Reset Buffer Protection et all
#1
Member
Thread Starter
Join Date: Feb 2011
Location: US
Posts: 522
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Reset Buffer Protection et all
Posted by NJT in a different thread:
Hmmm
And i swear i want to do this with the old boiler, this spring.
I thought i had it figured out but. there's always a but..
INDOOR reset and outdoor reset.
Veryyyyyyy interesting NJT.
I was thinking of using Tekmar thermostats for indoor feedback but only to tweak the buffer temp.
This idea of variable injection wth constant circulation, controlled by indoor reset, has got my attention.
NJT
Please, pray tell, what control would you use for the Indoor Reset?
And what happens if the outdoor reset temo for the buffer is not hot enough?
Peter
If I were going to do it... and I swear I am some day,
)... I would go with a Burnham MPO feeding a Boiler Buddy buffer tank, come off the buffer tank with variable speed injection into distribution system with constant circ. I would use INDOOR feedback to regulate the circulating water temp, and OUTDOOR feedback to regulate the water temp in the buffer tank.
)... I would go with a Burnham MPO feeding a Boiler Buddy buffer tank, come off the buffer tank with variable speed injection into distribution system with constant circ. I would use INDOOR feedback to regulate the circulating water temp, and OUTDOOR feedback to regulate the water temp in the buffer tank.
And i swear i want to do this with the old boiler, this spring.
I thought i had it figured out but. there's always a but..
INDOOR reset and outdoor reset.
Veryyyyyyy interesting NJT.
I was thinking of using Tekmar thermostats for indoor feedback but only to tweak the buffer temp.
This idea of variable injection wth constant circulation, controlled by indoor reset, has got my attention.
NJT
Please, pray tell, what control would you use for the Indoor Reset?
And what happens if the outdoor reset temo for the buffer is not hot enough?
Peter
#2
Please, pray tell, what control would you use for the Indoor Reset?
And what happens if the outdoor reset temo for the buffer is not hot enough?
#4
Don't worry about it. The MPO-IQ only needs 100f return temp and get above that before it shuts off. The only time I worry about flue gas condensation with the MPO is large gravity hot water systems or systems with all radiant floor heat. I don't even worry about it with cast iron radiator systems as long as there are multiple zones.
#6
And the reality is that when I finally get around to replacing the boiler (probably next summer if I can talk rbeck into a road trip! ) I'll probably just pipe it up as a standard system... but I like messing with complicated designs, so I'm gonna do that anyway.
I would like to give constant circ a try though... so may end up with something a bit more complex...
Maybe use the MPO-IQ controls and take the boiler demand signal from an aquastat on the buffer tank, use that as a 'battery' and only recharge it when needed... so many ideas, so little money!
I would like to give constant circ a try though... so may end up with something a bit more complex...
Maybe use the MPO-IQ controls and take the boiler demand signal from an aquastat on the buffer tank, use that as a 'battery' and only recharge it when needed... so many ideas, so little money!
#7
Member
Join Date: Dec 2011
Location: Usa
Posts: 63
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'm working on same design, different boiler, large buffer tank.
I want ODR to control boiler output and buffer tank temperature.
I want the system to draw down the buffer temperature, say 20*
Trying to figure out method to control boiler T-T
If I jumper T-T and set a constant call for heat, won't the boiler fire frequently & short cycle?
thanks BBP
I want ODR to control boiler output and buffer tank temperature.
I want the system to draw down the buffer temperature, say 20*
Trying to figure out method to control boiler T-T
If I jumper T-T and set a constant call for heat, won't the boiler fire frequently & short cycle?
thanks BBP
#8
If I jumper T-T and set a constant call for heat, won't the boiler fire frequently & short cycle?
You could look at using something like the Tekmar 256. Wire the boiler output on the 256 to the T T terminals of the boiler. Wire the demand signal on the 256 for a constant call for heat. Let the circ pump between the boiler and the tank run off the boiler control. Put the 256 boiler sensor in the well on the buffer tank. Experiment with the diff setting on the Tekmar to get where you want it.
For this to be of any benefit, the tank would have to be quite large... what were you thinking of using? AND you would want it well insulated... standby losses from a large uninsulated tank could be huge.
#9
If you really don't want the buffer to maintain temp this is simple with multiple zone relay. Of course that is presuming that you have a multiple zone relay. I have a large job site in Anchorage Alaska where they were maintaining tank temp. They had the aquastat on the tank wired to T-T. The boiler was cycling on and off in the shoulder seasons and I thought this was a waste of money. We ran the wire between T-T and aquastat in series with the end switch on the multi zone relay. If the tank was hot enough the aquastat would not allow the boiler to run and if there was no call from the multi zone relay the aquastat would not call. This same idea could be applied to the ODR in series with the aquastat and boiler t-t.
BTW NJT just say when and I will be there! You, me and Sam we can figure out anyproblem. Whether it works the next day who knows.
BTW NJT just say when and I will be there! You, me and Sam we can figure out anyproblem. Whether it works the next day who knows.
#10
Member
Join Date: Dec 2011
Location: Usa
Posts: 63
Upvotes: 0
Received 0 Upvotes
on
0 Posts
More info
Hello, thanks for input.
Boiler is a Buderus GB142-45-NG It has built in AM10 ODR
142MBH AFUE at sea level, here at 6,000' elevation, around 130MBH?
Buffer will consist of 3x50gal. (150gal.) Electric HWH plumbed in Parallel. (had these on hand & itemporary to keep house from freezing, $450 / month bills)
Large house 4350 ft2 5x zones of heat transfer plates under subfloor. + 2800 ft2 basement pex in slab 2x zones
I used the DOE rescheck online program & get a design load of 80MBH (seems low)
DHW will be 80gal Rheem commercial tank heated via external GEA flat plate heat exchanger
I think that the AM10 ODR controls the boilers variable temperature system ouput ONLY & thus the buffer tanks variable temperature.
This will be high enough to supply the medium temperature heat transfer plates, and will temper down for slab.
I won't be able to use a fixed temperature aquastat on the buffer tanks.
At this time, I don't know if control panel parameters will let me set the system delta temperature, but I think this is not possible as its computer controls this automatically (sorry for bad sentence structure as i'm already having champaign)
Thats it for now, Happy New Year 2012
Boiler is a Buderus GB142-45-NG It has built in AM10 ODR
142MBH AFUE at sea level, here at 6,000' elevation, around 130MBH?
Buffer will consist of 3x50gal. (150gal.) Electric HWH plumbed in Parallel. (had these on hand & itemporary to keep house from freezing, $450 / month bills)
Large house 4350 ft2 5x zones of heat transfer plates under subfloor. + 2800 ft2 basement pex in slab 2x zones
I used the DOE rescheck online program & get a design load of 80MBH (seems low)
DHW will be 80gal Rheem commercial tank heated via external GEA flat plate heat exchanger
I think that the AM10 ODR controls the boilers variable temperature system ouput ONLY & thus the buffer tanks variable temperature.
This will be high enough to supply the medium temperature heat transfer plates, and will temper down for slab.
I won't be able to use a fixed temperature aquastat on the buffer tanks.
At this time, I don't know if control panel parameters will let me set the system delta temperature, but I think this is not possible as its computer controls this automatically (sorry for bad sentence structure as i'm already having champaign)
Thats it for now, Happy New Year 2012
Last edited by NJT; 01-04-12 at 04:00 PM.
#13
Member
Join Date: Dec 2011
Location: Usa
Posts: 63
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'm unsure of heat loss, guessing at insulation values. Insulation under basement slab is a guess. Large shower multiple heads, Jacussi tub.
Got an estimate from some company for 300MBH boiler install.
Got an estimate from some company for 300MBH boiler install.
Last edited by NJT; 01-04-12 at 04:01 PM.
#14
rbeck, that's a great idea! I like!
So even if the ODR is wired for constant demand, the endswitch on the zone panel will prevent the boiler from firing in the absence of a heat call and prevent stranding heat in the tank... nice!
So even if the ODR is wired for constant demand, the endswitch on the zone panel will prevent the boiler from firing in the absence of a heat call and prevent stranding heat in the tank... nice!
#15
Member
Join Date: Dec 2011
Location: Usa
Posts: 63
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I have 2 zone Relay boxes, one medium temperature manifold for the heat transfer plates & a second low temperature manifold for the basement slab zones.
Good idea using relay box end switch, I will try that on the medium temperature one to boiler T-T
It S/B Illegal for "Heating Pros" to sell oversize boilers by a factor of 3X
Good idea using relay box end switch, I will try that on the medium temperature one to boiler T-T
It S/B Illegal for "Heating Pros" to sell oversize boilers by a factor of 3X
Last edited by NJT; 01-04-12 at 04:58 PM. Reason: no problema!
#16
When you say 'medium temperature' ... wondering why you can't run both at the same temperature?
By 'heat transfer plates', you are talking about tubing under a floor, correct?
And 'low temperature' ? How low?
By 'heat transfer plates', you are talking about tubing under a floor, correct?
And 'low temperature' ? How low?
#17
Member
Join Date: Dec 2011
Location: Usa
Posts: 63
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes, cheap thin aluminum heat transfer plates under the subfloor. Floor coverings & thus R-values TBD
As basement under slab insulation in unknown, water temps are unknown, but will use as low as possible.
If main levels of house require 150* or so, it would be too hot to run throug slab.
As basement under slab insulation in unknown, water temps are unknown, but will use as low as possible.
If main levels of house require 150* or so, it would be too hot to run throug slab.
#18
Got an estimate from some company for 300MBH boiler install.
Chances are that there is no insulation under your basement slab.
#19
Member
Join Date: Dec 2011
Location: Usa
Posts: 63
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Original builder was smart enough to put 2 zones of 8 loops each of O2 barrier pex into slab, so hopefully 2" of blueboard under it.
Builder was forclosed by bank & took a big loss. A boiler wasn't installed.
Builder was forclosed by bank & took a big loss. A boiler wasn't installed.
#22
Member
Join Date: Dec 2011
Location: Usa
Posts: 63
Upvotes: 0
Received 0 Upvotes
on
0 Posts
We shall see what temp is required. ODR will allow adjustment.
With large windows in great room, code minimum insulation in walls & cathedral ceiling, wood or carpet & pad floor coverings, I know this zones water temp will be much higher than what is needed for basement slab zones.
With large windows in great room, code minimum insulation in walls & cathedral ceiling, wood or carpet & pad floor coverings, I know this zones water temp will be much higher than what is needed for basement slab zones.
#23
Choose floor coverings carefully! Some manufacturers specify a max temp... some of that engineered flooring material can't withstand prolonged temps as high as 150... many solid flooring materials will discolor...
#24
Member
Join Date: Dec 2011
Location: Usa
Posts: 63
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Time Delay T-T control idea
ODR will control the boilers upper output limit on fire & thus the buffers upper temperature.
The "medium temperature" zone switching relays end switch will pass through a 24vac Delay-On-Make Time Delay Relay in series to boiler T-T (say set to 10-17 minute delay, testing required) This should prevent any short cycling.
This will allow small medium temperature zones to draw heat out of the buffer, possibly without firing boiler, if thermostat is satisfied before time delay expires.
This will also allow larger medium temperature zones to draw heat out of the buffer before firing boiler.
A basement slab low temperature zone will draw heat out of buffer without setting a call for heat. Buffer is large enough where it should never drop to 75* before a medium temperature zone calls for heat.
Feedback?
The "medium temperature" zone switching relays end switch will pass through a 24vac Delay-On-Make Time Delay Relay in series to boiler T-T (say set to 10-17 minute delay, testing required) This should prevent any short cycling.
This will allow small medium temperature zones to draw heat out of the buffer, possibly without firing boiler, if thermostat is satisfied before time delay expires.
This will also allow larger medium temperature zones to draw heat out of the buffer before firing boiler.
A basement slab low temperature zone will draw heat out of buffer without setting a call for heat. Buffer is large enough where it should never drop to 75* before a medium temperature zone calls for heat.
Feedback?
#25
Member
Thread Starter
Join Date: Feb 2011
Location: US
Posts: 522
Upvotes: 0
Received 0 Upvotes
on
0 Posts
3x50, 150 gallons of water to heat up.
I can't imagine, even with a boiler that big, especially throttled down by ODR, that you would have any need for a time delay.
Besides as far as i understand it, short cycling, refers more to short on cycles, not necessarily a short time between reasonably long on cycles.
At full 130k output, 150 h to 130 low:
Without any load at all, it would take about 12 minutes to heat up the 150g's of water.
With a 20k btu load it will take about an hour and 13 minutes to drop 20*
A 40K load, will take, 37 minutes to cool off 20*.
But then with a 40k load it will take 37 minutes to heat the tanks up again.
Not exactly short cycling, imo.
Additionally.
Presumably, the ODR wouod also widen the differental as needed, in warmer weather, thus extending the cycle times.
Peter
I can't imagine, even with a boiler that big, especially throttled down by ODR, that you would have any need for a time delay.
Besides as far as i understand it, short cycling, refers more to short on cycles, not necessarily a short time between reasonably long on cycles.
At full 130k output, 150 h to 130 low:
Without any load at all, it would take about 12 minutes to heat up the 150g's of water.
With a 20k btu load it will take about an hour and 13 minutes to drop 20*
A 40K load, will take, 37 minutes to cool off 20*.
But then with a 40k load it will take 37 minutes to heat the tanks up again.
Not exactly short cycling, imo.
Additionally.
Presumably, the ODR wouod also widen the differental as needed, in warmer weather, thus extending the cycle times.
Peter
#26
Member
Join Date: Dec 2011
Location: Usa
Posts: 63
Upvotes: 0
Received 0 Upvotes
on
0 Posts
goals
Thanks Peter for doing that math.
I'm unsure of the AM10 ODR controllers algorithms.
Time delay relay cost only $22
When it comes to boiler cycles "longer IS better"
My goals:
1. Heat this LARGE house, with its pex & manifolds already installed, with this boiler as efficiently as reasonably possible, while minimizing expense, using parts on hand.
2. Determine how to manage a large buffer tank, using ODR as high temperature limit and how to call for heat from boiler using its T-T input.
3. Prevent boiler short cycles, when small low mass zones call for heat, which is exaserbated in shoulder weather conditions. Draw buffer temperature down without firing boiler when possible.
I'm unsure of the AM10 ODR controllers algorithms.
Time delay relay cost only $22
When it comes to boiler cycles "longer IS better"
My goals:
1. Heat this LARGE house, with its pex & manifolds already installed, with this boiler as efficiently as reasonably possible, while minimizing expense, using parts on hand.
2. Determine how to manage a large buffer tank, using ODR as high temperature limit and how to call for heat from boiler using its T-T input.
3. Prevent boiler short cycles, when small low mass zones call for heat, which is exaserbated in shoulder weather conditions. Draw buffer temperature down without firing boiler when possible.
#27
2. Determine how to manage a large buffer tank, using ODR as high temperature limit and how to call for heat from boiler using its T-T input.
With large capacity buffer tanks, boiler bypass will probably be needed.
Zone valves or pumped zones, use appropriate Taco panel.
Pipe buffer tanks as 'reverse return' on both sides to ensure equal flow through all three tanks.
#29
Member
Thread Starter
Join Date: Feb 2011
Location: US
Posts: 522
Upvotes: 0
Received 0 Upvotes
on
0 Posts
NJT's diagram would be perfect for an on off boiler, with one exception, imo. I think an active control, based on return temps, is needed for protection, not a fixed bypass.
A further problem might be, that BBill is using water heaters and it might not be easy to pipe them up in the style of a hydraulic separator.
Anyway:
However, i've come to find out, BBill has a MOD CON.
Thus no need for a by pass, at least.
Using a mod con with a buffer, can be a real donnybrook.
We want the mod-con to stay in condensing mode, but the mod-con is going to kick butt trying to get that buffer tank heated up.
It's going to take a goodly amount of trial and error with the ontrols to get that to all work out as desired.
Not easy.
One thing to consider, with the mod con and a buffer..
I've read good arguments for putting the buffer on the return.
This collects and holds the coldest water to aid the boiler for condening mode.
Thus the supply from the boiler to the loads would have the ODR sensor, and the cold return water would load up the buffer on the way back.
Something to think about.
Peter
A further problem might be, that BBill is using water heaters and it might not be easy to pipe them up in the style of a hydraulic separator.
Anyway:
However, i've come to find out, BBill has a MOD CON.
Thus no need for a by pass, at least.
Using a mod con with a buffer, can be a real donnybrook.
We want the mod-con to stay in condensing mode, but the mod-con is going to kick butt trying to get that buffer tank heated up.
It's going to take a goodly amount of trial and error with the ontrols to get that to all work out as desired.
Not easy.
One thing to consider, with the mod con and a buffer..
I've read good arguments for putting the buffer on the return.
This collects and holds the coldest water to aid the boiler for condening mode.
Thus the supply from the boiler to the loads would have the ODR sensor, and the cold return water would load up the buffer on the way back.
Something to think about.
Peter
#30
One thing to consider, with the mod con and a buffer..
I've read good arguments for putting the buffer on the return.
This collects and holds the coldest water to aid the boiler for condening mode.
Thus the supply from the boiler to the loads would have the ODR sensor, and the cold return water would load up the buffer on the way back.
I've read good arguments for putting the buffer on the return.
This collects and holds the coldest water to aid the boiler for condening mode.
Thus the supply from the boiler to the loads would have the ODR sensor, and the cold return water would load up the buffer on the way back.
#31
However, i've come to find out, BBill has a MOD CON.
Thus no need for a by pass, at least.
Using a mod con with a buffer, can be a real donnybrook.
Thus no need for a by pass, at least.
Using a mod con with a buffer, can be a real donnybrook.
And now I'm questioning if it even makes sense to use the buffer tanks. What would be the point? Let the thing run and condense to beat the band! Let the built-in controls do their thing!
#32
using water heaters and it might not be easy to pipe them up in the style of a hydraulic separator.
I thought that it might be possible to use the domestic connections to feed and return from the system side, and to use the drain and the relief valve port (relief valve not needed now) to pipe to the boiler side.
I think the 'dip tube' in the water heater would survive the temperatures to be expected... or would it?
But again, what's the real point of the buffers with a mod/con in the first place?
Maybe the best solution has been offered by Peter... put them on the return line to the boiler, and pipe them in SERIES... return from system in the TOP, out the BOTTOM to the TOP of the next, etc, etc...
#33
I've read good arguments for putting the buffer on the return
#35
Member
Thread Starter
Join Date: Feb 2011
Location: US
Posts: 522
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I thought that it might be possible to use the domestic connections to feed and return from the system side, and to use the drain and the relief valve port (relief valve not needed now) to pipe to the boiler side
I have no way of knowing the versaity of this. If true, it could make life much easier for BBill.
Peter
#36
They aren't a standard NPT thread. It's a straight cut thread, I believe 1". I have heard of people using them myself, claiming that an NPT adapter fitting will thread in and seal as long as you goop it up real good, but I wouldn't trust that myself. It's definitely 'ghetto' in my opinion.
#37
Member
Join Date: Dec 2011
Location: Usa
Posts: 63
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I would post a picture of design if I could figure out how?
Went to FAQ & searched on pictures, it said go to user panel & click on a link to add an album, didn't see that link????
I need step by step as I'm old. Thanks
Went to FAQ & searched on pictures, it said go to user panel & click on a link to add an album, didn't see that link????
I need step by step as I'm old. Thanks
#38
Go to Image hosting, free photo sharing & video sharing at Photobucket and set up a FREE account.
Upload your pictures to a PUBLIC album.
Come back here and drop a LINK to the album so that we can go and view.
Upload your pictures to a PUBLIC album.
Come back here and drop a LINK to the album so that we can go and view.
#40
Member
Thread Starter
Join Date: Feb 2011
Location: US
Posts: 522
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hello BBill,
I think the illustrious Xiphias would say the first thing we want to know, is there a heat loss done for the house?
If so what are the results?
If not, then one needs to be done.
Sort of getting the horse in front of the cart, or sumthin'.
Just a quick look. Question.
Does there really need to be a separate boiler loop?
Peter
I think the illustrious Xiphias would say the first thing we want to know, is there a heat loss done for the house?
If so what are the results?
If not, then one needs to be done.
Sort of getting the horse in front of the cart, or sumthin'.
Just a quick look. Question.
Does there really need to be a separate boiler loop?
Peter