Shared pipe sizing

I'm planning on adding a zone for an indirect water heater to my current 1 zone setup. I will be piping the indirect with 1" pipe and it will be wired for priority. The current zone is 3/4" and at most I will be adding 1 more 3/4" zone in the future. Is it ok to pipe the shared piping with 1" pipe since the indirect will be on priority?
 
  #2  
Old 08-09-11, 04:01 AM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,407
Upvotes: 0
Received 64 Upvotes on 54 Posts
Yes it is OK. You can supply 2-3/4" zones off of one 1" pipe. What is the DOE output of the boiler?
 
  #3  
Old 08-09-11, 04:53 PM
D
Member
Thread Starter
Join Date: Sep 2009
Location: Rhode Island
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
The DOE output is 100,000.
 
  #4  
Old 08-09-11, 06:37 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,407
Upvotes: 0
Received 64 Upvotes on 54 Posts
Your boiler will probably be short cycling due to being over sized. A 3/4" pipe can carry about 40,000 btu's but may release less than that dependent on the amount of radiation. If the 3/4" loop has 50' of baseboard @ a water temp of 180f will get rid of approximately 30k btu's with a DOE of 100k. The indirect will give you a decent run time.
 
  #5  
Old 08-11-11, 06:39 PM
D
Member
Thread Starter
Join Date: Sep 2009
Location: Rhode Island
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
I believe you are correct with the boiler short cycling. The boiler is only 10 years old so it is not going anywhere. The reason for asking the initial question about shared pipe size is that I was going to reconfigure the boiler to pump away from the boiler and add a good air eliminator. The 1" air eliminators seem to be significantly cheaper than a 1 1/2" model. If necessary I will go ahead and keep the shared piping at 1 1/2".
 
  #6  
Old 08-11-11, 06:58 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
I don't think keeping the 1-1/2 is going to prevent any short cycling... I think what rbeck is saying is that with two small zones pulling heat out of a 'too large' boiler that they won't be able to move the heat to the home as fast as the burners are putting the heat back into the water. It might be a bit 'ghetto', but you could leave most of the 1-1/2 in place and just reduce down to 1" for the rework, then back up again to 1-1/2.
 
  #7  
Old 08-11-11, 07:11 PM
D
Member
Thread Starter
Join Date: Sep 2009
Location: Rhode Island
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
I was thinking about going from the current 1 1/2" supply pipe into a 1" air eliminator and continue with 1" into each of the pumps.
 
 