Aquastat 8182D installation
#1
Member
Thread Starter
Join Date: Nov 2010
Location: usa
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Aquastat 8182D installation
Hello,
I bought a used aquastat to get me through a few more months. I read the installation instructions which recommend hiring a pro. I have good mechanical ability but no experience working on a boiler or knowledge of what could happen. Is the aquastat installation something I should try?
Thanks-Robb
I bought a used aquastat to get me through a few more months. I read the installation instructions which recommend hiring a pro. I have good mechanical ability but no experience working on a boiler or knowledge of what could happen. Is the aquastat installation something I should try?
Thanks-Robb
#2
It's not hard really... of course you need to get the wires back on the right terminals... so label them when you take them off ... digital pics help also ...
When you reinstall, make sure that the temp sensing bulb is fully inserted into the 'well' on the boiler!
CAUTION: 120 VAC is present inside the aquastat! REMOVE POWER FROM BOILER BEFORE STARTING! (I know you know that, but I have to say it anyway)
How sure are you that the used one you bought is any better than the one you have?
When you reinstall, make sure that the temp sensing bulb is fully inserted into the 'well' on the boiler!
CAUTION: 120 VAC is present inside the aquastat! REMOVE POWER FROM BOILER BEFORE STARTING! (I know you know that, but I have to say it anyway)
How sure are you that the used one you bought is any better than the one you have?
#3
Member
Thread Starter
Join Date: Nov 2010
Location: usa
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
8182 d
It looks like basic electrical connections. Do you need to drain the system before taking off the old aquastat?
As far as the question; "How sure are you that the used one you bought is any better than the one you have?"
Only age. The one that is not working is 25 years, the one I've purchased is 6 months old. Fingers crossed. Thank you for the reply.
As far as the question; "How sure are you that the used one you bought is any better than the one you have?"
Only age. The one that is not working is 25 years, the one I've purchased is 6 months old. Fingers crossed. Thank you for the reply.
#7
Member
Join Date: Jan 2008
Location: Southeastern Pennsylvania
Posts: 3,104
Received 93 Upvotes
on
85 Posts
Hi Robb. Thought I would add my 2 cents. I had zero experience with boilers but with the help of this forum (notably from Trooper) I successfully replaced my Aquastat. I was nervous about the temp-bulb and the well. Don't know why but I thought it might be a bear to seat the bulb - but it wasn't.
However, I did one thing Trooper might say is wrong: With a new Aquastat you get some kind of thermal compound you can put on the temp-bulb in the well. Think this improves the heat transfer capability so the Aquastat gets a better reading? (I think?). But if I remember the compound is optional. My bulb fit very snugly so I never used the compound.
Everything seems fines however. So I really don't know the full story on the compound.
Good luck!
#8
I ain't gonna scold ya Dad! It will make the system more responsive, but it will work fine without it. And besides, when that crap dries up and hardens a bit it can make it a major PITA to get a tight fitting bulb out of the well. How long have aquastats been around and working fine without that stuff? Right, a long time.
On the other hand, if you were mounting final output transistors on a heatsink... then I would have something to say!
On the other hand, if you were mounting final output transistors on a heatsink... then I would have something to say!

#9
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I've used the heat compound when it came with the 'stat. But, it may be more important that the bulb physically touches the wall of the thermo-well. I can visualize the tube sticking into mid-air, not touching the wall. Maybe one chance in 50?
#10
If I was gonna use any at all, it would just be a bit in the very bottom of the well. Again though, with a bulb that fits properly in the well, probably not needed... the problem comes when you use so much that a good portion of the well is filled with it, and it actually makes it harder to get the bulb to the bottom because it's 'hydraulically' impossible to squeeze the mass of stuff in the bottom of the well past the bulb as you try to bottom it out.
Maybe the best way would be to put a blob on the end of the bulb before inserting?
Maybe the best way would be to put a blob on the end of the bulb before inserting?
#11
Based on 40 years experience, the best place for the heat transfer paste is the garbage can. I had to drain more than one system and replace the well in order to replace the aquastat because after 25 years that paste was more like Super Glue.
#13
Member
Thread Starter
Join Date: Nov 2010
Location: usa
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
2 weeks ago I started this
The 8182D was in and performed for 13 days with no problem. Last night I noticed the temperature in the house dropping. I hit the reset on my new aquastat and the boiler turned on ran for a minute, then shut off before heating any water. The thing was cold. I noticed that it shut off immediately after hearing a sound similar to a blow torch lighting. I tried to reset again, same thing except this time there was no blow torch sound. It just shut off after 30 seconds. Being so late, I slept on it and tried resetting again this morning and it has been running correctly today. Usually I'd leave things as is, since it is working. Instead I am wondering if anyone has had a similar experience and what I could do proactively to avoid future shut downs. Thank you, Robb
#14
Dang, that sooks...
So much for used equipment? Or, is there some other problem that caused the reset?
I can't imagine what that 'blowtorch' sound was.
What was the ORIGINAL problem with the old aquastat?
So much for used equipment? Or, is there some other problem that caused the reset?
I can't imagine what that 'blowtorch' sound was.
What was the ORIGINAL problem with the old aquastat?
#15
Member
Thread Starter
Join Date: Nov 2010
Location: usa
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
original problem
What started it all was the boiler would start then shut off after a minute + or -. Kind of similar to what happened Sunday night. After Monday AM's reset however it is still operating.
#16
Robb, let me ask you this: When was the last time you had the boiler cleaned, and the burner serviced?
There's a very good possibility that the Protectorelay is doing what it should be doing, and the problem is in the burner itself, the flame 'eye' (CAD cell) or the flame actually going out.
There's a very good possibility that the Protectorelay is doing what it should be doing, and the problem is in the burner itself, the flame 'eye' (CAD cell) or the flame actually going out.
#17
Member
Thread Starter
Join Date: Nov 2010
Location: usa
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Well, I had the aforementioned problem in October. I called in a boiler serviceman who did clean and service the boiler. He was the one who told me it was the aquastat. He thought I could get another year out of this one. Anyway, thank you for the suggestion. I have a good enough relationship with him to call and ask about the burner or CAD cell.
#18
Keep us posted ...
The reason I asked about the old one is because for the reset button to pop out and need resetting, the aquastat would have had to think there was no flame. The way that thing works is that there is a 'heater' and a 'bimetal strip'. If there is no flame sensed, the bimetal strip flexes and trips the safety. If the CAD cell senses the flame, it turns off the heater and the unit stays running.
Not saying there can't be a fault with both the old and the used... but don't dismiss the fact that it could be something else entirely...
The reason I asked about the old one is because for the reset button to pop out and need resetting, the aquastat would have had to think there was no flame. The way that thing works is that there is a 'heater' and a 'bimetal strip'. If there is no flame sensed, the bimetal strip flexes and trips the safety. If the CAD cell senses the flame, it turns off the heater and the unit stays running.
Not saying there can't be a fault with both the old and the used... but don't dismiss the fact that it could be something else entirely...