Join Date: Jul 2008
Location: NY
Posts: 10,265
Upvotes: 0
Received 0 Upvotes on 0 Posts
I don't see how it could be any better but wait for some other opinions.
 
  #3  
Old 04-11-10, 10:50 PM
W
Member
Join Date: Apr 2010
Location: New Jersey
Posts: 17
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thats good suppose to really be 15 degree TD try lowering the water tempa little possability your short cycling.
 
  #4  
Old 04-12-10, 04:51 AM
M
Member
Join Date: Nov 2009
Location: NYC
Posts: 23
Upvotes: 0
Received 0 Upvotes on 0 Posts
5 zones of heating only extract 10-12 degrees from the supply water? Either you're over-pumped or under-radiated. A smaller pump might save you some money, but I wouldn't bother if your 3 future zones are large enough to bring you closer to a 15°-20° ∆T.
 
  #5  
Old 04-12-10, 04:52 AM
X
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes on 0 Posts
Return temp is not 'supposed' to be anything except what it was designed to be at design load.

So, if you designed the system for a 10F drop, which is common for several flavors of radiant systems, then at design cold load conditions, it should be in that ballpark. At temperatures higher than design load, the drop will be a bit less.
 
  #6  
Old 04-12-10, 06:02 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,407
Upvotes: 0
Received 66 Upvotes on 55 Posts
Delta T is dependent on water temperature and flow. The Delta-T will be lower with cooler water and increase as water temperature increases. Flow also changes with water temperature.
This is one reason for the increased interest in variable speed pumps measuring Delta-T or Delta-P.
 
 