Prestige Solo 110 Flush/Purge and Refill Help

Hey everyone, I am new to these forums but need some help. Yesterday my Prestige Solo 110 gave the "b 26" error code. I have tried to flush/purge the system but can't get it to get water back into it. I've lost all pressure to the system and it doesn't have water flowing through it now. I don't think I've done any damage to the heater but I don't have any money to call a serviceman but I am pretty smart and I am sure that I can figure it out with some help from you guys. I have included pictures so you can see the setup/valves that I have. Any help is much appreciated.



 
Sponsored Links
  #2  
Old 01-09-12, 02:26 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,838
Received 20 Votes on 18 Posts
Gee possible there is no water feed???

Anything look like this?



If not you may be able to fill with water from your house plumbing. I would suggest adding the above device if its not there though.

Let us know.

I know there are instructions for it somewhere, but basically you will need to run a hose to one of those boiler drains to an outside hose bib.

BUT ONLY TO 12 PSI. AND NO HIGHER THEN 30PSI WHEN ATTEMPTING THIS. HOUSE PRESSURE IS AT 40-80 PSI NORMALLY. YOU CAN BLOW SEALS AND DAMAGE YOUR UNIT.



Mike NJ
 

Last edited by NJT; 01-10-12 at 05:16 PM.
  #3  
Old 01-10-12, 03:46 PM
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Thanks for replying to my thread. The problem is the fact that I can't seem to find the water input. It was installed by a professional and I'm in a condo building so maybe my water input is somewhere else. I am going to try to look for it somewhere else. It doesn't make sense to me but maybe that's where they put it. There definitely isn't a backflow preventer on the unit so I still don't know what to do aside from find the water input valve. Urghhhh.
 
  #4  
Old 01-10-12, 03:50 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,838
Received 20 Votes on 18 Posts
Could be inside the home tied into the copper line on the baseboard somewhere. If not they may have filled it manually.


That unit is inside correct? Being in Utah and all. It looks out doors.
Mike NJ
 
  #5  
Old 01-10-12, 05:13 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
From what I can tell, code b26 refers to this:

Factory supplied LWCO device or
external limit (terminals 15 & 16) is OPEN.
Burner off for 150 seconds, auto reset.
LWCO means "Low Water Cut Off" ... so by draining the boiler, you made the low water condition even lower...

Follow the pipes, you should be able to find a fill valve somewhere... but then you may have to purge all that air in the pipes when you refill...

Since the pressure is already at zero, take the opportunity to check and recharge the expansion tank to 12 PSI before you refill the system.
 
  #6  
Old 01-10-12, 05:48 PM
Join Date: Dec 2011
Location: Usa
Posts: 67
Received 0 Votes on 0 Posts
Looks like you could fill it via the red handle drain hose bibs, open the T&P valve on top right of cover to let air out as you do it.

Also where is your condensate P-trap that comes with unit?
 
  #7  
Old 01-10-12, 06:00 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
Also where is your condensate P-trap that comes with unit?
If I'm not mistaken, that 3" PVC with the duct tape on it is open on top, and the condensate just drips down in to it... kinda hokey if ya ask me.
 
  #8  
Old 01-10-12, 06:14 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,936
Received 1 Vote on 1 Post
Look at how close the boiler is to the gas meter. Musta been installed by the world's largest HVAC company, GTM&R. That's Get The Money & Run.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: