I have a small staple up under floor radiant heating system.
Right now 8 zone manifold that I am using 5 zones, will be adding 3 more zones in the near future.
I am running supply temp of 140deg F (it actually runs at 137 / 138deg F)
The return temp is between 126 and 128deg F, so it runs between 8 to 10deg F cooler.
Is this a good ratio?
Thanks for any info.
Right now 8 zone manifold that I am using 5 zones, will be adding 3 more zones in the near future.
I am running supply temp of 140deg F (it actually runs at 137 / 138deg F)
The return temp is between 126 and 128deg F, so it runs between 8 to 10deg F cooler.
Is this a good ratio?
Thanks for any info.
#4
Member
Join Date: Nov 2009
Location: NYC
Posts: 23
Upvotes: 0
Received 0 Upvotes
on
0 Posts
5 zones of heating only extract 10-12 degrees from the supply water? Either you're over-pumped or under-radiated. A smaller pump might save you some money, but I wouldn't bother if your 3 future zones are large enough to bring you closer to a 15°-20° ∆T.
#5
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Return temp is not 'supposed' to be anything except what it was designed to be at design load.
So, if you designed the system for a 10F drop, which is common for several flavors of radiant systems, then at design cold load conditions, it should be in that ballpark. At temperatures higher than design load, the drop will be a bit less.
So, if you designed the system for a 10F drop, which is common for several flavors of radiant systems, then at design cold load conditions, it should be in that ballpark. At temperatures higher than design load, the drop will be a bit less.
#6
Delta T is dependent on water temperature and flow. The Delta-T will be lower with cooler water and increase as water temperature increases. Flow also changes with water temperature.
This is one reason for the increased interest in variable speed pumps measuring Delta-T or Delta-P.
This is one reason for the increased interest in variable speed pumps measuring Delta-T or Delta-P.