We just had our Hot water heating system replaced with a Burnham. Used the system for a few days, and now I noticed the pressure relief valve had spilled some water.
After a week of trying to reach the plumber that installed the system, unfortunately, I found out that he got hurt and is hospitalized for about a month. I explained to him what was going on, and he emailed back that we have to replace the Expansion tank to a size 60, or add another 30 size tank to the existing tank.

The house is about 2500 s.f. It has 8 good sized cast-iron radiators, and the whole second floor is Baseboard (fin type). The system is 115,000 BTU.

Does this sound right? Do we need the 60 size tank, and would that solve the issue of leaking water when hot.

Thanks,
Buzzy
 
Sponsored Links
  #2  
Old 10-26-11, 11:27 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,894
Received 25 Votes on 23 Posts
Hi,

That would be correct, I would say a 60 size.

Possibly a 90 size if large amounts of water.

Here is some data.

http://www.amtrol.com/media/document...OLbrochure.pdf

http://www.amtrol.com/media/document..._EXTROL_IO.pdf


Make sure you secure it properly. Straps...etc... Those suckers get heavy when they fail.

Mike NJ
 

Last edited by NJT; 11-18-11 at 05:43 PM.
  #3  
Old 10-27-11, 05:00 PM
Member
Join Date: Aug 2009
Location: USA
Posts: 4,947
Received 0 Votes on 0 Posts
It would be a good idea to add a few things to your expansion tank pipe when you change it. If you don't already have one, add a ball valve so you can isolate it from the rest of the system for maintenance. Next, add a tee after the ball valve. Put a length of pipe with a hose bib at the end. The idea of this is so you can check your tank pressure every year easily. You shut off the ball valve and open the hose bib to bring the pressure down to 0. You need to the pressure at 0 to properly check the air charge in the expansion tank. The pipe with the hose bib should be long enough so you can put a bucket under it to catch the water. You could also attach a hose to it. More water than you think will come out of there.
 
  #4  
Old 10-27-11, 05:45 PM
Member
Thread Starter
Join Date: Oct 2011
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Thanks a lot lawrosa and drooplug. It all makes sense, and I'll try to do all that you suggested.

Buzzy.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: