Replacing pressure relief and checking air tank
#1
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 162
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Replacing pressure relief and checking air tank

I am going to replace the leaky pressure relief valve this weekend and want to get it right.
The pic is a bit fuzzy but:
1) Cool boiler
2) I shut off the lever circled in yellow, this the valve where you add the water very fuzzy).
3) To change the relief valve I would have to shut the valves circled in red and let the water out at the valve circled in green to zero and replace the valve.
4) Then re pressure the system to 12 to 15 cold
If I wanted to check the air in the air tank I am assuming I would shut the zone valves after the tank circled in blue (very fuzzy and hard to see) and leave the right hand red circled valve open. This would include the air tank in the isolated zone.
With the pressure at 0 pressurize to 12 psi.
Another question is how much water will come out to get the pressure to 0
Sounds pretty straight forward and I did a search so I think I got it.
#2
Yes all you say is correct. Close off valves to boiler mate if their there.
I would say about a gallon of water or so to get 0 psi. I would also change the airvent (little can above exp. tank) while your at it.
Also when you fill the boiler make sure the auto fill valve fills boiler to 12 psi. This is what they are preset to.
Mike NJ
I would say about a gallon of water or so to get 0 psi. I would also change the airvent (little can above exp. tank) while your at it.
Also when you fill the boiler make sure the auto fill valve fills boiler to 12 psi. This is what they are preset to.
Mike NJ
#3
Dropping the pressure in the boiler to zero will allow you to change the relief without water coming out UNDER PRESSURE, but you may still have some flow out by gravity... the water above the level of the relief valve may want to flow a bit... but with the two red valves closed you might get lucky and none will flow. In any case, be prepared to work quickly when you take the old valve off... have the new one ready to go within reach... and please, don't freak out with the teflon tape! TWO WRAPS is more than enough, and keep any tape or pipe dope off the first two threads of the valve. You want those first two threads METAL TO METAL.
I'm betting way less than a gallon... wouldn't surprise me if it's less than a quart!
As for the tank charging, you can actually do this with the zones open/closed, don't matter... as long as the pressure at the tank water side is at zero.
Here's the thing... if the air charge in the tank IS very low, there will be water in the tank. When you add air, you will push some, but not all of that water out. When that water pushes out into the system, the pressure in the system may rise. So, after the first dose of 12 PSI air in the tank, check the boiler gauge and drain a little more water if needed to drop the boiler back to zero. Then recheck the tank. Repeat until the boiler gauge stays at zero, and the tank stays at 12.
If you get any water out of the air valve, replace the tank.
I'm betting way less than a gallon... wouldn't surprise me if it's less than a quart!
As for the tank charging, you can actually do this with the zones open/closed, don't matter... as long as the pressure at the tank water side is at zero.
Here's the thing... if the air charge in the tank IS very low, there will be water in the tank. When you add air, you will push some, but not all of that water out. When that water pushes out into the system, the pressure in the system may rise. So, after the first dose of 12 PSI air in the tank, check the boiler gauge and drain a little more water if needed to drop the boiler back to zero. Then recheck the tank. Repeat until the boiler gauge stays at zero, and the tank stays at 12.
If you get any water out of the air valve, replace the tank.
#4
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 162
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The thing above the expansion tank says spirovent, micro bubble resorber. Do they go bad?? I am pretty sure I heard air come out of it when I flicked the relief valve. Changing that looks a little more into it than I want to go, especially if it is not bad. Don't know if I could get it off with out cutting and sweating some pipe. Pipe is threaded in on both sides.
Thanks I thought I had it right, but it's nice to know for sure.
Thanks I thought I had it right, but it's nice to know for sure.
#5
Yeah, I thought it looked like a Spiro... I'm sure it's OK. The top does unscrew on those if needed to clean them out, but don't fix it if it ain't broke.
Is there something between the tank and the Spiro? A valve perhaps?
Is there something between the tank and the Spiro? A valve perhaps?
#6
One more thing I wanted to mention... because I know you are going to ask at some point...
When your boiler starts up, and the pump runs, I would expect that you will see the pressure gauge on the boiler drop, perhaps as many as 5 PSI. Not to worry about that, it's because of the pump position in relation to the expansion tank.
When your boiler starts up, and the pump runs, I would expect that you will see the pressure gauge on the boiler drop, perhaps as many as 5 PSI. Not to worry about that, it's because of the pump position in relation to the expansion tank.
#7
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 162
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Nope, just a T to the valve where you add water. I do lose 5 psi or so when the Pump is on. I have researched pumping away. As far as the air tank the Plumber said he had to blip the schrader a few times because it was leaking bit. I check it and it is still holding fine, but I thought I would take the time to change it when I had the pressure down
#8
he had to blip the schrader a few times because it was leaking bit
For that little bit of extra seal, pick up a METAL cap, the kind with a rubber gasket and screw that on when yer done.
I wonder how many perfectly good tanks are replaced because a 49 cent air valve is leaking?
#9
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 162
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Well I changed the Pressure relief valve and the schrader tonight, it took more time for the boiler to heat up after than it did to change both . All went smooth, it was less than a quart that came out to go to 0 pressure. Filled the pressure tank to 12 and when I opened up the auto fill valve the pressure went right up to 12 an stopped. There was a little seepage (very little like a few drops) from the relief valve when I checked after the boiler was up to temp, but that was it. 3 hours later all is still dry so we will see if this fixes it. All I have left to do is to re sweat and reinstall the copper drain pipe from the valve
My cap is plastic but it does have an O ring seal on it.
My cap is plastic but it does have an O ring seal on it.
#10
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
All I have left to do is to re sweat and reinstall the copper drain pipe from the valve.
#12
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 162
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I forgot to say that there did look to be a bit of junk in the old valve and I did notice some green flecks in the water when I drained it. I am assuming it is from the copper pipe.
As far as a union or something I will see what I have in my box of parts. I did not come off and down from the valve. I ran ran the pipe to the back of the boiler. If it comes straight down from the valve and it ever blew a good one it would probably get the electronics in the front wet. I moved it to the back to keep it away from all that stuff.
As far as a union or something I will see what I have in my box of parts. I did not come off and down from the valve. I ran ran the pipe to the back of the boiler. If it comes straight down from the valve and it ever blew a good one it would probably get the electronics in the front wet. I moved it to the back to keep it away from all that stuff.
#15
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Union, thread adapters, Shark-Bite or whatever, just make it so it is unnecessary to unsolder or cut the piping in order to replace the safety valve. The same holds true at the make-up water supply (backflow preventer and pressure reducing valve) plus have valves on both sides of these parts.
#16
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 162
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks to everyone. I am on day 6 with no leaks at all. I would not have even known where to begin with this forum. Over the past 6 months or so I have gained a comfortable working knowledge of what the parts are on my boiler and how they work. I try to visit everyday just to learn more.
#18
Member
Join Date: Mar 2011
Location: United States
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
water coming out of resorber
I have water coming out of my spirovent microbubble resorber. I had a repair guy come and say that the rersorber and the expansion tank needs to be replaced. Because the gasket in the tank probably blew. Do I really have to replace BOTH the resorber AND the tank? The tank is sealed, so I don't think I can replace the gasket. But can't I just replace the tank?
#19
If you've got a Spirovent, they can be opened and cleaned. You probably have some 'crud' stuck under the valve. Here is a PDF file that explains the procedure:
http://www.spirotherm.com/docs/installation/JrIOM-A.pdf
You will of course need to drain the system unless you have valves positioned such that you can isolate that portion of the piping.
Here is a source of the vent head if it needs replaced:
Patriot Supply -
If the O-ring is damaged when taking it apart, you can likely find a proper replacement at any good plumbing supply store. Bring the old one with you and match it up.
There is no need to replace the body of the valve.
If the tank is bad, and needs replaced, that's one thing. If there is water leaking from the Spirovent, that's a whole 'nother issue, so I would say, Yes, they both need work... but replacing the entire Spirovent is probably not necessary.
http://www.spirotherm.com/docs/installation/JrIOM-A.pdf
You will of course need to drain the system unless you have valves positioned such that you can isolate that portion of the piping.
Here is a source of the vent head if it needs replaced:
Patriot Supply -
If the O-ring is damaged when taking it apart, you can likely find a proper replacement at any good plumbing supply store. Bring the old one with you and match it up.
There is no need to replace the body of the valve.
If the tank is bad, and needs replaced, that's one thing. If there is water leaking from the Spirovent, that's a whole 'nother issue, so I would say, Yes, they both need work... but replacing the entire Spirovent is probably not necessary.
#20
Member
Join Date: Mar 2011
Location: United States
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Spirovent/Bleeding
Great! I'll take the Spirovent out tomorrow and clean it to see if that works. At the end of the pdf link that you sent me it says that I have to do manual bleeding. How do I do that?
#21
I don't think it's a great idea to just jump into this... if you are going to drain the system to take the Spirovent apart and clean it, there is no point in not also replacing the expansion tank at the same time. It just doesn't make any sense at all to go to the trouble of draining to do the SV and then draining again to do the tank!
You need a STRAP WRENCH to get that top off the vent. If you try to use a plumbing wrench you will bugger it all up.
In order to properly answer this, we would need to see pictures of your system to see what valves you have where, so we can tell you which ones to turn when...
Take IN FOCUS, WELL LIGHTED, and LARGE ENOUGH TO SEE pictures (cell phone pics generally 5uck) and set up a free account at Image hosting, free photo sharing & video sharing at Photobucket and upload the pics to a PUBLIC album. Past a link to your album here for us to view.
We need to see, in addition to any close-up shots, several shots of the entire system taken from several angles. We need to see everything!
Please, don't jump into anything that you have the slightest doubt about being able to complete. We can't judge your skill set, only you can do that! We can tell you how, but don't be hasty.
You need a STRAP WRENCH to get that top off the vent. If you try to use a plumbing wrench you will bugger it all up.
I have to do manual bleeding. How do I do that?
Take IN FOCUS, WELL LIGHTED, and LARGE ENOUGH TO SEE pictures (cell phone pics generally 5uck) and set up a free account at Image hosting, free photo sharing & video sharing at Photobucket and upload the pics to a PUBLIC album. Past a link to your album here for us to view.
We need to see, in addition to any close-up shots, several shots of the entire system taken from several angles. We need to see everything!
Please, don't jump into anything that you have the slightest doubt about being able to complete. We can't judge your skill set, only you can do that! We can tell you how, but don't be hasty.
#23
Member
Join Date: Mar 2011
Location: United States
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks! But I was trying to separate the head from the spirovent and i'm having a hell of a time. Right now I'm using two pipe wrenches (one to keep the bottom from moving while I'm trying to loosen the head) but it just won't budge. Will two strap wrenches work better to get it loosened up?
#26
Member
Join Date: Mar 2011
Location: United States
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I do plan on replacing the tank and the Spirovent head (if needed). I have all of the parts ready to go. Here is a link showing my system:
Boiler - Windows Live
There are 3 zones (1- Main level, 2- master bedroom, 3- basement).
I was asking about the bleeding because once I have everything replaced I want to make sure I know everything to be done to get the system up and running.
Thanks for your help.
Boiler - Windows Live
There are 3 zones (1- Main level, 2- master bedroom, 3- basement).
I was asking about the bleeding because once I have everything replaced I want to make sure I know everything to be done to get the system up and running.
Thanks for your help.
#27
John, I've gotta head out for the evening, when are you planning on doing?
Maybe one of the other guys will be able to drop in and give you some pointers on bleeding out the system when yer done...
You sure that tank is actually bad? Looks pretty new to me... might just need an air charge... was there any water coming out the air valve on the bottom of the tank? (you might have told us already but I'm too lazy to go back and look)...
Maybe one of the other guys will be able to drop in and give you some pointers on bleeding out the system when yer done...
You sure that tank is actually bad? Looks pretty new to me... might just need an air charge... was there any water coming out the air valve on the bottom of the tank? (you might have told us already but I'm too lazy to go back and look)...
#28
Member
Join Date: Mar 2011
Location: United States
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I plan on replacing the tank and cleaning out the Spirovent head tomorrow. And I have a spare head just in case it needs to be replaced. The system is 11 years old. And no water was coming out of the air valve at the bottom of the tank. Only from the Spriovent head.
#29
In that case I'm betting that the tank is just fine... probably just needs a charge.
Check the air charge on the new tank before installing.
I'll try to check in tomorrow from the day job and see how yer doing...
Check the air charge on the new tank before installing.
I'll try to check in tomorrow from the day job and see how yer doing...
#30
Member
Join Date: Mar 2011
Location: United States
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Once I was able to get the head off everything was easy. I cleaned the head out and let it soak. But when I put it all back together it was still leaking water. I then replaced the the head and everything worked just fine.
For the tank it would not hold a charge. So I just replaced it with the new tank.
Everything is working fine and I have heat in all three zones. Thanks for you help!
For the tank it would not hold a charge. So I just replaced it with the new tank.
Everything is working fine and I have heat in all three zones. Thanks for you help!