Honeywell L8124A Aquastat

I have an oil hot water furnace with a "summer/winter" hookup, meaning it also provides domestic hot water. The Aquastat controller is getting 120 volts in, but there is no power coming out for the burner motor or the circulator when the thermostat is set to demand heat. My guess is the thermostat transformer is burnt out. What is the replacement information for the thermostat transformer?
 
Sponsored Links
  #2  
Old 05-14-11, 12:54 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,081
Received 13 Votes on 11 Posts
The transformer is not field replaceable & likely not the problem. Disconnect the thermostat wires from the aquastat & check for 24 volts AC between the terminals. If you have 24 VAC, the transformer is good. Install a jumper across the T-T terminals & see what happens. If the relay(s) pull in & the circulator & burner run, the problem is either in the thermostat or it's wiring.
 
  #3  
Old 05-15-11, 09:54 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
When you say 'thermostat transformer', then perhaps you have a separate transformer with electric zone valves? If you have zone valves, it's more likely a problem with one of those. Need more info...
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: