Hot water radiator(s) don't heat properly

Hi,
I have a two unit rental property with forced hot water heating. Each unit has its own boiler.

It seems that 2 of the 4 radiators on the 2nd floor are not heating up properly or are heating erratically. I was just at the apartment and the temperature throughout was fine and as set by the thermostat.

I bled the rads - no air.

The two boilers were serviced last year.

Any thoughts. - wondering about the valves.

Nick
 
Sponsored Links
  #2  
Old 11-15-12, 09:26 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,159
Received 374 Votes on 351 Posts
Which valves were you wondering about ? Normally on a hot water heating system there aren't valves on the radiators.
 
  #3  
Old 11-15-12, 09:29 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,833
Received 19 Votes on 17 Posts
It would most certainly seem like air. You would tell by how the system is piped.

If piped in a loop , if the first rads are hot the others would be also. I would say it may be a mono flo tee set up?

Possibly also since its the second floor the PSI in the boiler could be low.

Last it could be a split loop also with a common return.


What is the PSI and temp say on the boiler gauge? How does the air elimation device look on the boiler?

What is the make and model of the boiler?


Take pics.... Or you can always call your service guy....
 
  #4  
Old 11-15-12, 09:30 PM
Member
Thread Starter
Join Date: Jun 2012
Posts: 19
Received 0 Votes on 0 Posts
The valve - if that is the correct term- to regulate the water inflow to each radiator.
 
  #5  
Old 11-15-12, 09:47 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,833
Received 19 Votes on 17 Posts
Those valves should be left open. Possibly one was broke? Does the valve just turn and turn and not stop open or closed?
 
  #6  
Old 11-16-12, 09:55 AM
Member
Thread Starter
Join Date: Jun 2012
Posts: 19
Received 0 Votes on 0 Posts
Thanks for the replies.
Both boilers are Crown Boiler Model ABF 105 PPD

The PSI and temp on the 2nd floor boiler are 20 psi and 180 degree (1st floor is about 10 psi)
The valve on one of the 2nd floor rads did spin, but I think it stopped. I'll check. Wondering if the shaft broke in the "off" position.

Also, I noticed that there is a drip from the pipe connected to the pressure release valve on the 1st floor boiler. I releleased the valve and let out a bucket of water, but it still drips.

Thanks,
Nick
 
  #7  
Old 11-16-12, 03:55 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
Hi Nick,

Please read both of the following posts:

http://www.doityourself.com/forum/bo...sion-tank.html

http://www.doityourself.com/forum/bo...ure-gauge.html

If the pressure relief valve on a boiler with a gauge that is reading 10 PSI is dripping, you need to find out why. It could be the gauge is bad, it could be the relief valve is bad, it could be the expansion tank is bad. Or... all THREE.

It's very possible the gauge on the second boiler is defective as well. If there is low pressure in the boiler the water won't be pumped properly through the upper floors.

Check the gauges first. Don't presume that because they were serviced that the tech checked the gauges. I guarantee that he did NOT. I also guarantee that he did not check or adjust the expansion tank air charge.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: