Water heater blower keeps shutting off
I have a AO Smith FPSH 50 water heater. Since today i am noticing that the water heater exhaust air blower turns on and shuts off with in a minute.
I checked and noticed that the pilot flame does not come on.
The blower starts again in 5 mts and does the same thing again. Does anyone what is wrong and how can i fix it.
Also the blower has become very noisy (it always was noisy). Is something going bad on it ?
Thanks.
I checked and noticed that the pilot flame does not come on.
The blower starts again in 5 mts and does the same thing again. Does anyone what is wrong and how can i fix it.
Also the blower has become very noisy (it always was noisy). Is something going bad on it ?
Thanks.
#2
Not real familiar with your unit... sounds like a high efficiency job...
There are circuits that 'prove' the exhaust blower is operating properly before the pilot and main flame are allowed to ignite.
It's very possible that the problem is that these circuits are working for your safety and not letting the flame light because there is a problem with the blower.
Normally your post should go into the 'water heater' forum, since this is mainly for home heating systems, but there are some guys here who might wanna have a 'crack' at your question... so we'll leave it here for a bit. (and nobody is heating right now!)
There are circuits that 'prove' the exhaust blower is operating properly before the pilot and main flame are allowed to ignite.
It's very possible that the problem is that these circuits are working for your safety and not letting the flame light because there is a problem with the blower.
Normally your post should go into the 'water heater' forum, since this is mainly for home heating systems, but there are some guys here who might wanna have a 'crack' at your question... so we'll leave it here for a bit. (and nobody is heating right now!)
#3
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes
on
0 Posts
This unit has a power vent, but otherwise it isn't a high-efficiency model. There are several interlocks that may be causing the failure to light.
There is a hot-surface ignitor along with a flame-proving device. If the flame sensor doesn't verify a flame, the unit will lock out. Could be either the flame sensor or the ignitor.
The only fan interlocks are high flue gas temp and high fan suction vacuum - either could lock out the system. But just a noisy fan shouldn't do it?
AO Smith has troubleshooting here (which you ought to be able to perform with a voltmeter): http://www.hotwater.com/lit/training/tc048r6.pdf
There is a hot-surface ignitor along with a flame-proving device. If the flame sensor doesn't verify a flame, the unit will lock out. Could be either the flame sensor or the ignitor.
The only fan interlocks are high flue gas temp and high fan suction vacuum - either could lock out the system. But just a noisy fan shouldn't do it?
AO Smith has troubleshooting here (which you ought to be able to perform with a voltmeter): http://www.hotwater.com/lit/training/tc048r6.pdf
#4
THere is a blower proving switch the makes and allows the smart valve to continue in operation. Detach the rubber tube from the blower to the pancake switch{ prover}. Blow it out, there may be condensation in there. When the blower starts, there should be a audible click when the prover closes.