Back Flow Valve Needed on TT System

I recently installed a Solo 110 with a Smart 40 storage tank. They did an excellent install, but I have a question since the heating system is over.
I have a very simple setup just the one loop for CH and the DHW loop.
This is my first summer season with my new equipment and I have noticed that when there is a call for DHW that the return line of the system gets backed up with hot water. The system has a common return line for CH and DHW and I was wondering if the installer should have installed a back flow valve in the section of the return line to provides CH.
If the DWH is on more that 5 minutes, I can feel heat in a couple of my baseboard heaters. I am now trying to cool the house so I do not need any extra heat.
 
Sponsored Links
  #2  
Old 05-18-10, 02:30 PM
T
Member
Join Date: Jul 2009
Location: Toronto
Posts: 1,174
Received 0 Votes on 0 Posts
yes they sure should have
 
  #3  
Old 05-18-10, 03:02 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
I would say probably yes... there should have been something done to prevent heating the home when there's a DHW call. If there's a pump for each the CH and the DHW, then it might be as simple as changing the pumps for ones with internal check valves. If it's done with a single pump and zone valves, might be something more... flow check valves might need to be installed.

Can you post pics of the install?
 
  #4  
Old 05-18-10, 05:27 PM
T
Member
Join Date: Jul 2009
Location: Toronto
Posts: 1,174
Received 0 Votes on 0 Posts
Originally Posted by NJ Trooper View Post
I would say probably yes... there should have been something done to prevent heating the home when there's a DHW call. If there's a pump for each the CH and the DHW, then it might be as simple as changing the pumps for ones with internal check valves. If it's done with a single pump and zone valves, might be something more... flow check valves might need to be installed.

Can you post pics of the install?
The Solo 110 has a built in grundfos 15-58 three speed.
Suppose you could open it and install a check, but it would be easier to add them in the field pipework I'd think
 
  #5  
Old 05-18-10, 07:42 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
Isn't the check standard on the 15-58 ?

and the pump on the boiler is for the boiler loop... and the system should have been piped P/S... correcto?

So, if it is P/S, then there must also be another pump for the CH loop...

I still wanna see pics.
 
  #6  
Old 05-19-10, 04:22 AM
T
Member
Join Date: Jul 2009
Location: Toronto
Posts: 1,174
Received 0 Votes on 0 Posts
Originally Posted by NJ Trooper View Post
Isn't the check standard on the 15-58 ?

and the pump on the boiler is for the boiler loop... and the system should have been piped P/S... correcto?

So, if it is P/S, then there must also be another pump for the CH loop...

I still wanna see pics.
Checks are optional on OEM pumps.
The solo 110 does not ALWAYS need hydraulic isolation, the healoss thru the boiler is low enough that it can supply the boiler flow and still have head left for the system.

The indirect comes of a third line, it's tee'd into the outlet of the heat exchanger and the inlet to the CH pump.
 
  #7  
Old 05-20-10, 05:48 AM
V
Member
Thread Starter
Join Date: Jan 2010
Location: Western Pennsylvania
Posts: 7
Received 0 Votes on 0 Posts
There is two pumps. One internal for CH and one external for DHW.
There is no noticeable heat on the supply side where the internal pump is housed, just on the common return side. I have a ball valve on the return side that I have closed for summer until I find out if I should install something else.

[IMG] [/IMG]
 
  #8  
Old 06-15-10, 06:24 AM
1
Member
Join Date: May 2010
Location: USA
Posts: 29
Received 1 Vote on 1 Post
On piping applications utilizing a single
zone or other recognized piping design
arrangements, it is recommended that the
installer uses flow/check valves with
weighted seats at or near the appliance to
prevent gravity circulation.

http://www.triangletube.com/document...0%20Manual.pdf
 
  #9  
Old 06-16-10, 07:13 PM
T
Member
Join Date: Jul 2009
Location: Toronto
Posts: 1,174
Received 0 Votes on 0 Posts
Originally Posted by VetteGarage View Post
There is two pumps. One internal for CH and one external for DHW.
There is no noticeable heat on the supply side where the internal pump is housed, just on the common return side. I have a ball valve on the return side that I have closed for summer until I find out if I should install something else.
I will always try to put a flow check as close to the top return line on the Smart series tanks. This prevents flow thru the tank during a CH call, and I have seen many times where a micro flow will develop in the line off the return pipe. This will bleed heat out of the tank and increase your standby loss of the tank.

You also NEED a check on the return to prevent heat from migrating up the return during a DHW call in the summer.
You could use a check in the pump to control flow, but you still need at the very least a heat trap at the return junction between the Ch flow path and the DHW flow path.

Get the installer back (hopefully you can) and get them to install the checks.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: