Boiler with indirect water heater

Reply

  #1  
Old 02-25-11, 10:31 PM
C
Member
Thread Starter
Join Date: Mar 2007
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Boiler with indirect water heater

I am getting a Weil-Mclain WGO4 oil boiler with a Superstor 45 water heater. The instalation manual on the water heater said to use 1 inch copper and a 1 inch zone valve between the boiler and the water heater. The installer said he wants to use a 3/4 zone valve like on the other heating zones for a total of 4 valves.

He claims he does this all the time with no problems. Does this seem like a good practice?
 
Sponsored Links
  #2  
Old 02-25-11, 11:31 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,145
Received 60 Votes on 52 Posts
Whats he is going to pipe it all 3/4? You may want to find a new installer.

You may not get the full benefits of the recovery rating. Indirects are sized by boiler size, having the correct flow rate to the indirect, and pressure drop. (How long of pipe, elbows, check valves, etc. is all calculated for 1")

You need 10 GPM for the 40 and 8 for the 30

For that tank you boiler needs a min. of 141,000 BTU out to meet 1st hour ratings. I think your boiler has a IBR of 126,000 BTU. You might be better of with a 30 gal, It needs a min of 113,000 btu. If installed properly I think full recovey is like 10 minutes.

People usually way oversize a indirect. So you may want to rethink this whole thing.



I am not big on the # crunching and I might be off on my statments, and I am sure the more advanced BTU pros will be replying soon.

Mike NJ
 
  #3  
Old 02-26-11, 04:30 AM
X
Member
Join Date: Nov 2005
Location: USA
Posts: 2,459
Received 0 Votes on 0 Posts
Pipe the indirect with 1" like the manual says. Also use a dedicated circulator for the indirect and separate circ with zone valves for the space heating. Use a control (e.g., Taco ZVC) that allows priority on the indirect.
 
  #4  
Old 02-26-11, 05:22 AM
D
Member
Join Date: Aug 2009
Location: USA
Posts: 4,947
Received 0 Votes on 0 Posts
We went from a 50 gallon direct fired to a 35 gallon indirect. We never run out of hot water with the indirect.
 
  #5  
Old 02-26-11, 05:38 AM
rbeck's Avatar
Member
Join Date: Jul 2007
Posts: 2,482
Received 5 Votes on 4 Posts
As Lawrosa stated to achieve the number of gallons the correct flow and velocity must be achieved.
The 40 gal will supply 154 gallons first hour rating @ 141,000 btu boiler output.
If you are concerned with capacity think about stone lined indirect.
A 35 gallon stone lined tank will give you 200 gallon first hour rating @ 99,000 btu boiler input. This still uses 1" pipe and 6 gpm flow in the boiler piping side instead of 10 or 8 so possibly a smaller pump coulg be used.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: