Hello,

I'm new to the forum.

I have removed the iron pipes from my 100+ year old house and replaced with 3/4 pex. The old system was a "branching" type, with one pipe coming from the boiler, then branching into three and then branching once more before reaching each radiator. I replaced that with two 1" copper manifolds with 3/4" outlets/inlets. Each radiator now has its own supply and return directly back to the manifolds (with valves).

My question is, do I need to replace the pump? It is not very old but it seems bigger than the ones I've seen in other manifold systems. I am not changing te size or number of radiators.

Please help - winter is coming!

John in Toronto
 
Sponsored Links
  #2  
Old 10-11-11, 06:51 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Posts: 2,481
Received 5 Votes on 4 Posts
What size boiler and what is the heat loss?
 
  #3  
Old 10-12-11, 06:49 AM
P
Member
Thread Starter
Join Date: Oct 2011
Location: Canada
Posts: 5
Received 0 Votes on 0 Posts
The boiler is 117000 BTUs. As for heat loss - well it's a 2000 ft2 house with almost no insulation and some original windows. In any case, the heating was sufficient before I made the switch. I am just wondering if the change in piping will require a different pump.

John
 
  #4  
Old 10-12-11, 07:21 AM
G
Member
Join Date: Oct 2008
Location: USA
Posts: 2,981
Received 11 Votes on 11 Posts
What's the pump manufacturer and model number?

Sizing a pump, if you want to do it in a theoretically correct way, is tricky - and much more info would be needed than you provided. I would leave the pump alone and see if it performs satisfactorily. If it's way oversized, there will be flow noise in the piping system. Changing the pump later wouldn't be a major task provided you have isolation valves on each side of the pump (otherwise you'd have to drain the system). If you don't have such valves, now would be a perfect time to install them - use full-port ball valves.

If you post some photos, we might get a better idea of your situation.
 
  #5  
Old 10-12-11, 12:34 PM
P
Member
Thread Starter
Join Date: Oct 2011
Location: Canada
Posts: 5
Received 0 Votes on 0 Posts
It's an Armstrong (model E6312?). The following is written on it: 3.6 FLA, 1.75 SF, 4.7 SFA, 48 FR, 1/6 HP, 50 AMB.

I have 10 runs of 3/4" pex serving 10 rads in a 3 story house. The longest run is about 30'.

I ran the system and there was some noise. I also noticed the supply pipe was only lukewarm after a couple of minutes of running. Usually it heats up much faster.

John
 
  #6  
Old 10-12-11, 01:04 PM
G
Member
Join Date: Oct 2008
Location: USA
Posts: 2,981
Received 11 Votes on 11 Posts
Your system is probably air locked. You'll need to stop running the pump before you damage it, and vent the air. Photos would help us suggest how if you are unsure. Show near-boiler piping, expansion tank, air elimination devices, and any fittings on the ends of the radiators. What does the pressure and temp gauge show on the boiler?

Couldn't find the model number at armstrongpumps.com

Did you use special oxygen barrier PEX? I hope so.
 
  #7  
Old 10-12-11, 05:14 PM
P
Member
Thread Starter
Join Date: Oct 2011
Location: Canada
Posts: 5
Received 0 Votes on 0 Posts
I asked a heating guy to come over tomorrow. He converted my neighbour's place to pex. I did use the oxygen barrier pex, btw.

I will let you know what he says.

John
 
  #8  
Old 10-13-11, 05:11 PM
P
Member
Thread Starter
Join Date: Oct 2011
Location: Canada
Posts: 5
Received 0 Votes on 0 Posts
So...it turns out that there are some air locks. I did everything correctly but I did not realize that dips in the line could trap air and cause problems. I am in the process of removing the dips and purging the system. The pump is a good size for the system. If you have any tips for me before I finish the job, they would be most welcome.

Will let you know how it goes.

John in Toronto
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: