Circulator pump not turning on when t-stat calls for heat.
I have a honeywell L8148A aquastat and a Tace pump. The boiler turns on when the low limit is reached and turns off when the high is reached. No volts on the C1-C2 circuit in the aquastst even when the boiler is on. I checked the pump and it works when I wire directly to a separate 120V. The (4) zone valves have 24V coming from the transformer and the valves opens when the t-stat calls for heat. Is it possable that all 4 zone valves are bad or is it the aquastat?
When you say "the boiler turns on", you mean that the BURNER fires, correct?
I don't understand what you mean by "when the low limit is reached", there is no low limit control on the 8148A aquastat. There IS a fixed 'differential', is that what you mean?
If the burner is firing, but the pump is not running, and you do have an L8148A (not a typo), then the problem is in the aquastat. Probably either toasted contacts on the relay, or a bad solder connection on the pc board.
Thanks, Looks like I'll be changing the aquastat before it gets to cold since I'll have to drain the boiler first.
Correct the burner fires.
Correct this aquastat is a fixed differential type and the model number is correct.
I just encountered the same problem (no continuity between L3 and C1). I disconnected hot, neutral and ground, bent the four metal chassis tabs straight, tipped the circuit board out and found a bad solder joint behind the solenoid. Reassembled and it works perfectly. This is apparently a common problem with these Aquastats...