Hydro Therm HC-125 NJ Trooper


  #1  
Old 01-07-12, 09:18 AM
H
Member
Thread Starter
Join Date: Jan 2012
Location: usa
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hydro Therm HC-125 NJ Trooper

I have a question about the switching relay on my Hydro-Therm HC 125. I am barrowing a couple of links from other member hope this is o.k...
This is the current Relay. photos #2, 4 and 5
boiler-relay pictures by rviger - Photobucket
I have read through various posts and I noticed robertk54 used this switching relay in his HC-125. DIY post (his posts start about 3/4 the way down the thread)
I found this Taco too What other relays are out there for the HC 125? What would you suggest?

Thanks for your help.
 
  #2  
Old 01-07-12, 09:34 AM
P
Member
Join Date: Feb 2011
Location: US
Posts: 522
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hello,
I'm a huge fan of Taco equipment.
Highly recommended.

I pray your existing stuff is in better shape than the 2,4,5 pics.

Peter
 
  #3  
Old 01-07-12, 10:31 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Hart, tell us what the problem is first... what got you started investigating this? we need some history.
 
  #4  
Old 01-07-12, 11:14 AM
H
Member
Thread Starter
Join Date: Jan 2012
Location: usa
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
The Switch relay was hit and shorted out. ( Moving Christmas decorations) The pilot light is on, no voltage from the inductor to the PP. From PP to TH with heat call there is no voltage. It may be the aquastat but because of the damage done to the relay....
 
  #5  
Old 01-07-12, 11:47 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
What happens when you move the switch on the relay box from AUTO to MANUAL ?

Does the burner light?
 
  #6  
Old 01-07-12, 11:48 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
When the thermostats call for heat, does the CIRCULATOR RUN ?
 
  #7  
Old 01-07-12, 11:54 AM
H
Member
Thread Starter
Join Date: Jan 2012
Location: usa
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
The circulator does not run with a heat call. The burner does not light with the switch on manual.
 
  #8  
Old 01-07-12, 04:36 PM
H
Member
Thread Starter
Join Date: Jan 2012
Location: usa
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hey Peter,

thanks for the prayers. ;-)
 
  #9  
Old 01-07-12, 05:54 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
The circulator does not run with a heat call. The burner does not light with the switch on manual.
OK... based on what I have learned so far, it is possible that there are more than one problem.

How so was the control 'hit' and shorted out? Was it absolutely smashed into? and sparks came out? Or bumped... and then just didn't work?

Anyhow, if the relay is working when the thermostat calls for heat, you should hear the relay 'click' and the circulator should run. If the boiler is cold, the main burner should also light.

When you switch from 'auto' to 'manual', the burner should light, REGARDLESS of whether there's a heat call or not, and regardless of whether or not the relay is working. Not only that, but the burner should light when switching to manual even if the POWER IS OUT!

The fact that the pump doesn't start, and you probably don't hear a 'click' when the thermostat calls for heat, means that yes, you should replace the relay, but the fact that the burner doesn't fire MIGHT mean there's also another problem. It could mean that the auto/man switch in your relay is just cruddy though... so the best way to find that out is to replace the relay.

Note that the replacement relays do NOT have the 'auto/man' switch on them.

You can use any of the 'single zone' relay boxes... my personal choice for this application would be the R8845, but any of them will work.

Honeywell R8845U1003 http://customer.honeywell.com/techli...it/69-1292.pdf

Honeywell RA832A1066 http://customer.honeywell.com/techli...0s/69-2041.pdf

Taco SR501 http://www.taco-hvac.com/uploads/Fil...ry/102-169.pdf

Argo AR822 http://www.ecrinternational.com/secu...ument/1545.pdf
 
  #10  
Old 01-08-12, 05:39 AM
H
Member
Thread Starter
Join Date: Jan 2012
Location: usa
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
The control was hit with a wooden pole. Slid off the box I was carrying and cracked the plastic around the switch. A loud snap, some small sparks and a quick whiff of ozone.

I will start with the relay and hope for the best. If not, I know where I can get some good advice. Thank you for your time and help.
 
  #11  
Old 01-08-12, 08:48 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
I know where I can get some good advice.
I hope that you mean here!

OK, based on that description, it is pretty much a given that the relay box is toast. What we don't know is whether anything else got damaged.

You can do one more thing to troubleshoot while you are waiting for the replacement relay to arrive...

If you remove the wires on X1 and X2 on the relay box, and touch them together, the burner should fire. If it does not, then there's another problem... just so you know what to be prepared for.
 
 