Cast Iron Rad BTU's
#1
Member
Thread Starter
Join Date: Oct 2009
Location: Connecticut
Posts: 69
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Cast Iron Rad BTU's
I Figured out the BTU's of my cast iron Rads at 180deg water temp but does anyone have a chart for the multipliers for lower water temps?
#3
Member
Join Date: Jul 2009
Location: Toronto
Posts: 1,043
Upvotes: 0
Received 0 Upvotes
on
0 Posts
#4
Member
Thread Starter
Join Date: Oct 2009
Location: Connecticut
Posts: 69
Upvotes: 0
Received 0 Upvotes
on
0 Posts
#5
Member
Join Date: Mar 2006
Location: USA
Posts: 197
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Here's a weird question about cast iron rads running hot water:
According to this from Comfort Calc/Burnham
at 180F the unit puts out 590 BTUH per linear foot. Subtracting the 15% factor, it's actually 513. The baseray is about 9" tall, so a linear foot is about .75sf, so the total output is 684 per sf.
However, according to this from Comfort Calc/Burnham
a cast iron radiator puts out 170BTUH per sf at 180F.
Am I missing something here? Why the huge difference? Or am I using one of the charts wrong?
According to this from Comfort Calc/Burnham
at 180F the unit puts out 590 BTUH per linear foot. Subtracting the 15% factor, it's actually 513. The baseray is about 9" tall, so a linear foot is about .75sf, so the total output is 684 per sf.
However, according to this from Comfort Calc/Burnham
a cast iron radiator puts out 170BTUH per sf at 180F.
Am I missing something here? Why the huge difference? Or am I using one of the charts wrong?
#6
The 9A baseboard is 3.4 sq ft per lineal ft. The rads are anywhere between 1 and 3 sq ft per section on tube types and even more on column type. It depends on the type of radiator. The chart you are referring to is once you calculate the sq ft from the type of radiation it is btu's per sq ft of radiator. I don't know where you got the figure of 0.75 sq ft per lineal ft. The 9A chart shows 3.4 sq ft per lineal ft.
I am not sure what the 15% factor is you are deducting.
I am not sure what the 15% factor is you are deducting.
#7
Member
Join Date: Mar 2006
Location: USA
Posts: 197
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The 9A baseboard is 3.4 sq ft per lineal ft. The rads are anywhere between 1 and 3 sq ft per section on tube types and even more on column type. It depends on the type of radiator. The chart you are referring to is once you calculate the sq ft from the type of radiation it is btu's per sq ft of radiator. I don't know where you got the figure of 0.75 sq ft per lineal ft. The 9A chart shows 3.4 sq ft per lineal ft.
I am not sure what the 15% factor is you are deducting.
I am not sure what the 15% factor is you are deducting.
The 15% factor is the extra heating factor that IBR allowed baseboard manufacturers to add to their heat ratings. The thought was that because they are lower to the ground than conventional radiators, they are more effective. According to Sigenthaler, this factor has no basis in reality, and if the manufacturer data includes it (as the Baseray data does), it should be taken out when doing calculations.
#8
Leave it in. The idea of cast iron being about 70% radiant accounts for less air currents which reduces the heat loss. I do not and never have reduced the btu output.
The square ft is the actual sq ft of iron not the physical dimension.
The square ft is the actual sq ft of iron not the physical dimension.