Tekmar 260 problem

I'm having a problem with my 260. I just re-piped my DHW tank and in the process changed from a ZV to a Taco 007 for the tank. The 260 will not turn the DHW pump on. According the 260 literature when terminals 3 & 4 get voltage (27 Vac in my case) it closes contacts 9 & 10 to start the pump. Terminal 9 & 10 read zero Vac. The burner fires as normal and if I remove the 27 Vac from terminal 3 & 4 the burner will shut down like it should. The dip switch is set to DHW pump. I know the pump is good, I plugged directly into a nearby recepticle and it ran. Am I doing something wrong or could the 260 be bad. The 260 has worked for several years with a DHW valve.
 
Sponsored Links
  #2  
Old 07-23-11, 11:01 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
Do you have the H and N from the pump wired directly to 9 and 10 ? Won't work...

From the I&O for the 260 http://tekmarcontrols.com/media/literature/260_d_06.pdf

DHW Pump / Valve Contact
The DHW Pmp / Vlv terminals (9 and 10) are an isolated output in the 260. There is no
power available on these terminals from the control. These terminals are to be used
as a switch to either make or break power to the DHW pump or DHW valve. Since this
is an isolated contact, it may switch a voltage between 24 V (ac) and 240 V (ac).

-----------------------

In other words, the AC neutral goes right to the pump, the AC HOT goes to 9 (or 10) and the Hot to the pump goes to 10 (or 9) ...
 
  #3  
Old 07-23-11, 12:04 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: Pennsylvania
Posts: 2,452
Received 2 Votes on 2 Posts
What Trooper is saying is supply 120v to terminal 9 and the hot to the pump to 10. Than you will also need to get a neutral to the pump.
 
  #4  
Old 07-23-11, 06:59 PM
Member
Thread Starter
Join Date: May 2006
Location: Sparta, NJ
Posts: 169
Received 0 Votes on 0 Posts
Success !! After wiring as stated above the pump started as required. I assumed the DHW pump would wire up like the main pump. So much for assuming, right ? Now its time to insulate the pipes, thanks so much for the help.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: