balancing heat output in different rooms (somewhat long)
#41
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 316
Upvotes: 0
Received 0 Upvotes
on
0 Posts
sminker, the carpet was between the fins and the back cover, not the face cover, so there was some circulation. the baseboards are in straight series.
PeterNH, no aluminum foil yet, i guess i will try the insulation first.
my wife mentioned that the cold bedroom was "hot", so maybe there is already some balance restored. i'm pretty sure with some insulation in the master bedroom it will turn out good!
PeterNH, no aluminum foil yet, i guess i will try the insulation first.
my wife mentioned that the cold bedroom was "hot", so maybe there is already some balance restored. i'm pretty sure with some insulation in the master bedroom it will turn out good!

#42
It does look as if things are 'disproportionate'. I'm really kinda surprised that you aren't also complaining about the bathroom, but it's probably got only one small exposed wall.
Let's do a bit of massaging of the numbers. I'm using 550 BTU/FT of fin-tube (conservative number, Slant Fin 30 is rated at 610 at 180 water, and 480 at 160 water).
Room --------area---radiation--BTU out---BTU/SQ FT
Master BR:--220 sq ft--18 FT---9900 BTU----45
Cold BR:----155 sq ft--11.6 FT--6416 BTU----41.4
The difference doesn't look that great. BUT the cold room is a corner, on the northeast, at the end of the loop. So it's all adding up to a cold room.
Has it got anything else going wrong for it? above an unheated garage or anything?
Rerun with 160 water for the cold room, because we know it has cooled some, using a very conservative number of 400 BTU/FT this time...
Cold BR:----155 sq ft--11.6 FT--4640 BTU----30
so there ya go... sure it's gonna be cooler!
Now, in general terms, 45 BTU per SQ FT is a LOT of heat. Most reasonably well constructed homes are under 30 BTU / SQ FT, and modern construction can be as low as 15-20 , my home uses about 25 (50s construction, lots of improvements).
So, it's doubtful that the overall problem is a lack of radiation, rather an imbalance of same. So it would seem that if you can easily add some element to the cold room, it would probably solve the problem. The designers failed at this installation to consider the heat loss of the rooms and the fact that the water would be cooler when it got to the end of the loop.
Let's do a bit of massaging of the numbers. I'm using 550 BTU/FT of fin-tube (conservative number, Slant Fin 30 is rated at 610 at 180 water, and 480 at 160 water).
Room --------area---radiation--BTU out---BTU/SQ FT
Master BR:--220 sq ft--18 FT---9900 BTU----45
Cold BR:----155 sq ft--11.6 FT--6416 BTU----41.4
The difference doesn't look that great. BUT the cold room is a corner, on the northeast, at the end of the loop. So it's all adding up to a cold room.
Has it got anything else going wrong for it? above an unheated garage or anything?
Rerun with 160 water for the cold room, because we know it has cooled some, using a very conservative number of 400 BTU/FT this time...
Cold BR:----155 sq ft--11.6 FT--4640 BTU----30
so there ya go... sure it's gonna be cooler!
Now, in general terms, 45 BTU per SQ FT is a LOT of heat. Most reasonably well constructed homes are under 30 BTU / SQ FT, and modern construction can be as low as 15-20 , my home uses about 25 (50s construction, lots of improvements).
So, it's doubtful that the overall problem is a lack of radiation, rather an imbalance of same. So it would seem that if you can easily add some element to the cold room, it would probably solve the problem. The designers failed at this installation to consider the heat loss of the rooms and the fact that the water would be cooler when it got to the end of the loop.
#43
I believe we need to pay attention to an accurate to the system delta-T since this room is at the end of the loop. We already know the heat loss is greater propionate to the other rooms. Maybe the water is flowing too slow. If the delta-T is too great and we speed the water to reduce the delta-T we will get more heat out of the radiation even at the end of the loop where this room is. Increase flow get more heat, decrease flow get less heat.
This is only correct if it is a pot on the stove at sea level. A heating system at 12 psi the boiling point of water is 236f. Raise the pressure raise the boiling point. Any cast iron boiler can operate to 210f safely. I am not saying to do this but I know there are systems that need to run there in extreme cold temps. I also have some systems at 240f but at higher water pressure due to under-radiated buildings. This 240f is not safe without the proper calculations. Cast iron boilers according to ASME code are rated at a max operating temp of 250f, again this is for information purposes, I am not saying to do this.
water boils at 212F he's too high on his temperature setting
#44
Member
Join Date: Feb 2011
Location: US
Posts: 522
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I don't believe this has had a definitive answer, although it seems not to be a problem.
Peter
#46
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 316
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Has it got anything else going wrong for it? above an unheated garage or anything?
So it would seem that if you can easily add some element to the cold room, it would probably solve the problem
Way back early in this thread, the issue was raised, by NJT, about the possiblility of there being some air in the pipes upstairs.
I don't believe this has had a definitive answer, although it seems not to be a problem.
I don't believe this has had a definitive answer, although it seems not to be a problem.
I'm still kinda hoping that Diver is going to get some reasonably accurate measurements of the supply and return temps from the loop... it's a very real possibility.
well, at least i can say that i'm already seeing some improvment - when heat is on, it seems that the cold room temp now overshoots a bit a temp in the warm room. i will add some pipe insulation to the warmer room for more pronounced effect and adjust the tstat and i think i might be done. these are the things that were done in the cold room:
carpet tucked behind the back section of the baseboard instead of in front of the back
damper removed
fins vacuumed
furniture moved a way a bit
i think the main remaining issue is that cold room does not retain heat as good as the master bedroom. besides adding/improving wall insulation, everything else was already done.
i'm still not sure if i should lower the boiler temp. it's a cast iron boiler and i would guess it was running as is for all its life, which is almost 30 year now

#47
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes
on
0 Posts
even that would cut some of the BTUs into the room on the back fin section getting the convection up thru the baeboard.suggestion which is a pain in the A** cut all the carpet so it hits the wall and lays flat doesn't curl up..do a room a weekend and it will make a difference.so your in series on the supply from the boiler as you go along the temps should drop on the line as it passes thru the rooms as the room pulls on the heat should never rise.how is the height on the space from the floor to the bottom of the kick panel that snaps on same all around....
#48
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes
on
0 Posts
something stupid to check but have to ask check this Slant-Fin video,and see how the flat parts of the fin and tube is slid in so the open fins are top and bottom and the flat bend is front and back you shouldn't be looking at straight fins when the kicker is removed Slant/Fin Baseboard Installation - YouTube
#49
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 316
Upvotes: 0
Received 0 Upvotes
on
0 Posts
sminker, i already cut the carpet (pain) and tucked it behind. the fins are oriented vertically so the air passes thru.
the biggest problem is the retention of the heat it seems, even though it gets warmer when the heat is on, it cools a lot faster in that room.
the biggest problem is the retention of the heat it seems, even though it gets warmer when the heat is on, it cools a lot faster in that room.
#50
is there anything i can do to check for lazy flow, air traps, etc?
Other than that, the only thing you could really do is to 'purge' the zone and see if things improve, but I don't advocate doing that just yet without knowing if it needs to be done. Your system may not be set up with appropriate valving to do this easily anyhow.
Since you've seen a marked improvement already, one would have to assume that the airflow through the baseboards was a big part of the issue. There's nothing that any further changes to the heating system can do to remedy the heat loss in the room... so you may be about as good as you can get at this point.
still not sure if i should lower the boiler temp.
is there such a thing as a snap on fin element?

#51
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 316
Upvotes: 0
Received 0 Upvotes
on
0 Posts
NJTrooper, the original house owner has the pilot on all summer long. i turned it off last summer and plan on doing it again from now on. i read somewhere on this forum that having the pilot on all the time makes sure that the heat exchanger is always hot and that prevents the condensation. the boiler is in the unfinished part of the basement and it's humid there (i do run the dehumidifer on and off in the summer but not all the time), usually about 70% rh. so things get rusty there. i wonder if the fact that the pilot was on contributed to the long life of the boiler? it's going to be 30 years next year. am i making a mistake by turning the pilot off? the boiler is cast iron.
thank you for all you help.
#52
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes
on
0 Posts
residential companies always say that about a pilot running in the summer keeps the boiler from condensating...they just don't want to go around lighting 5000 pilots in the fall.unless your feeding cold water in your not going to condensate the last heating cyce of th eyear will temper it right into the summer ambient temps...on the colder rooms heating up but not holding it might check all the walls just above the baseboard next windy cold night even with the BB running might see drafting or missing insulation with the hotter rooms something is pulling on that baseboard temp 180F supplied..I gOT IT move the stat into the colder rooms and adjust the warmer ones what the hell it's worth the mention...kidding have a good X-MASS
#53
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 316
Upvotes: 0
Received 0 Upvotes
on
0 Posts
why not? it's easy money...
#54
It definitely IS possible for dew to form in and on a boiler in the summer. When the temp and humidity increase faster than the water that is in the system can warm up, and the water in the system is below the dew point, of course dew will form.
I do think that the pilot burning will help to keep the boiler guts dry in the summertime... but will it actually do anything to promote longevity of the unit? maybe... or maybe not...
If I had a pilot light, I would keep it on... but that's just me, and I've been known to keep a 25 watt lamp inside my oil burner combustion chamber during the summer, on a dimmer... way down low... but again, that's just me... kinda AR about some stuff.
I do think that the pilot burning will help to keep the boiler guts dry in the summertime... but will it actually do anything to promote longevity of the unit? maybe... or maybe not...
If I had a pilot light, I would keep it on... but that's just me, and I've been known to keep a 25 watt lamp inside my oil burner combustion chamber during the summer, on a dimmer... way down low... but again, that's just me... kinda AR about some stuff.
#55
I just googled around some... and the answers on the internet are all over the place... throwing out the ones that have no creds, like any from answers.yahoo.com, and focusing on the ones from people that sell and service gas appliances, the answers are STILL all over the place, and good reasoning on both sides.
The pilot will cost a few bucks a month to keep running.
It MAY actually CONTRIBUTE to condensation in the appliance... one of the byproducts of burning gas is WATER. If the pilot is not big enough to keep the interior warm enough, that water from the combustion will condense inside the boiler.
Which is more harmful for a thermocouple? To keep it hot all the time? or to let it cool in the off months and then reheat in fall? Dunno...
Will not having the pilot lit encourage spiders to nest in the unit and clog up the orifices? Dunno... maybe... happens all the time with my gas grill.
You are never more than 3' from a spider.
Up to you... keep a thermocouple on hand as a spare, and learn how to clean the gas orifices.
Oh by the way... don't ask the gas company, they want to sell gas so they will definitely tell you to leave it on. They want that $5 a month from all the customers.
The pilot will cost a few bucks a month to keep running.
It MAY actually CONTRIBUTE to condensation in the appliance... one of the byproducts of burning gas is WATER. If the pilot is not big enough to keep the interior warm enough, that water from the combustion will condense inside the boiler.
Which is more harmful for a thermocouple? To keep it hot all the time? or to let it cool in the off months and then reheat in fall? Dunno...
Will not having the pilot lit encourage spiders to nest in the unit and clog up the orifices? Dunno... maybe... happens all the time with my gas grill.
You are never more than 3' from a spider.
Up to you... keep a thermocouple on hand as a spare, and learn how to clean the gas orifices.
Oh by the way... don't ask the gas company, they want to sell gas so they will definitely tell you to leave it on. They want that $5 a month from all the customers.
#56
One more thought... if the pilot uses 750 BTU/HR... and it ran on fuel oil, it would use about a gallon a week to keep it going. That's almost $20 a month!
I know natgas is cheaper... but still... yikes!
Do you know how much you pay per therm?
I know natgas is cheaper... but still... yikes!
Do you know how much you pay per therm?
#57
Member
Join Date: Feb 2011
Location: US
Posts: 522
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I vote for the light bulb.
No water vapors. Hot and Dry.
Even at the full 25 watts,
at 14 cents a KW,
if i did my math right,
comes out about $2.50 month.
15 watts, $1.50
Peter
No water vapors. Hot and Dry.
Even at the full 25 watts,
at 14 cents a KW,
if i did my math right,
comes out about $2.50 month.
15 watts, $1.50
Peter
#58
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 316
Upvotes: 0
Received 0 Upvotes
on
0 Posts
i do, but the price is not straightforward. here is the latest with winter rate (this is my actual bill from mid november till mid december):
97therms overall (heat + hot water)
Customer Charge $11.15
Distribution Charge
First 50.00 Therms x $0.3044 $15.22
Next 47.00 Therms x $0.3546 $16.67
Delivery Adjustment Charge
All 97.00 Therms x $0.0945 $9.17
Decoupling Adjustment
All 97.00 Therms x -$0.0147 $1.43
Cost of Gas
All 97.00 Therms x $0.7929 $76.91
Total Charges for Service This Period $127.69
summer charges: (hot water, mid july to mid august)
11 therms overall
First 10.00 Therms x $0.3044 $3.04
Next 1.00 Therms x $0.3546 $0.35
Delivery Adjustment Charge
All 11.00 Therms x $0.0917 $1.01
Decoupling Adjustment
All 11.00 Therms x $0.0270 $0.30
Cost of Gas
All 11.00 Therms x $0.5275 $5.80
Total Charges for Service This Period $21.65
97therms overall (heat + hot water)
Customer Charge $11.15
Distribution Charge
First 50.00 Therms x $0.3044 $15.22
Next 47.00 Therms x $0.3546 $16.67
Delivery Adjustment Charge
All 97.00 Therms x $0.0945 $9.17
Decoupling Adjustment
All 97.00 Therms x -$0.0147 $1.43
Cost of Gas
All 97.00 Therms x $0.7929 $76.91
Total Charges for Service This Period $127.69
summer charges: (hot water, mid july to mid august)
11 therms overall
First 10.00 Therms x $0.3044 $3.04
Next 1.00 Therms x $0.3546 $0.35
Delivery Adjustment Charge
All 11.00 Therms x $0.0917 $1.01
Decoupling Adjustment
All 11.00 Therms x $0.0270 $0.30
Cost of Gas
All 11.00 Therms x $0.5275 $5.80
Total Charges for Service This Period $21.65
#59
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 316
Upvotes: 0
Received 0 Upvotes
on
0 Posts
i might come back here for some directions

as for thermocouple, should i get one to keep on hand right now?
#60
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes
on
0 Posts
if you want to pack the cold rooms with more fins have santa bring you a 5' lenght of Slant-Fin slip the elements off cut the tin sharp side and pinch them in..on cleaning that rusted cover is the only way in get a long bristle brush from a boiler supply place they have all lenghts.remove the burner run outs push in and pull up over orifice one with the pilot might have to stay then brush away let it all fall down if it is just light rust your good to go.remove that insulation off the circulator they run hot need air around them..can't go in the top of the boiler it is sealed the burner is the only access to brush up..should burn blue and straight...tap jets with screw driver handle after cleaning with heat running.air inlets on the burner tubes should be screwed in...and fixed adjust one you'll see it starve the burner and go yellow which makes black soot....once you add fins and clear the baseboard i would consider dropping that 180F to much for 70F setpoints on stats...160-170 tops...get back on those walls during a cold windy night see that readings...might ask santa for a laser thermometer..SEARS Hardware cheap and convient hang it on a hook
#61
jeeze, punctuate much?
I believe the 'hood' on this boiler lifts off...
Those fins need a good tight factory contact with the pipe to work as designed and they are very flimsy metal. Once you cut through to bend and slip them on, for all the trouble, you are wasting your time and money. If you are going to do anything, cut the dang pipe and solder in the new piece...
Yes.
Never a bad idea really... they always seem to go bad at the most inconvenient time.
can't go in the top of the boiler
slip the elements off cut the tin sharp side and pinch them in
should i pull those out first and give them some cleaning?
as for thermocouple, should i get one to keep on hand right now?
#62
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Cold rooms are a hassle.
Get in the attic above the cold room. Pull up the insulation. Air seal all penetrations in the top plates, and even along the top plates themselves. The 2-part foams in the larger canisters are good for this. After reinstalling the insulation, consider adding a few inches of cellulose on top.
Make sure any outlets or other wall penetrations in the cold room are gasketed and/or caulked.
Also feel for drafts around where the baseboard pipes go into the floor. But be careful about sealing these; you don't want to limit expansion and cause rubbing or banging.
The foil around the fins works wonders. Fin-tube works mostly by convection through the fins. The foil not only stops the convection, but also creates dead air space around the pipe.
I like the idea of increasing flow rate in case this is a deltaT problem.
Get in the attic above the cold room. Pull up the insulation. Air seal all penetrations in the top plates, and even along the top plates themselves. The 2-part foams in the larger canisters are good for this. After reinstalling the insulation, consider adding a few inches of cellulose on top.
Make sure any outlets or other wall penetrations in the cold room are gasketed and/or caulked.
Also feel for drafts around where the baseboard pipes go into the floor. But be careful about sealing these; you don't want to limit expansion and cause rubbing or banging.
The foil around the fins works wonders. Fin-tube works mostly by convection through the fins. The foil not only stops the convection, but also creates dead air space around the pipe.
I like the idea of increasing flow rate in case this is a deltaT problem.
#63
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 316
Upvotes: 0
Received 0 Upvotes
on
0 Posts
xiphias, all those things were done last year. the only thing left is to do/redo insulation in the walls, but that would require either ripping the walls from inside or cutting holes in them from inside or outside.
NJTrooper,
i got good readings on the temps, black electrical tape does work wonders. the beginning of the loop read 191.5 and the the end of the loop in the cold room was 189.5. suspiciously close. but i guess i don't have a lazy flow problem...
NJTrooper,
i got good readings on the temps, black electrical tape does work wonders. the beginning of the loop read 191.5 and the the end of the loop in the cold room was 189.5. suspiciously close. but i guess i don't have a lazy flow problem...
#64
cutting holes in them from inside or outside.
the beginning of the loop read 191.5 and the the end of the loop in the cold room was 189.5. suspiciously close.
I think we can conclude that you don't have an air (or other, like a potato chip bag) blockage in the loop.
#65
Are you absolutely certain that the system is piped the way you believe it is? Can you actually SEE the pipe the entire way around the loop? It doesn't disappear into the floor and emerge again?
How about down at the boiler? Can you identify the supply and return for that loop? What do the temps measure there?
How about the in and out from each fin-tube element? can you get incremental readings around the loop?
For a 2° delta T across a loop with that much fin-tube installed, it is darn near impossible to have THAT MUCH flow !
Using say 600 BTU/FT of element, you have 52 feet installed, that's about 32K BTU.
If you were flowing 3.2 GPM you would have a 20° delta T on that loop. Since the relationship is relatively proportional, a 2° DT would mean you are flowing something like 30-ish GPM!
No... impossible... 30 GPM in a 3/4" pipe? I have to question that IR temp gun's accuracy.
How about down at the boiler? Can you identify the supply and return for that loop? What do the temps measure there?
How about the in and out from each fin-tube element? can you get incremental readings around the loop?
For a 2° delta T across a loop with that much fin-tube installed, it is darn near impossible to have THAT MUCH flow !
Using say 600 BTU/FT of element, you have 52 feet installed, that's about 32K BTU.
If you were flowing 3.2 GPM you would have a 20° delta T on that loop. Since the relationship is relatively proportional, a 2° DT would mean you are flowing something like 30-ish GPM!
No... impossible... 30 GPM in a 3/4" pipe? I have to question that IR temp gun's accuracy.
#67
Not without spending a ton of money. The ones that I've used have all been equally 5ucky.
The one I've got now is this Extech model,
42530 - Wide Range IR Thermometer
which is 'ok'... in other words, as bad as any. I think it's about $75 or so. I have no great love of these IR guns, but they do have their place.
If you've got a meat thermometer, slip a piece of insulation around the pipe and put the thermometer inside the insulation. This would be a cheap way to at least somewhat verify the gun.
OH YEAH, I keep forgetting to say this... I think it might have been sminker who wrote to remove the cotton candy from the pump. As he said, those motors run hot and need air around them. You risk burning up the motor with that insulated.
What's inside the big glom of insulation between the water heater and the boiler?
The one I've got now is this Extech model,
42530 - Wide Range IR Thermometer
which is 'ok'... in other words, as bad as any. I think it's about $75 or so. I have no great love of these IR guns, but they do have their place.
If you've got a meat thermometer, slip a piece of insulation around the pipe and put the thermometer inside the insulation. This would be a cheap way to at least somewhat verify the gun.
OH YEAH, I keep forgetting to say this... I think it might have been sminker who wrote to remove the cotton candy from the pump. As he said, those motors run hot and need air around them. You risk burning up the motor with that insulated.
What's inside the big glom of insulation between the water heater and the boiler?
#68
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 316
Upvotes: 0
Received 0 Upvotes
on
0 Posts
OH YEAH, I keep forgetting to say this... I think it might have been sminker who wrote to remove the cotton candy from the pump. As he said, those motors run hot and need air around them. You risk burning up the motor with that insulated.
What's inside the big glom of insulation between the water heater and the boiler?
What's inside the big glom of insulation between the water heater and the boiler?
the glom is the extension tank - it's also wrapped in insulation... should i remove that too?
#69
Oh that motor will get way hotter than the water! I would definitely remove it from the pump.
I guess the expansion tank is OK, but there won't be any heat loss from it, only the top of the tank will have hot water in it, and only when the pressure is up... but it won't hurt it.
I guess the expansion tank is OK, but there won't be any heat loss from it, only the top of the tank will have hot water in it, and only when the pressure is up... but it won't hurt it.
#71
I would say you pay about $1.25 per therm. The customer charge doesn't figure into it because if you use 0 therms, you still have to pay for it. As far as charges for the first 50 and then anything over, always go with the anything over rate. I am paying about the same as you here in NJ right now.
#72
I did some googling on nat gas prices the other day then forgot to come back here and report...
Looks like national average is a bit over a buck / therm, but let's go with 'worst case' of $1.25 per, and a pilot running at 1000 BTU.
720 hours in a month (30 days)
X 1000 BTU
= 720K BTU
= 7.2 Therms
X 1.25
= $9.00 a month to run the pilot.
If the pilot runs less BTU and your cost per therm is less, of course the bill will be less...
So let's say that a single pilot light would run between 5 and 10 bucks a month.
Makes a pretty good case for shutting 'er down in the summer!
Let's say ya stick a 25 watt bulb in there over the summer if yer worried about condensation:
$0.12 per KW/HR (maybe more, but that's what I'm paying now)
40 hours at 25 watts is a KW/HR
720 hours div by 40
= 18 KW/HR / Month
X 0.12
= $2.16 / month
But then, a 25 W bulb is only 85 BTU... so that small amount of heat may not be enough to make any difference anyway.
To get to 1000 BTU you would need a 293 W bulb!
= 211 KW/HR / Month
X 0.12
= $25.33
Can that be right? I think so... somebody check my brain. Droo, yer good at cipherin'... I'm using 3410 BTU / KW
Looks like national average is a bit over a buck / therm, but let's go with 'worst case' of $1.25 per, and a pilot running at 1000 BTU.
720 hours in a month (30 days)
X 1000 BTU
= 720K BTU
= 7.2 Therms
X 1.25
= $9.00 a month to run the pilot.
If the pilot runs less BTU and your cost per therm is less, of course the bill will be less...
So let's say that a single pilot light would run between 5 and 10 bucks a month.
Makes a pretty good case for shutting 'er down in the summer!
Let's say ya stick a 25 watt bulb in there over the summer if yer worried about condensation:
$0.12 per KW/HR (maybe more, but that's what I'm paying now)
40 hours at 25 watts is a KW/HR
720 hours div by 40
= 18 KW/HR / Month
X 0.12
= $2.16 / month
But then, a 25 W bulb is only 85 BTU... so that small amount of heat may not be enough to make any difference anyway.
To get to 1000 BTU you would need a 293 W bulb!
= 211 KW/HR / Month
X 0.12
= $25.33
Can that be right? I think so... somebody check my brain. Droo, yer good at cipherin'... I'm using 3410 BTU / KW
#73
Member
Join Date: Feb 2011
Location: US
Posts: 522
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ya NJ Trooper, your math is right.
I think there is a but.
The pilot may have many more btu's but i don't understand why the pilot , is not doing a micro job of flue gas condensation.
Matter of fact, it would almost seem the pilot would do significantly more harm than good.
So a 25 watt bulb, while many times less btu's, is totally dry heat, and may be all that's needed.
Peter
I think there is a but.
The pilot may have many more btu's but i don't understand why the pilot , is not doing a micro job of flue gas condensation.
Matter of fact, it would almost seem the pilot would do significantly more harm than good.
So a 25 watt bulb, while many times less btu's, is totally dry heat, and may be all that's needed.
Peter
#74
My first check on your math is the rate you pay for electricity. It's more like .16 per KWH. You forgot the delivery charge. 
I'm not sure I understand why there is such concern about condensation on the boiler during the summer. My basement has a moisture problem. I have never witnessed any of my pipes, domestic supply or hydronic heating, have condensation on them anytime during the year. The only time I saw a problem between metal and water vapor in my basement is when I left a scrap of 2x4 on my table saw for a couple weeks. One day I picked up the scrap and saw the table had rusted underneath. No where else was there rust but under the 2x4. Now, was this because of moisture in the air or in the 2x4? I don't know for sure. But I do know that everywhere air is able to come into contact with the surface, I don't have a problem with rust.
Now lets suppose there is some level of condensation happening inside the heat exchanger despite my observations. Where does the harm come form? The acidic nature of the soot stuck to the inside, right? The condensation alone isn't going to cause flaking rust which is the kind that is harmful. Surface rust will form a layer of protection against further corrosion. So if the acid from the soot is the most dangerous part of the equation, then get your boiler cleaned in the spring every year. I'd say you would get more value for those dollars spent than powering a light bulb of gas pilot.
By the way, I run a dehumidifier now.

I'm not sure I understand why there is such concern about condensation on the boiler during the summer. My basement has a moisture problem. I have never witnessed any of my pipes, domestic supply or hydronic heating, have condensation on them anytime during the year. The only time I saw a problem between metal and water vapor in my basement is when I left a scrap of 2x4 on my table saw for a couple weeks. One day I picked up the scrap and saw the table had rusted underneath. No where else was there rust but under the 2x4. Now, was this because of moisture in the air or in the 2x4? I don't know for sure. But I do know that everywhere air is able to come into contact with the surface, I don't have a problem with rust.
Now lets suppose there is some level of condensation happening inside the heat exchanger despite my observations. Where does the harm come form? The acidic nature of the soot stuck to the inside, right? The condensation alone isn't going to cause flaking rust which is the kind that is harmful. Surface rust will form a layer of protection against further corrosion. So if the acid from the soot is the most dangerous part of the equation, then get your boiler cleaned in the spring every year. I'd say you would get more value for those dollars spent than powering a light bulb of gas pilot.
By the way, I run a dehumidifier now.

#75
The only time i have seen pilots cause flue gas condensation is larger water volume systems that have no flow checks so the water moves into and out of the boiler. By using multiple zones and zone valves or flow checks this usually is not a problem over the summer.To create condensation you need warm and cold. If there is no flow and the iron is room temp, the water is room temp where does the condensation come from?
All boilers today are built for cold start so this is not normally an issue. Heat is not the only way to keep things dry if you are concerned about this. Just moving air will dry things. If you are concerned with summer condensation on chimney vented products open the peep door and remove the burner access door on gas boilers to allow more airflow through them.
Remember standing pilot goes away on new equipment as of Sept 1 2012 as far as the manufacturing of them.Sales stop when they are gone.
All boilers today are built for cold start so this is not normally an issue. Heat is not the only way to keep things dry if you are concerned about this. Just moving air will dry things. If you are concerned with summer condensation on chimney vented products open the peep door and remove the burner access door on gas boilers to allow more airflow through them.
Remember standing pilot goes away on new equipment as of Sept 1 2012 as far as the manufacturing of them.Sales stop when they are gone.