Boiler has no pressure
Here are my pictures.
My guess, based on what I've read here, is it's the pressure regulating valve or the gate after the valve. I'm pretty handy, but have never had a boiler before this place. Any tips on how I might determine the faulty part would be greatly appreciated.
Thanks,
Justin
My guess, based on what I've read here, is it's the pressure regulating valve or the gate after the valve. I'm pretty handy, but have never had a boiler before this place. Any tips on how I might determine the faulty part would be greatly appreciated.
Thanks,
Justin
#2
Member
When did you first notice the pressure was zero? The valve you refer to, I think is ahead of the PRV, not after. Is the boiler still running, with heat? Tell us the pressure and temp reading on the boiler gauge.
#3
Member
Thread Starter
Join Date: Mar 2010
Location: US
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I can't say the pressure was ever not at zero, this is my first winter here. There is a lot of gurgling in the system, which I attribute to not enough water. The temp is currently at 180 with the system running and the pressure is at zero. The gate valve is definitely closer to the boiler than the PRV. I'm currently not getting a lot of heat out of the system, and it seems to be running near constantly. Do you know if there is a way to circumvent the PRV to get some water in the system for now, or is that a terrible idea?
Thanks,
Justin
Thanks,
Justin
#4
The gauge may not be working and you have other issues. That expansion tank looks like it has holes in it and should probably be replaced. Possibly the fill valve also. And a new air vent probably should be replaced. Heck change the gauge also.
I see another boiler there. Is this your boiler? Are you renting?
Let the landlord take care of it if you are.
Mike NJ
I see another boiler there. Is this your boiler? Are you renting?
Let the landlord take care of it if you are.
Mike NJ
#5
Member
Thread Starter
Join Date: Mar 2010
Location: US
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Unfortunately, I own the place and both boilers. My tenant's unit is okay for the moment. I'm pretty sure the pressure is correct, I get nothing when I attempt to bleed the radiators, even when they're hot. and they are heating up less and less, the heat barely comes up six inches on some of them.
#6
Member
Thread Starter
Join Date: Mar 2010
Location: US
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I got it. I took the strainer off the PRV and flushed that out, but that didn't fix anything. I ended up turning the gate ALL the way left (it was sticking) and it opened up and let the water flow. I now bled all the radiators and have pressure and heat! Thanks for your responses!!!
#7
I believe that you've tried to adjust that regulator too... because that screw is all the way in...
There IS a way to feed water in... there always is... but you must be EXTREMELY CAREFUL!
For one thing, you have no idea if the pressure gauge even works, so you could EASILY over-pressure the system with what I'm about to describe.
Next, if the boiler is HOT, DO NOT do this, you could shock the boiler and crack it...
TURN THE BOILER OFF AND ALLOW TO COOL TO 100°F OR LESS!
Is there a washing machine anywhere near there?
Do you have a garden hose?
Is there a boiler drain that works?
Connect the garden hose to the boiler drain.
Unscrew a hose from the back of the washing machine. Use the HOT... less chance of shocking the boiler. Connect the other end of the garden hose to the washing machine hose.
Open the washing machine valve first... only a little bit.
Next, slightly loosen the hose end at the boiler drain and let the air out of the hose. When you get water, screw the hose on tight.
VERY SLOWLY! open the boiler drain while watching the gauge pressure!
When you see the pressure come up to 15 PSI, close the drain valve, disconnect the hose.
If the pressure drops again, you've got a leak somewhere... but this might get you some heat until you can get that mess fixed... it appears to need a LOT of maintenance!
There IS a way to feed water in... there always is... but you must be EXTREMELY CAREFUL!
For one thing, you have no idea if the pressure gauge even works, so you could EASILY over-pressure the system with what I'm about to describe.
Next, if the boiler is HOT, DO NOT do this, you could shock the boiler and crack it...
TURN THE BOILER OFF AND ALLOW TO COOL TO 100°F OR LESS!
Is there a washing machine anywhere near there?
Do you have a garden hose?
Is there a boiler drain that works?
Connect the garden hose to the boiler drain.
Unscrew a hose from the back of the washing machine. Use the HOT... less chance of shocking the boiler. Connect the other end of the garden hose to the washing machine hose.
Open the washing machine valve first... only a little bit.
Next, slightly loosen the hose end at the boiler drain and let the air out of the hose. When you get water, screw the hose on tight.
VERY SLOWLY! open the boiler drain while watching the gauge pressure!
When you see the pressure come up to 15 PSI, close the drain valve, disconnect the hose.
If the pressure drops again, you've got a leak somewhere... but this might get you some heat until you can get that mess fixed... it appears to need a LOT of maintenance!
#9
Member
Thread Starter
Join Date: Mar 2010
Location: US
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'm going to get to the maintenance asap. Just getting moved in and already did a new roof, porch and plumbing/electrical. This is next on the list. But for now, looks like my expansion tank couldn't handle the pressure. The rusted spots are spraying water everywhere. I shut off the heat for the night, but I'm going to have to replace this in the morning. Can I buy these at Home Depot or do I need to find a heating & cooling place?
Thanks again!
Thanks again!
#11
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes
on
0 Posts
if you bleed the rads do it with the system off on the stat don't want the circulator running let the water auto feed pressure blled it shuld stop feeding at 12psi....verify that pressure guage and or replace it HD and Grainger
#12
Member

looks like my expansion tank couldn't handle the pressure. The rusted spots are spraying water everywhere.
By adjusting the pressure reg valve, you (or the previous owner) has likely gotten it out of whack. It needs to be returned to the original adjustment position, or replaced.
Seems like you may have some significant deferred maintenance.
#13
Member
Thread Starter
Join Date: Mar 2010
Location: US
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
That's interesting, truely. Because I replaced the tank this morning and now have a NEW problem, the pressure is getting a little too high and triggering the overflow valve (not sure of the term), to open up spilling yet more water all over my basement. My guess is that the PRV is set wrong, letting too much water into the system, the pressure gets above 30psi and the "overflow valve" opens up. My plan for the moment is to let the system cool down below 100, empty out some water, let it refill to 12 PSI cold and then shut off the water supply. I'm hoping that will get me through the night (why does this keep happening at night?), and in the morning I can get a new PRV. What do you think of that plan?
thanks again for all the replies on this thread, it's been extremely informative.
thanks again for all the replies on this thread, it's been extremely informative.
#14
My guess is that the PRV is set wrong,
Loosen the locknut on the adjusting screw and back it WAY out... then after you drain some water out of the boiler to drop the pressure down to say 5 PSI or so, start screwing the adjustment in until you hear a little water flowing in...
STOP! and wait until the pressure stabilizes... IF it stabilizes... these valves are VERY slow to 'line out' at the final setting, so you have to give it time, like at LEAST 15 minutes... go like a half turn at a time at that point until the pressure stabilizes cold at 12 PSI.
let it refill to 12 PSI cold and then shut off the water supply.
#17
Member
Thread Starter
Join Date: Mar 2010
Location: US
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Looks like fixing the PRV setting did the trick. I'm at ~20 hours of sustained heat & pressure with no leaks. Thanks for all your help, I'll get some maintenance done on these ASAP.