Purchasing gas boiler to replace oil

We are new owners of a 1700 colonial and the heating system is being converted from oil to gas. The boiler recommended is a Weil McLain standing pilot 4 section. The current owner will replace it, and has had a WM oil burner for 20 years with no problems. He is thoughtful and generous, and I'm just doing my due diligence in researching in case there is something better (as in more reliable; not looking for the top of the line). Thank you for your thoughts.
 
  #2  
Old 07-04-12, 08:25 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Before replacing ANY boiler, a thorough HEAT LOSS CALCULATION should be performed. The house is OLD, so may well have high heat loss, but chances are that replacing the current boiler with the same BTU output may be a mistake. Surely the home has been 'improved' with insulation and air leak sealing and all that...

Read this 'sticky' post:

http://www.doityourself.com/forum/bo...nt-boiler.html

How many square feet is the home? How many BTU on the current boiler nameplate?

Why put a 'too large' boiler in place and pay for the extra fuel the rest of the time you live there?

Check out the Burnham ES2 and see what you think.
 
  #3  
Old 07-04-12, 06:48 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,407
Upvotes: 0
Received 66 Upvotes on 55 Posts
I totally agree with Trooper about the heat loss. Proper sizing of the boilers is te greatest fuel savings. I cannot speak for this particular boiler but most old existing boilers are 100% or more oversized.

The US Boiler ES2, ESC and Series 3 boilers will have an updated control next month to meet the new 2012 compliance standards. The efficiency will not change but updates will be made to the control. The updates will add fuel savings automatically and make some of the wiring easier.
 
  #4  
Old 07-05-12, 11:53 AM
O
Member
Join Date: Jun 2008
Location: Rockville MD
Posts: 101
Upvotes: 0
Received 0 Upvotes on 0 Posts
rbeck,
Are they just including the optional ODR as standard equipment now, or are there additional changes? I have to say we are very happy with the ES2 boiler we put in last year.
 
  #5  
Old 07-06-12, 06:45 PM
I
Member
Join Date: Nov 2010
Location: USA
Posts: 42
Upvotes: 0
Received 0 Upvotes on 0 Posts
Is this steam or hot water?
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: