Can open vent damper extinguish pilot light?

Hi,
My gas fired steam boiler occasionally does not fire because of auto vent damper. I did verify that the motor (model GVD-8) does turn vent damper open when thermostat requires heat, but sometimes apparently it does not activate a button (when I slightly shake the dumper blade the boiler fires). I moved vent damper switch to "hold open" position, so it always stay open, which seems to work for me. However, my plumber said that when vent is always open it can extinguish the pilot light. I wonder if anyone experienced this? The manual says the auto vent damper is just for better boiler efficiency. Are there any negative effects of keeping vent damp always open?
 
Sponsored Links
  #2  
Old 11-15-12, 09:08 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,425
Upvotes Received: 213
Keeping that vent damper on hold open is allowing your heating dollars to float up the chimney. When the damper opens it hits a switch that tells the burner that since the vent is fully open it can fire. It could be out of mechanical alignment or that microswitch is shot, I'm not sure if keeping the damper open will cause the pilot to extinguish.... I wouldn't think so.
 
  #3  
Old 11-15-12, 09:27 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: Pennsylvania
Posts: 2,444
Upvotes Received: 1
Keeping the damper open will not extinguish the pilot. Boilers ran for years without vent dampers.
 
  #4  
Old 11-16-12, 06:14 AM
Member
Thread Starter
Join Date: Dec 2010
Location: usa
Posts: 42
Thanks everybody for the replies.

@PJmax >>... When the damper opens it hits a switch that tells the burner that since the vent is fully open it can fire. It could be out of mechanical alignment or that microswitch is shot...<<

Where is this microswitch located-- inside the vent pipe or inside the motor assembly?
 
  #5  
Old 11-16-12, 01:21 PM
Member
Join Date: Oct 2008
Location: USA
Posts: 2,862
Upvotes Received: 5
I think your plumber is misinformed. But, sometimes a very strong wind can blow out a pilot on a unit not equipped with vent damper, so I guess it could with a vent damper held open. You need to get the vent damper fixed or, better yet, replaced.
 
  #6  
Old 11-16-12, 02:42 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Upvotes Received: 1
I would probably also recommend replacement rather than repair. That's something you don't want 'messing up' on you.

But, if you feel you have the skills to do a proper repair and can locate a replacement microswitch, well, that's your call.
 