EDR calculations

Reply

  #1  
Old 03-03-11, 10:55 AM
B
Member
Thread Starter
Join Date: Oct 2009
Location: USA
Posts: 13
Received 0 Votes on 0 Posts
EDR calculations

I'm replacing my oil fired steam boiler with a gas fired one. I have read over and over to properly size it. My plumber suggested a Burnham Independence model IN6. I decided to calculate the EDR values myself.
I have 6 radiators 36"tall by 9" deep, between 4-9 sections. I also have one steam Iron baseboard radiator 8' long. Through my calculations, I have determined my total sq. ft. EDR to be 191.
Looking at the spec. sheet, the IN6 steam sq. ft. rating is 450. A couple of questions:

1) Could my plumber have been that far off?
2) Does my calculation of 191 sound reasonable?
3) Am I looking at the right specs? Multiplying by 240 gives me 45,840.

The spec sheet lists:
1) Input MBH
2) DOE Heating Capacity
3) Steam MBH
I have read there's a factor of 1.3 or 1.5 to cover all the mains and risers, I'm just not sure which is the best number to try and match.
It's a simple 1920's single pipe steam system with a 40+ year old Weil-McClein boiler I can't read the model #.
Any thoughts would be very helpful. Thanks in advance.
 
Sponsored Links
  #2  
Old 03-03-11, 11:19 AM
D
Member
Join Date: Aug 2009
Location: USA
Posts: 4,946
Received 0 Votes on 0 Posts
Compare the size of your old boiler to the size of the one being suggested by your plumber. He may be just matching the size to the old one. You calcs don't sound too far off to me. I have 10 radiators with a total of 571 sq ft EDR. Now mine are all tube type and yours are column type. The tube type have more surface area as well.
 
  #3  
Old 03-03-11, 11:39 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
1. Probably

2,3. I think so.

Sounds like the IN4 is a better fit.

disclaimer: I'm steam-stupid, so don't trust me (or your 'plumber', because my bet is he's steam-stupid too! It's real good that you are verifying this info!)

How many square feet are you heating again?
 
  #4  
Old 03-03-11, 02:00 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,251
Received 23 Votes on 21 Posts
This may help in calculating the existing EDR. U.S. Boiler::Sizing Obsolete Radiation - Cast Iron Radiators
 
  #5  
Old 03-03-11, 03:03 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Posts: 2,481
Received 5 Votes on 4 Posts
Always size a steam boiler on the sq ft of steam. Verify the steam mains are insulated in the basement and do not add anything for piping. It is already in there.
For more steam info see FAQ in the upper left of this link.
Technical Menu
 
  #6  
Old 03-04-11, 10:30 AM
B
Member
Thread Starter
Join Date: Oct 2009
Location: USA
Posts: 13
Received 0 Votes on 0 Posts
thanks

Thanks to all for your responses. I'm feeling good about my value of 191 and getting a grip on all the other numbers.

I'm thinking the IN4 model would be sufficient:
DOE:87
Steam MBH:65
Steam sq.ft.:271
Does the fact that I have 2 10' hot water baseboards on a loop in the basement effect my needs? If so will the IN4 still cover it?
 
  #7  
Old 03-04-11, 05:16 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Posts: 2,481
Received 5 Votes on 4 Posts
If your numbers are correct you should be good. Why don't you supply me with the info on the radiators and I can double check them.
Please private message me the info.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: