Adding additional transformer to Honeywell L8148E aquastat

I have replaced the 3 original B&G Modumate zone valves, with the new B&G Comfort-Trol zone valves. Shortly after installing these my transformer burned up in my aquastat. The instructions which came with the new zone valves stated not to use more than three with the aquastat but suggested using an additional transformer to power the zone valves. My question is how do I wire up the additional transformer to the aquastat. Would it be used in series with the built in transformer? I bought a new Honeywell 8148E aquastat and a new 40VA transformer to go with it. I am running a Burnham gas fired boiler with a standing pilot and a vent damper. Any suggestions are appreciated.
 
Sponsored Links
  #2  
Old 01-26-12, 12:35 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
Follow figure 2A in this PDF file.

http://completewatersystems.com/wp-c...011/05/604.pdf

NO, do NOT wire the transformer in series!
 
  #3  
Old 01-26-12, 03:20 PM
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Thanks for the quick reply, I have another question though, after looking at the diagram on the B&G link, are the "T" terminals on the aquastat already be supplied 24v from the internal transformer? If so what will happen by adding this additional transformer? I don't want to smoke another aquastat!
 
  #4  
Old 01-26-12, 03:52 PM
Member
Join Date: Oct 2008
Location: USA
Posts: 2,897
Received 5 Votes on 5 Posts
NO, do NOT wire the transformer in series!
For different reasons that don't need explaining here, don't try to wire two transformers' 24-V secondaries in parallel, either. You need to use separate, 40-VA, unconnected xfmrs for each three (or fewer) valves. The 120-V primaries will, of course, be in parallel.
 
  #5  
Old 01-26-12, 04:31 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
what will happen by adding this additional transformer?
The additional transformer will power the zone valves, the transformer in the aquastat will power the aquastat. As long as you wire it as shown and make no mistakes, you will not fry the aquastat.

Note that in your aquastat, the "T" terminals are probably labeled "T" and "TV"
 
  #6  
Old 01-27-12, 09:37 AM
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Yes, the "T" terminals are labeled "T" and "TV". Thanks very much for the info. I plan on working on it this weekend.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: