No heate! radiant floor system


  #1  
Old 02-19-12, 07:38 AM
H
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 11
Received 0 Votes on 0 Posts
Unhappy No heate! radiant floor system

My "Mini-Boiler WarmFlo" is not heating pumps are running and circulating but the water coming out of the boiler is only 60 degrees,

has been installed for seven years first time there has ever been a problem

there is water in the system 10 lbs of pressure and

there is power to the boiler thanks
 
  #2  
Old 02-19-12, 07:54 AM
P
Member
Join Date: Feb 2011
Location: US
Posts: 552
Received 0 Votes on 0 Posts
Possible that the oil tank is empty?
 
  #3  
Old 02-19-12, 08:02 AM
H
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 11
Received 0 Votes on 0 Posts
It is an electric boiler...
 
  #4  
Old 02-19-12, 08:13 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
What size boiler? i.e. model number?.............
 
  #5  
Old 02-19-12, 08:22 AM
H
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 11
Received 0 Votes on 0 Posts
  #6  
Old 02-19-12, 08:32 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
EMB-S-9 or EMB-H-9 ? ....................
 
  #7  
Old 02-19-12, 08:38 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
Have you found the reset button? Have you pushed it?

WARNING! HIGH VOLTAGE PRESENT, YOU CAN BE KILLED!
 
  #8  
Old 02-19-12, 08:39 AM
H
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 11
Received 0 Votes on 0 Posts
the actual sticker on the unit says
EMB-w-90
but I always thought it was an EMB-H- 9
 
  #9  
Old 02-19-12, 08:50 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
  #10  
Old 02-19-12, 08:52 AM
H
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 11
Received 0 Votes on 0 Posts
Originally Posted by NJ Trooper View Post
Have you found the reset button? Have you pushed it?

WARNING! HIGH VOLTAGE PRESENT, YOU CAN BE KILLED!

NO
I can not find it, I have looked searched the manual and it mentions it but no location...
 
  #11  
Old 02-19-12, 08:55 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
How about the 'status LEDs' ? What are they telling you?
 
  #12  
Old 02-19-12, 08:59 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
Can you tell if the circulator pump is running or not?
 
  #13  
Old 02-19-12, 09:18 AM
H
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 11
Received 0 Votes on 0 Posts
Originally Posted by NJ Trooper View Post
Can you tell if the circulator pump is running or not?
found the reset button it looks like it is in , does not push in any farther

circulator pumps are running
lights are
160 auto reset,
off peak
mini boiler on
 
  #14  
Old 02-19-12, 09:24 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
I know what lights are on the boiler, but are you saying that all those lights are ON ?

If the 160 auto reset is lit, and the water is at 60, then there's a problem with that circuit at the very least. It may be a faulty temperature sensor. That one should AUTOMATICALLY reset when the boiler cools to 120...
 
  #15  
Old 02-19-12, 09:26 AM
H
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 11
Received 0 Votes on 0 Posts
now the auto reset light has gone out and the heater is running for the moment...


lets hope it runs long enough to keep the house warm , like untill the month of May
 
  #16  
Old 02-19-12, 09:41 AM
H
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 11
Received 0 Votes on 0 Posts
If the 160 auto reset is lit, and the water is at 60, then there's a problem

My thoughts exactly!


now the water is up to 80, yee haa!!
 
  #17  
Old 02-19-12, 09:42 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
This concerns me... yes, I hope it works until May... but typically, well, never mind.

It sounds as if that 160 limit switch is 'flaky'. Fortunately, it's probably not an expensive part, but obtaining one might be not so easy. It's just a sensor on top of the tank, and has two red/white wires coming down to the circuit board.

Do you own and know how to use a multi-meter?

Is the off-peak still on? Has that light always been on?

Do you have the boiler connected to the power company load monitoring equipment? OR is there a blue jumper on terminals on TB1 ?
 
  #18  
Old 02-19-12, 10:12 AM
H
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 11
Received 0 Votes on 0 Posts
NJ Trooper
THANKS!

Of peak light is always on and I reinstalled the blue jumper wire just to take that out of the equation

I do have a couple digital multi meters
just tell em what to do...
thanks!
 
  #19  
Old 02-19-12, 10:27 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
The next time you have the problem, set the multimeter to measure continuity, pull the red and white wires and see if the 160 sensor is open or closed...

When that sensor reaches 160 it OPENS, and should close again at 120.

I wonder if the temp gauge is whack?

In normal operation, I don't think there should be a reason for that to trip.

What setting do you have on the switch next to the blue jumper?
 
  #20  
Old 02-19-12, 10:29 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
I think if that jumper is removed the boiler will still operate, but it will only run at half capacity... I think. Not sure... but that's kinda what the manual seems to say.
 
  #21  
Old 02-19-12, 10:45 AM
H
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 11
Received 0 Votes on 0 Posts
the boiler is set on 5 (135 degrees)

Are these mini boilers dependable?
I talked to the power company who supplied it to me and they say they quit selling them

When I did plumb the unit I did set it up to incorporate a a second heat source. Now am thinking of adding one of those super insulated 80 gallon water heaters,
I wonder if that would be more efficient since my electric rates have doubled in the past 7 years
 
  #22  
Old 02-19-12, 12:51 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
Are these mini boilers dependable?
I dunno really... never seen one... but yours has run for 7 years without trouble, that's not too shabby.

Now am thinking of adding one of those super insulated 80 gallon water heaters,
Safe to assume that you mean a gas fired water heater? If you do use a water heater, please make sure it's got the " H " rating to be used as a home heating appliance.

By the way, 10 PSI may be OK if your boiler is above all the heating pipes, but generally speaking, it's a bit on the low side. Is this a one story with only radiant in the bottom floor?
 
  #23  
Old 02-19-12, 02:10 PM
H
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 11
Received 0 Votes on 0 Posts
I was thinking a Marathon water heater
Marathon Water Heaters: For Consumers

the mini boiler is in the basement and heats the two floors above it with radiant infloor heat, staple up method
10 psi when cold and then increases to about 15 when hot

also when cold one pressure gauge reads 10 psi and the other reads 20 these are gauges that measure temp and pressure
 
  #24  
Old 02-19-12, 03:10 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,538
Received 7 Votes on 5 Posts
I am quite sure that the Marathon's are not H rated.

You are aware that it's a plastic tank, correct?

The other thing to consider is that it's still electric! I don't really understand how that's going to be a savings for you, and these heaters are quite pricey. I think the 40 gallon was between 800-900 when I priced them several years ago. I'm sure the 85 gallon will be well over a grand.

Also, these are only 4500 watts. Which is HALF what your current boiler is. That's only around 15000 BTU and probably not enough to heat your home.

It would seem that one, or both, of your pressure gauges is not accurate!
 
 