prv thrush model c2 pressure reducing valve


  #1  
Old 01-23-11, 04:31 PM
F
Member
Thread Starter
Join Date: Jan 2011
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Unhappy prv thrush model c2 pressure reducing valve

anyone know how to reduce pressure the valve has pointed screw that comes off
 
  #2  
Old 01-23-11, 05:22 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Can we assume that the pressure in your boiler is high and that the relief valve opened and you are assuming that the pressure reducing valve is at fault?

In other words, what is the problem to start with?
 
  #3  
Old 03-09-11, 02:42 AM
F
Member
Thread Starter
Join Date: Jan 2011
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Pressure is high almost 40 to 60 psi have reduced by removing water with hose to 30psi. When boiler starts quickly rises 10 psi. Have just replaced expansion tank. How to check prv short of putting gauge in.
 
  #4  
Old 03-09-11, 05:28 AM
D
Member
Join Date: Aug 2009
Location: USA
Posts: 4,345
Upvotes: 0
Received 1 Upvote on 1 Post
Verify that your pressure gauge is accurate. Your relief valve should be open and dumping water if your system is above 30 psi.
 
 