new homeowner, questions about my boiler
#1
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
new homeowner, questions about my boiler
Hello all! First time homeowner here, just bought my first house. It has a hot water boiler for baseboard heating. I have some question that hopefully you guys can help me with, with patience. I've done a lot of searching and googling but can't seem to find answers to these questions.
First off, house was built in 1960. The boiler looks ancient so I'm assuming it is original with the house. It says Bryant on it. One part of it, a red box, looks newer and the color doesn't match. I think this might be the "circulator".
Any way, someone told me if I shut off the main water to the house, it can cause the boiler to explode if I don't properly bleed the lines afterwords? Is this true? I actually had to shut off the main water supply 2 days ago, because I had a plumbing problem under the bathroom sink, and the shutoff underneath the sink is busted (hehe, found that out the hard way after 2 inches of water in the bathroom. Not to go off on a tangent but the sink is busted on the hot water side and no hot water was coming out, so there was no way of knowing that the hot water shut off didn't work. I'm not that stupid!)
So I've done research and I can't come to any conclusions about boilers exploding after not bleeding the lines after shutting off the main water supply. So is this true or not?
I'm panicking, because when my boiler is done firing up (natural gas burner), after the flame shuts off, I hear a very fast dripping sound coming from inside the boiler, like something is leaking. The dripping sound slows down over time the longer the burner has been off.
Thanks for any help!
Also my other question would be, if anyone has any suggestions to what I can do about the wire on it. It is exposed and kind of just hanging out. My kitty's litter box is about 2 feet from the boiler (only spot in the house I can really put his litter box) and he has a habit of chewing on wires. I fear he will do this. I was thinking of boxing in the boiler or something but no idea how to without damaging it.
First off, house was built in 1960. The boiler looks ancient so I'm assuming it is original with the house. It says Bryant on it. One part of it, a red box, looks newer and the color doesn't match. I think this might be the "circulator".
Any way, someone told me if I shut off the main water to the house, it can cause the boiler to explode if I don't properly bleed the lines afterwords? Is this true? I actually had to shut off the main water supply 2 days ago, because I had a plumbing problem under the bathroom sink, and the shutoff underneath the sink is busted (hehe, found that out the hard way after 2 inches of water in the bathroom. Not to go off on a tangent but the sink is busted on the hot water side and no hot water was coming out, so there was no way of knowing that the hot water shut off didn't work. I'm not that stupid!)
So I've done research and I can't come to any conclusions about boilers exploding after not bleeding the lines after shutting off the main water supply. So is this true or not?
I'm panicking, because when my boiler is done firing up (natural gas burner), after the flame shuts off, I hear a very fast dripping sound coming from inside the boiler, like something is leaking. The dripping sound slows down over time the longer the burner has been off.
Thanks for any help!
Also my other question would be, if anyone has any suggestions to what I can do about the wire on it. It is exposed and kind of just hanging out. My kitty's litter box is about 2 feet from the boiler (only spot in the house I can really put his litter box) and he has a habit of chewing on wires. I fear he will do this. I was thinking of boxing in the boiler or something but no idea how to without damaging it.
#2
To shut the water off for servicing the sink or anything else in the home should not affect the boiler at all. If the check valve, keeps water from going the wrong direction in a pipe, is bad you could lose pressure in the boiler. To be safe you can look at the gage to verify there is 12 - 18 psi on the gage, shut the valve that feeds water into the boiler making a note to turn it back on when the water is turned back on.
The dripping sound could be caused by metal contraction, mineral build-up in the boiler or an actual leak.
As far as the wires, by code, although may not have applied when that boiler was installed, is required to be in metal. They call this metal coating MC, BX, Conduit or flexible conduit. Today it is illegal to use 120v plastic coated wire, romex, around boilers. 24v can be wired without metal coating. I would suggest you go to the building supply stores and get the pre-split wire covering. You just open it and slip it over the wire to keep the little kitty teeth off the actual wire. It comes it different sizes. My calico has left her teeth marks on my laptop charger plug when she was younger.
The dripping sound could be caused by metal contraction, mineral build-up in the boiler or an actual leak.
As far as the wires, by code, although may not have applied when that boiler was installed, is required to be in metal. They call this metal coating MC, BX, Conduit or flexible conduit. Today it is illegal to use 120v plastic coated wire, romex, around boilers. 24v can be wired without metal coating. I would suggest you go to the building supply stores and get the pre-split wire covering. You just open it and slip it over the wire to keep the little kitty teeth off the actual wire. It comes it different sizes. My calico has left her teeth marks on my laptop charger plug when she was younger.
#3
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes
on
0 Posts
hot water boiler systems for hot water rads/baseboards is a sealed system with that RED assemblt valve on the boiler maintaining 12psi constantly if you don't see water in the home or in the basement boiler area the noises are expansion and contraction of the metal and water cooling off.
[NJT edit: Sminker, not all "Pressure Reducing Valves" are RED! There are Green ones, Brown ones, Gold ones... ]
[NJT edit: Sminker, not all "Pressure Reducing Valves" are RED! There are Green ones, Brown ones, Gold ones... ]
Last edited by NJT; 01-08-12 at 09:33 AM.
#4
Member
Join Date: Feb 2011
Location: US
Posts: 522
Upvotes: 0
Received 0 Upvotes
on
0 Posts
RED assemblt valve
I don't have one of those.
Mine is a different color.
Do you think i should worry about the the boiler might blowing up becuase it's not a RED one?
[Sarcasm off]
Peter
Last edited by NJT; 01-08-12 at 09:34 AM.
#5
You should not worry about the boiler blowing up. I don't know who told you that it would, but they don't know what they are talking about. Your boiler should have a back flow preventer on it. If your domestic water supply was shut off at the meter and then drained for work like you had mentioned, then the black flow preventer would stop any water in the boiler system from leaking out into the domestic supply side. Check to make sure you have one. You can also shut off the valve between the boiler system on the domestic. That would stop flow in either direction. As rbeck mentioned, checking your boiler gauge to make sure you have a minimum of 12 psi when the boiler is cold will tell you if you have enough water in your system. Adding a low water cut off will also add another level of safety. This is now being required for all new boiler installations.
#6
With a name like Photog0411, I'm willing to bet that you are good at taking pictures?
Set up a FREE account at Image hosting, free photo sharing & video sharing at Photobucket and upload the pics there. Come back here and drop a link to your PUBLIC album and we'll take a look and advise...
Set up a FREE account at Image hosting, free photo sharing & video sharing at Photobucket and upload the pics there. Come back here and drop a link to your PUBLIC album and we'll take a look and advise...
#7
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Here are pics requested. When boiler is off, PSI seems to read about 11.9 PSI. When it's on and burning the flames, jumps up to about 16 PSI.
When it first kicks on, flames shoot out of the bottom of the front! I'm scared. If you look in 2nd pic with wires, you see burn marks on the boiler, it's from when the flame shoot out the front below where the wires are. It's only for a split second when burner first ignites, but I'm scared if my kitty was sitting there and get roasted like a pheasant. I know, call me stupid for putting kitting litter box 2 feet from boiler, but it's really only place in this house I can put it. The boiler is in a small 8x10' laundry room with washer and dryer, water softener (which is busted and leaks) and water heater. Everything else in house is living space we can't have smelling like cat litter.



When it first kicks on, flames shoot out of the bottom of the front! I'm scared. If you look in 2nd pic with wires, you see burn marks on the boiler, it's from when the flame shoot out the front below where the wires are. It's only for a split second when burner first ignites, but I'm scared if my kitty was sitting there and get roasted like a pheasant. I know, call me stupid for putting kitting litter box 2 feet from boiler, but it's really only place in this house I can put it. The boiler is in a small 8x10' laundry room with washer and dryer, water softener (which is busted and leaks) and water heater. Everything else in house is living space we can't have smelling like cat litter.




#8
When it first kicks on, flames shoot out of the bottom of the front! I'm scared.
Your boiler needs to be disassembled, properly cleaned, combustion checked SOON! like NOW!
The pressure gauge is either NON functional, or you have no pressure in your system... you really need to have a good technician come in and service that unit before there is a much bigger problem.
PLEASE tell me that you have CO detectors all around the home!
#9
Member
Look at the first photo. It looks to me like you have two burner tubes, and the inlet to the one on the left is catty-whampus - at an odd angle, possibly broken or bent.
If the gas company comes and sees this situation, they will shut off your gas at the meter, and lock it with a padlock.
If the gas company comes and sees this situation, they will shut off your gas at the meter, and lock it with a padlock.
#11
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
My home inspector didn't say anything really about the boiler other than it might need some maintenance in the future. He did detect a gas leak in a pipe above the hot water heater (not the boiler), and as far as I know the gas company (national grid) actually came and fixed the gas leak. I say as far as I know, because that's what the seller of my house told me. I did drive by 2 days after that, and did see a national grid truck parked in the road in front of this house. So I have partial verification. The pipes don't look new though, so my guess is they just snugged something down.
To NJ trooper, I have to check on the carbon monoxide detectors. I know there's a smoke alarm in the hallway that is so old it sounds like a fax machine and not an actual alarm, I was planning on replacing it. I think there may be one carbon monxoide detector in the hallway that leads to all the bedrooms.
UPDATE: Yes there is a carbon monoxide detector in the hallway that leads to the bedrooms. Not any in the actual bedrooms though.
To NJ trooper, I have to check on the carbon monoxide detectors. I know there's a smoke alarm in the hallway that is so old it sounds like a fax machine and not an actual alarm, I was planning on replacing it. I think there may be one carbon monxoide detector in the hallway that leads to all the bedrooms.
UPDATE: Yes there is a carbon monoxide detector in the hallway that leads to the bedrooms. Not any in the actual bedrooms though.
#12
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Here's more pics I took with my iPad. I don't know if they will help. I still haven't unpacked my real camera, lol. Does anyone know a good reputable nationwide boiler service I can call to come look at it? I'm leary about local people that might want to rip me off and have a whole new boiler installed which can cost like 3 grand after labor. I tried searching for boiler servicemen but could only find boilers, like industrial boilers in factories. 




#13
Does anyone know a good reputable nationwide boiler service I can call to come look at it?
You want to look for 'heating contractors' in your area. Tell them up front that you are looking for a complete inspection and cleaning AND COMBUSTION TEST with proper INSTRUMENTS!
Shop your service guys real carefully, and CHECK any references and stuff. If the guys are honest and upstanding, they will be happy to provide them. Don't let anyone fast talk you... if you 'smell scare tactics' steer clear! Boiler salespeople are birds of prey... (deepest apologies to any HONEST boiler 'salesnicians' out there... )
Have the heat exchanger inspected ... and brushed out.
BURNERS removed and cleaned.
PILOT BURNER checked, cleaned if necessary.
Entire fire side of boiler needs brushing and vacuum.
It would be a good idea to have the flue pipe inspected now, and soon, when the weather warms a little (if not sooner), have the CHIMNEY INSPECTED also.
The gas pressure setting on the valve should probably be checked with a MANOMETER.
The PRESSURE RELIEF VALVE should be replaced if it's more than five years old.
The 'Pressure and Temperature' GAUGE should be checked and made to work properly.
The EXPANSION TANK (which I can't see in any of your pictures) should be checked for proper operation and serviced as needed.
The DRAIN VALVE on the boiler, to the left of the burner looks pretty tired... probably replace.
How much more of your money can I spend?
By the way... that site you've got your pics loaded on is AS SLOW AS MOLASSES! I think they have that server running on a Commodore 64!
#14
PLEASE have something done soon... I REALLY don't like the flame rollout issue you mentioned... seriously... and those last pics showing the 'sooty' deposits on the front... very disturbing... where there's SOOT, there's CARBON MONOXIDE!
#15
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes
on
0 Posts
And all of that work Trooper describes, which you should absolutely have done ASAP, will probably take 3-4 hours and consume maybe $150 or so in parts.
Shop your contractor carefully. Do not be surprised if you find only 1 out of 4 or 5 that aren't knuckleheads.
Shop your contractor carefully. Do not be surprised if you find only 1 out of 4 or 5 that aren't knuckleheads.
#16
Member
With a gas-fired boiler, I wonder where all that ash seems to be coming from, as shown in the pix.
#17
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
What's a fair rate per hour for this service?
I also have some electrical problems with this house, NOTHING MAJOR except one thing (power lines to house from utillity pole are about 5 feet above the deck and can be touched by children easily. amazed that bank passed this when I bought house. Inspector even said a kid might want to swing from them and play tarzan, then they would be fried to a crisp.) Most electricians quoted me for about $180 to $220 per hour of labor. I also have some plumbing issues (again nothing major, the pipes goes to water softener sprays out tons of water if you engage the bypass. Also one sink is broken, and the shut-off valve below the sink is broken so I can't fix the sink myself. These are copper pipes, I don't know how to weld the joints on.) Most plumbers quoted me about $140 to $170 per hour of labor.
If the boiler people are gonna charge this much ouch... 3-4 hours of work you say? That's gonna be like $800 for just the labor, not including the $150 in parts you said. OUCH.
Looks like I need to sell my car to fix up my house. LOL
I also have some electrical problems with this house, NOTHING MAJOR except one thing (power lines to house from utillity pole are about 5 feet above the deck and can be touched by children easily. amazed that bank passed this when I bought house. Inspector even said a kid might want to swing from them and play tarzan, then they would be fried to a crisp.) Most electricians quoted me for about $180 to $220 per hour of labor. I also have some plumbing issues (again nothing major, the pipes goes to water softener sprays out tons of water if you engage the bypass. Also one sink is broken, and the shut-off valve below the sink is broken so I can't fix the sink myself. These are copper pipes, I don't know how to weld the joints on.) Most plumbers quoted me about $140 to $170 per hour of labor.
If the boiler people are gonna charge this much ouch... 3-4 hours of work you say? That's gonna be like $800 for just the labor, not including the $150 in parts you said. OUCH.
Looks like I need to sell my car to fix up my house. LOL
#18
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
one other issue I might add. When the boiler is on (both burning and not burning), it makes a really loud buzzing noise. Sounds electricial. Kind of like, hmm a huge flourescent light kind of buzzing? Am I thinking the right type of noise? Maybe like the buzzing noise on a clothes dryer, just a little quieter?
#19
Sounds like a relay buzzing... might not be a 'real' problem... they do that sometimes.
There may be something that could be done to quiet the buzz, but get that other stuff fixed first! Stop delaying, this is serious!
The CLEANING should be done first.
There may be something that could be done to quiet the buzz, but get that other stuff fixed first! Stop delaying, this is serious!

The CLEANING should be done first.
#20
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok I have a technician come to look at it Tuesday morning. They are charging $70.00 to come out and do inspection, then determine what needs to be done. I hope this doesn't get pricy.
#21
Just don't let them talk you into anything with fear tactics... I'm not saying they won't find anything bad, but there's no reason that I can see in the pics that they can't clean that thing up and get it running safely for you...
#23
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
update..
technician came, inspected boiler, and cleaned it out. As he was taking it apart, parts from inside just started falling off (they weren't secured). He had to drill out screws to put everything back together, screws and bolts just snapped in half. Valves are corroded, like the shut off valves. The flame-guard has a hole burnt through it which is causing the flames to shoot out the front when it first turns on. 2 inches of ash underneath boiler from the melting metal. Burners not in good shape. Water pressure was "ok" but not as high as it should be. Temperature gauge was not working. Relay on it's way out, causing the humming noise. Only thing that was working fine was the pilot light.
Basically speaking, the boiler works, just doesn't work well. It heats the house. But it's a ticking time-bomb.
He said it's not even serviceable. Will cost more to service it than get a new boiler. Not happy! But glad I got it inspected.
He quoted me about $3,200 for a new boiler including installation. Said my set-up and zone system would be very easy to put a new one in. Does that price seem reasonable? I will surely shop around.
Is it much to put a new one in myself? With help from family? Or should I not mess around with gas lines and all of that?
technician came, inspected boiler, and cleaned it out. As he was taking it apart, parts from inside just started falling off (they weren't secured). He had to drill out screws to put everything back together, screws and bolts just snapped in half. Valves are corroded, like the shut off valves. The flame-guard has a hole burnt through it which is causing the flames to shoot out the front when it first turns on. 2 inches of ash underneath boiler from the melting metal. Burners not in good shape. Water pressure was "ok" but not as high as it should be. Temperature gauge was not working. Relay on it's way out, causing the humming noise. Only thing that was working fine was the pilot light.
Basically speaking, the boiler works, just doesn't work well. It heats the house. But it's a ticking time-bomb.
He said it's not even serviceable. Will cost more to service it than get a new boiler. Not happy! But glad I got it inspected.
He quoted me about $3,200 for a new boiler including installation. Said my set-up and zone system would be very easy to put a new one in. Does that price seem reasonable? I will surely shop around.
Is it much to put a new one in myself? With help from family? Or should I not mess around with gas lines and all of that?
#24
He at least cleaned the thing out and left you with a working boiler, correct? Didn't tear it apart and leave you with no heat, did he?
Yeah, they all say that. More than $3200 to vacuum and replace a few parts?
Around here I would think the guy quoting that price was smokin' crack... DEPENDING on the boiler he plans to install, it's not a bad price...
I don't think I would recommend it... there's just too much to learn in a short time... margin for error is too great.
By the way... to keep kitty away... you could use some wire garden fencing around the boiler.
He said it's not even serviceable. Will cost more to service it than get a new boiler.
Does that price seem reasonable?
Is it much to put a new one in myself? With help from family? Or should I not mess around with gas lines and all of that?
By the way... to keep kitty away... you could use some wire garden fencing around the boiler.
#25
The flame-guard
causing the flames to shoot out the front when it first turns on.
melting metal
Burners not in good shape
Water pressure was "ok" but not as high as it should be.
Relay on it's way out, causing the humming noise.
#27
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I meant to ask ya, but forgot... what is that piece of green garden hose for ?
Well, the service guy said the boiler isn't serviceable because the shut off valves and such on the pipes are all corroded and would have to be replace, and all the other valves. He says the time and labor to fix those issues before he can get to the boiler and take that fully apart will add up (plus the needed parts) and be about just as much as a new boiler which will work better than this 50 year old one.
I'm not saying I trust the guy, but I have a feeling just about any company I call to service the boiler will tell me the same thing and try to sell a new boiler. I can't fix it myself, so I might be out of luck. I heard that some green energy program will give you loans for energy-efficient boilers at 2% interest rate. Maybe I should look into that.
My biggest issue right now is I just opened the door to the laundry room and smelled gas, bad. Obviously a leak. Either from the boiler, or the hot water heater (that had a leak during the home inspection, seller said they fixed it.) The best thing to do is call the power company? But I'm scared with what was said earlier in this topic about power company seeing boiler and shutting off the gas at the main. We have a gas fireplace, and gas oven, gas hot water heater, and gas dryer. So if that gets shut off (15 degrees fahrenheit here) we won't be able to live here. And it might be a week or two before I can scrape together the money for a new boiler.
Um as far as flame guard, I don't know. My memory fails me but I think that's what he said it was called. He showed it to me and it was a flat piece of steel plating with a 4" burnt out hole in the middle. The "melting" was my word, sorry. He actually said it "burnt a hole through" not "melted a hole through."
#28
Member
My biggest issue right now is I just opened the door to the laundry room and smelled gas, bad. Obviously a leak.
Step 1: Call a qualified service-person, and pay him overtime to come out ASAP.
Step 2: The other alternative is to call the gas company - they will come right away, at no charge, and verify the leak - and then shut off your gas at the meter. Then go back to Step 1.
#29
2nd to gilmorrie.
Dont mess with a gas leak.
True, it doesnt take much to smell gas.. way before it gets to explosive mix levels..
BUT.. you cant tell that with your nose ! Plus, the more you are exposed to it, the less sensitive your nose will become to it.
Once you reach 100% of LEL (lower explosive level which isnt 100% gas, but the level at which it will ignite at), all it takes is an ignition point.. an appliance motor, a light switch, a smoker, etc etc
Gas leaks have blown houses into lumber bits.
Call the gas CO. If its a nice tech, and they find something simple, they might even fix it for ya (loose fitting etc).
Dont mess with a gas leak.
True, it doesnt take much to smell gas.. way before it gets to explosive mix levels..
BUT.. you cant tell that with your nose ! Plus, the more you are exposed to it, the less sensitive your nose will become to it.
Once you reach 100% of LEL (lower explosive level which isnt 100% gas, but the level at which it will ignite at), all it takes is an ignition point.. an appliance motor, a light switch, a smoker, etc etc
Gas leaks have blown houses into lumber bits.
Call the gas CO. If its a nice tech, and they find something simple, they might even fix it for ya (loose fitting etc).
#32
Member
I'm not in NY to hear the local news, but maybe he was blown up? Hope not. But, anyway, like Elvis, he seems to have left the building. I suspect we'll never hear from him again here - even after trying to help him.