Converting to gas from oil heat, and I have a chimney question.
#1
Member
Thread Starter
Join Date: Oct 2009
Location: Hackettstown, NJ
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Converting to gas from oil heat, and I have a chimney question.
I'm in the process of converting from an oil fired boiler to a gas fired one. My question pertains to the exhaust venting.
The boiler I'm installing is a Weil Mclain CGI-3 pin. It is an induced draft boiler. I will also be installing a conventional (non-induced vent) 50 gallon gas fired hot water heater.
What is giving me a hard time is the venting/chimney connection. Currently, I have an electric hot water tank and an oil fired boiler. The oil fired boiler is connected to the tile lined chimney with a 7" single wall pipe.
Here's the current setup:

My question is as follows: How do I connect the new boiler and water heater? The boiler is induced draft, the water heater is not. They'll be put in the same locations, roughly, but the new boiler is less than 1/2 the size of the oil burner.
I have a 6" chimney lining kit, as I know the exhaust gases will eat at the existing chimney liner. How do I configure the vent piping for the boiler and the water tank? I'm concerned that the induced draft boiler will cause exhaust to blow back into the water heater.
Thanks for any help.
The boiler I'm installing is a Weil Mclain CGI-3 pin. It is an induced draft boiler. I will also be installing a conventional (non-induced vent) 50 gallon gas fired hot water heater.
What is giving me a hard time is the venting/chimney connection. Currently, I have an electric hot water tank and an oil fired boiler. The oil fired boiler is connected to the tile lined chimney with a 7" single wall pipe.
Here's the current setup:

My question is as follows: How do I connect the new boiler and water heater? The boiler is induced draft, the water heater is not. They'll be put in the same locations, roughly, but the new boiler is less than 1/2 the size of the oil burner.
I have a 6" chimney lining kit, as I know the exhaust gases will eat at the existing chimney liner. How do I configure the vent piping for the boiler and the water tank? I'm concerned that the induced draft boiler will cause exhaust to blow back into the water heater.
Thanks for any help.
#3
Member
Thread Starter
Join Date: Oct 2009
Location: Hackettstown, NJ
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Budget is the main reason. Those indirect fired tanks sure seem expensive, last time I checked. Also, boiler capacity. Sized the unit for heating, not heating and DHW and I already own the boiler.
#4
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Agree. I don't know of an acceptable way to do what you want - combine the mechanical-draft boiler and water heater into the same flue. In addition to an indirect, you could consider a condensing water heater, and vent it through the wall in a plastic pipe.
Fitting a new metal liner inside your fireclay flue is fine, but it is not required by NFPA 211, the fire-protection code applicable to chimneys. If your new boiler is significanly more efficient or a higher rating than the old one, a Level 2 flue inspection is required. If the new boiler is within the old boiler's efficiency and rating, a Level 1 inspection is required. The Code defines the inspection levels, but only accessible areas need be inspected, not concealed area.
The applicability of such codes is determined by local ordinances, which may specify other requirements or no requirements.
Is there space inside your chimney to snake a metal flue just for a water heater? I'm wondering if a 4" liner might be OK for the water heater.
Fitting a new metal liner inside your fireclay flue is fine, but it is not required by NFPA 211, the fire-protection code applicable to chimneys. If your new boiler is significanly more efficient or a higher rating than the old one, a Level 2 flue inspection is required. If the new boiler is within the old boiler's efficiency and rating, a Level 1 inspection is required. The Code defines the inspection levels, but only accessible areas need be inspected, not concealed area.
The applicability of such codes is determined by local ordinances, which may specify other requirements or no requirements.
Is there space inside your chimney to snake a metal flue just for a water heater? I'm wondering if a 4" liner might be OK for the water heater.
#5
Capacity shouldn't be a problem unless your boiler is real tiny. The DHW can be set as priority so the boiler dedicates itself to heat the water and not the house. But the budget is the budget. I think there are direct vent hot water heaters out there. Have you checked to see if your boiler has an option to have a direct vent?
#7
I checked online and it seems the direct vent water heaters are more expensive than indirect tanks. I would consult with a chimney guy. You may be able to vent them both in the same flue, but I wouldn't know for sure. It seems like it would work logically to me, but I have very little knowledge on this type of thing. The 6" lining kit may not be large enough either. Maybe some people in the chimney forum can shed some better light on this.
#8
Member
Thread Starter
Join Date: Oct 2009
Location: Hackettstown, NJ
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The boiler can do direct vent, but not PVC direct vent. The supplier mentioned stainless direct vent piping, but I'm not sure what the particulars are.
#9
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I doubt that a 4" liner will be satisfactory for your non-condensing boiler. The liner needs to be at least the same size as the outlet flue from the boiler.
#10
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Your biggest problem is going to be a lack of height from the top of the water heater to the chimney connection. You need a minimum of 12 inches of vertical run from the water heater vent before bending to enter the chimney.
You CAN have both an atmospheric water heater and a furnace/boiler on the same chimney IF the "capacity" of the chimney is high enough. Capacity is related to the interior cross sectional area and the effective height of the chimney. You would normally use a Y fitting with the furnace/boiler venting into the "run" of the Y and the atmospheric burner (water heater) venting into the side of the Y. The installation instructions for both the boiler and the water heater need to be carefully read to see if there are any restrictions or recommendations.
You CAN have both an atmospheric water heater and a furnace/boiler on the same chimney IF the "capacity" of the chimney is high enough. Capacity is related to the interior cross sectional area and the effective height of the chimney. You would normally use a Y fitting with the furnace/boiler venting into the "run" of the Y and the atmospheric burner (water heater) venting into the side of the Y. The installation instructions for both the boiler and the water heater need to be carefully read to see if there are any restrictions or recommendations.
#11
Member
Thread Starter
Join Date: Oct 2009
Location: Hackettstown, NJ
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Mike: The outlet on the boiler is 3", according to the installation instructions it needs a minimum of a 4" flue.
Furd: I'm in the process of reading the instructions now to see what I can deduce.
Furd: I'm in the process of reading the instructions now to see what I can deduce.
#12
Furd, don't forget that the CGi is an INDUCED DRAFT boiler... I don't think it's allow to common vent it with another appliance...
Bishop, page 8, section 1c... third paragraph down.
Bishop, page 8, section 1c... third paragraph down.
#13
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes
on
0 Posts
True, but the boiler is mechanical draft, not atmospheric.
#14
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I tend to agree with your wanting to go with a gas-fired water heater. They are reasonably efficient and have decent recovery times - and if you go with the common 40-gal size, inexpensive. (The recovery time for a gas heater will be shorter than your current electric heater.) My last gas water heater lasted 50+ years, but that is probably unusual.
If you've got a couple of teenage kids in the family, a 40-gal gas heater might be a bit skimpy. But if going to a larger heater, say 50 gal, get your pocketbook out.
Last edited by Mike Speed 30; 11-17-10 at 05:36 PM.
#16
The outlet on the boiler is 3", according to the installation instructions it needs a minimum of a 4" flue.
#17
Member
Join Date: Jul 2009
Location: Toronto
Posts: 1,043
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Some boiler manufacturers will allow a induced draft boiler to be vented with an atmospheric appliance. The idea is that the 3 to 5 or 6" increaser changes the vent from a positive pressure to a negative pressure, and at that point the chimney effect takes over and expels that products of combustion.
If you can side wall vent it, and the distance is not too great think about going that route.
If you can side wall vent it, and the distance is not too great think about going that route.
#18
Member
Thread Starter
Join Date: Oct 2009
Location: Hackettstown, NJ
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Trooper, which code book? Also, (not that it's being kept) what's wrong with the baro damper? (So I know what to look for next time.)
TOHeating, I'll look into sidewall venting it, but problem is my basement is completely below grade, ceiling of the basement is roughly at ground level. Not sure how I can make that work.
I'm leaning towards leaving the electric tank as is for now, and going with an indirect fired unit once I can save up some more pennies. That eliminates a lot of my headaches, and simplifies the changeover so I can minimize the amount of down-time I have in my heating.
TOHeating, I'll look into sidewall venting it, but problem is my basement is completely below grade, ceiling of the basement is roughly at ground level. Not sure how I can make that work.
I'm leaning towards leaving the electric tank as is for now, and going with an indirect fired unit once I can save up some more pennies. That eliminates a lot of my headaches, and simplifies the changeover so I can minimize the amount of down-time I have in my heating.
#21
which code book?
what's wrong with the baro damper?
http://www.fieldcontrols.com/pdfs/DC01575700.pdf
Forced draft or induced draft there is still a positive pressure at the exhaust gas outlet.
Some boiler manufacturers will allow a induced draft boiler to be vented with an atmospheric appliance. The idea is that the 3 to 5 or 6" increaser changes the vent from a positive pressure to a negative pressure
#22
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Forced draft or induced draft there is still a positive pressure at the exhaust gas outlet.
Right... and the water heater will have an atmospheric hood on it, and if there is a positive pressure, the boiler will backdraft out that hood, UNLESS, as TO points out below:
Some boiler manufacturers will allow a induced draft boiler to be vented with an atmospheric appliance. The idea is that the 3 to 5 or 6" increaser changes the vent from a positive pressure to a negative pressure
...IF the "capacity" of the chimney is high enough.
It isn't the preferred method but it does work and is safe IF all things are done properly. I dare say there are tens of thousands of these installations in current use.
#23
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes
on
0 Posts
FWIW, I like the idea of keeping electric for now and going indirect with saved pennies. All that stainless venting adds up in cost, and a good indirect will far outlast and outperform a standard gas-fired water heater. One instead of two combustion appliances is a good thing, too.
#25
That is only true for the direct vent though...
What Furd and TO are saying is that by upsizing the flue pipe, you may be able to safely vent an atmospheric vented water heater into the same flue IF DONE PROPERLY.
I personally would choose not to do that though... I don't think I could sleep at night... but that's just me...
What Furd and TO are saying is that by upsizing the flue pipe, you may be able to safely vent an atmospheric vented water heater into the same flue IF DONE PROPERLY.
I personally would choose not to do that though... I don't think I could sleep at night... but that's just me...
#26
Member
Join Date: Mar 2006
Location: USA
Posts: 197
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I agree with Xiphias. Leave the electric for now, then get an indirect tank (Triangle Tube, Weil-McLain, or Willams are the only ones I'd use) when you can afford it. Just prepare some stubs in your boiler piping where you can later attach the pipes to the indirect.
#27
Member
Thread Starter
Join Date: Oct 2009
Location: Hackettstown, NJ
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok, that leads to *another* question, then. My current heating has no zone valves, it's one large pipe with those 'takeoff' fittings for each baseboard loop. If I was to use an indirect tank, I'd have to zone it, correct? That will be a bit of a pain, as that main loop runs the length of the house and some of those takeoffs are hidden behind the sheetrock ceiling.
#28
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Is there just a single piping loop - with baseboard supplies and returns teed off the same pipe? If so, then it sounds like a monoflo system.
But, whatever. If it is a monoflo system, you'd want two zones: one for the enitre monoflo loop and one for the indirect. The indirect would be set as priority. It would take two zone valves.
The fact that some of your existing loop is concealed behind walls, etc., shouldn't be a problem.
But, whatever. If it is a monoflo system, you'd want two zones: one for the enitre monoflo loop and one for the indirect. The indirect would be set as priority. It would take two zone valves.
The fact that some of your existing loop is concealed behind walls, etc., shouldn't be a problem.
#29
Member
Thread Starter
Join Date: Oct 2009
Location: Hackettstown, NJ
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes, it would be a single loop, with the baseboard supplies and returns teed off that loop.
I didn't know that there were zone valves that large.
So, if I have this right, I'd install a T in the beginning of the main loop, and that would be the takeoff for the indirect. Then, in the main loop return, I'd have another T, with a zone valve to close off the return from the main loop placed before the T, and another in the return from the indirect tank.
Does this sound correct, or am I off base?
I didn't know that there were zone valves that large.
So, if I have this right, I'd install a T in the beginning of the main loop, and that would be the takeoff for the indirect. Then, in the main loop return, I'd have another T, with a zone valve to close off the return from the main loop placed before the T, and another in the return from the indirect tank.
Does this sound correct, or am I off base?
#30
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If I follow you correctly, you've got the right idea. The zone valves can be on either the supply or return of a loop, whichever is easier.
How large is your main loop? Zone valves are available up to 1-1/4" from Taco and probably other manufacturers. If you used a 1-1/4" valve on a 1-1/2" line, it wouldn't be the end of the world.
How large is your main loop? Zone valves are available up to 1-1/4" from Taco and probably other manufacturers. If you used a 1-1/4" valve on a 1-1/2" line, it wouldn't be the end of the world.
#32
Member
Thread Starter
Join Date: Oct 2009
Location: Hackettstown, NJ
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yeah, DOE rating is 51k. Besides that factor, the indirect tanks are $$$! Minimum investment on my part will be at least $1000. Holy crap!
I'm going to call Weil Mclain Monday, get some clarification on the venting issue. From what I'm reading, I can't vent both appliances if it's a positive pressure vent, but if I increase the vent pipe to 6" right at the boiler connection, it's not a positive pressure vent anymore, it's a natural draft.
The plumber I spoke to today didn't see a problem with using 6" vent pipe right at the boiler, with a T that sweeps in at a 45 degree angle to add in the water heater. Says he's installed them that way before with no issues.
I'll see what Weil Mclain says Monday, I guess.
I'm going to call Weil Mclain Monday, get some clarification on the venting issue. From what I'm reading, I can't vent both appliances if it's a positive pressure vent, but if I increase the vent pipe to 6" right at the boiler connection, it's not a positive pressure vent anymore, it's a natural draft.
The plumber I spoke to today didn't see a problem with using 6" vent pipe right at the boiler, with a T that sweeps in at a 45 degree angle to add in the water heater. Says he's installed them that way before with no issues.
I'll see what Weil Mclain says Monday, I guess.
#33
Member
Join Date: Jul 2009
Location: Toronto
Posts: 1,043
Upvotes: 0
Received 0 Upvotes
on
0 Posts
For 50,000 BTU even a 3/4" zone valve would do no problem.
You can also zone with circulators and leave the monoflow on a summer winter switch.
I have gotten away from zoning with circulators except for large BTU systems, where zone valves make no sense.
You can also zone with circulators and leave the monoflow on a summer winter switch.
I have gotten away from zoning with circulators except for large BTU systems, where zone valves make no sense.
#35
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I think so. My relatively new, cheapo, 40-gal, gas-fired water heater is rated 40,000 Btu/hr input. The two of us never run out of hot water - including showering, clothes washing, dishwashing, etc. - or even with company staying with us.
#36
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Unless your boiler is running constantly during the coldest weather I suspect that you have enough capacity to use it with an indirect. You would have to use a priority setting on the indirect and you may even need to use a maximum time default back to space heating but only during the coldest of weather.
From your pictures the biggest problem in using the gas-fired water heater is that you simply don't have enough height to the chimney connection. You need a minimum of 12 inches vertical rise from the water heater vent before entering the chimney. You might be able to make a new flue connection higher up on the chimney and then cap the hole presently in use.
From your pictures the biggest problem in using the gas-fired water heater is that you simply don't have enough height to the chimney connection. You need a minimum of 12 inches vertical rise from the water heater vent before entering the chimney. You might be able to make a new flue connection higher up on the chimney and then cap the hole presently in use.
#37
Member
Join Date: Mar 2006
Location: USA
Posts: 197
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yup, the indirects (the good ones at least) aren't cheap. About the cheapest I've seen is a TT Smart 30 for $880 (SMART30 - Triangle Tube SMART30 - Smart 30 Indirect Water Heater). OTOH, a gas-fired water heater is something you'll replace every 5-15 years (usually after it fails catastrophically and causes a flood), whereas a good indirect (a stainless steel tank-in-tank design) should outlast you.
As to what Furd said - IMHO, if you have a priority on the DHW for your boiler (and you should, with a boiler that small), you MUST have a maximum time cutoff on the priority. This is a vital safety measure - if your DHW circulator/valve fail, or if the DHW aquastat fails closed, or even if there's just a short in the wiring, the system will never come off priority otherwise. If you are home, you'll get cold. If you aren't, you can get into a pipe freezing situation. I can't think of any situation where it's a good idea to have priority for the DHW without having a time-out on that priority.
As to what Furd said - IMHO, if you have a priority on the DHW for your boiler (and you should, with a boiler that small), you MUST have a maximum time cutoff on the priority. This is a vital safety measure - if your DHW circulator/valve fail, or if the DHW aquastat fails closed, or even if there's just a short in the wiring, the system will never come off priority otherwise. If you are home, you'll get cold. If you aren't, you can get into a pipe freezing situation. I can't think of any situation where it's a good idea to have priority for the DHW without having a time-out on that priority.
#38
The plumber I spoke to today didn't see a problem with using 6" vent pipe right at the boiler, with a T that sweeps in at a 45 degree angle to add in the water heater. Says he's installed them that way before with no issues.
You need a minimum of 12 inches vertical rise from the water heater vent before entering the chimney.
When you talk to W-M, or check the manual, think about the possibility of running the 3" pressure vent up the chimney. You might be able to fit that AND the WH vent in that chimney flue... but only IF W-M says it's OK to run the 3" vent that long a distance, and up the chim...
#40
Member
Thread Starter
Join Date: Oct 2009
Location: Hackettstown, NJ
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I figured I'd give a followup on the project, now that it's done and inspected and passed, with no problems.

I have a 3" to 5" adapter at the boiler, which then meets up with the 6" Y that is connected to the new liner. Weil-Mclain confirmed that if you increase the flue size directly at the boiler it is considered an atmospheric vent.
The other leg of the Y reduces down to 4" for the flue pipe connected to the hot water tank. From the top of the water tank to the bottom of the chimney entrance is a hair over 12" even if it doesn't look like it from the pictures. The 4" flue has a very steep rise to the 6" Y.
When I was assembling the flue piping, while everything was cold, it was still drafting hard. Before firing up anything, I smoke tested the hood on the hot water tank and it was drafting fine. I fired up the tank first to check the draft and it was very strong.
I then fired the boiler while checking the draft on the hot water tank, and it didn't change at all. It didn't blow back, but kept pulling the smoke right in from all sides of the hood.
This picture is from before I sealed the chimney with the high temp cement, so rest assured it's closed up.
I'd like to thank everyone for their help and insight!

I have a 3" to 5" adapter at the boiler, which then meets up with the 6" Y that is connected to the new liner. Weil-Mclain confirmed that if you increase the flue size directly at the boiler it is considered an atmospheric vent.
The other leg of the Y reduces down to 4" for the flue pipe connected to the hot water tank. From the top of the water tank to the bottom of the chimney entrance is a hair over 12" even if it doesn't look like it from the pictures. The 4" flue has a very steep rise to the 6" Y.
When I was assembling the flue piping, while everything was cold, it was still drafting hard. Before firing up anything, I smoke tested the hood on the hot water tank and it was drafting fine. I fired up the tank first to check the draft and it was very strong.
I then fired the boiler while checking the draft on the hot water tank, and it didn't change at all. It didn't blow back, but kept pulling the smoke right in from all sides of the hood.
This picture is from before I sealed the chimney with the high temp cement, so rest assured it's closed up.
I'd like to thank everyone for their help and insight!