Argo Arm-4P Relay box

Have a Argo ARM-4P relay set for cold start Hooked up with Honeywell Aquastat L8148E want to set it to hot start any help Thank You
 
  #2  
Old 09-21-10, 07:05 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Can you tell us why you want to change to warm start? It's a huge waste of fuel... but maybe you have a good reason?

There's nothing on the Argo panel that is going to let you change to warm start, that's a function of the aquastat. You would have to lose the 8148 and replace with a 'triple' aquastat.

But again, why ?
 
  #3  
Old 09-22-10, 02:01 PM
D
Member
Thread Starter
Join Date: Sep 2010
Location: usa
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
runing low on hot water

With the showers at all different times i am running out of hot water with my indirect water tank because the boiler is cold when the indirect calls for water
The Argo has ZC and ZR to hook up to the aquastat i have nothing i can find
Thank You for your help
 
  #4  
Old 09-22-10, 09:26 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
OK, understand... and your 'solution' may help the problem somewhat, but daggone it's gonna cost ya some bux for the extra fuel.

I guess perhaps the indirect is too small then, if yer runnin' out of hot water before the unit can recover.

Still, you will have to change the aquastat. Those ZC and ZR terminals on the Argo won't help you go warm start...

There is a way to go warm start with an add on aquastat, but you would need another immersion well on the boiler for that.

I think the easiest way is to change the a'stat out.

I wonder if there is something else going on that the indirect can't recover fast enough?

Is this a long term problem? Something you've lived with for years? Or did you maybe just move into this home ?

Give us a little history please...
 
  #5  
Old 09-23-10, 11:45 AM
D
Member
Thread Starter
Join Date: Sep 2010
Location: usa
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes bought the house with a bad tank(leaking) install new 35 Gal have five people 3 are Girls you understand Were only two people in house before and they had no problem could you help with what A'state to install
Thank you for you help
 
  #6  
Old 09-23-10, 04:33 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
OK then... let me ask you this: On the new indirect, was a TEMPERING VALVE, or sometimes called a MIXING VALVE installed when it was replaced?

What temperature is the aquastat on the indirect set at?

A tempering valve, properly piped, will 'extend' the amount of hot water available from a water heater. It does this by allowing the water heater to run at a higher temp, say 140° and tempers the water going to the home to a 'safe' 120°, by mixing some cold with the hot from the water heater. So, you end up using less of the hot water in the tank.

I would definitely explore this idea first, before commiting to a warm start... cuz it's gonna cost some bucks to keep the boiler warm 24/7/52 !
 
  #7  
Old 09-23-10, 06:54 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,407
Upvotes: 0
Received 66 Upvotes on 55 Posts
I think making the boiler a warm start is a mistake. Let's determine why you are running out of hot water. My guess is a piping or flow issue.
Let's start by gathering some info.
What is the model and manufacturer of the tank?
What is the make and model of the circulator?
What size pipe is between the boiler and the tank?
What is the make and model of the boiler along with the boiler DOE or Gross output?
 
  #8  
Old 09-24-10, 04:35 PM
D
Member
Thread Starter
Join Date: Sep 2010
Location: usa
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you I will try this and let you know how it works
 
  #9  
Old 09-24-10, 05:42 PM
D
Member
Join Date: Aug 2009
Location: USA
Posts: 4,344
Upvotes: 0
Received 1 Upvote on 1 Post
I have a 35 gallon indirect and my boiler has a DOE output of 88k btu. I can tell you with one shower going I never run out of hot water and the recovery time is short. I have mt tank set to 130 degrees with a 10 degree differential.
 
 