Heating system gone mad! Please help!

I have a Laars Endurance Heating System (model EBP-110) currently in my condo. It was installed on 10-24-03, well before I moved in (2007). The other day my heat went dead. I still had hot water though. Figuring it was the cheap $20 Honeywell thermostat that I installed when I moved in, I replaced it.

I marked what I saw with the wires. White wire to W, red wire to Rh. I purchased an almost identical Honeywell and no change. I'd have the temp set to 72, and you'd head it click. But it wouldn't call for heat on the spot. After 30 minutes of waiting, the only way to get it going was to turn the system off then back on, reset used to work but now for some reason it doesn't.

If I removed the thermostat and connected the wires it would run unregulated. Didn't know if it THAT thermostat was bad...

So we had a family friend come take a look at it. He wasn't 100% as he mostly works with oil, and wasn't too familiar first hand with Laars. But he said that from what he's heard, they're a PIA to fix and parts are really expensive. Oy...

He bled the system and replaced the circulator pump as the needle on the testing thing was going extremely slow. 10 minutes later all pipes were scolding hot, and radiators were hot. It worked.

I took back the Honeywell and installed a Lux TX9100U because of National Grids $35 rebate. We like the house warmer so I set every day and time frame at 72.

So today we were moving stuff in and out and the door was open, it dropped a few degrees. The system started right up it went from 67 to 70, then it went quiet for a bit. A few minutes later it started up again and hit 72 and stayed there until I went to bed at 11am. I work 3rd shift so my sleeping is erratic.

Woke up at 6 and felt the cold right away, it was 65. Double checked the programming, maybe I missed a setting? Nope still set at 72. Gave it a another hour, never kicked on.

I had to go back to the heater and turn it off and on again. The heat is back up to 71.

This seems to be the theme. Once it drops below the set temperature, the thermostat won't control it. It has to be switched off then on, I'd say reset but like I mentioned that doesn't work.

PSI is about 20, and it requires a minimum of 12 to run properly.

Any insight would be a great help! Thanks
 
Sponsored Links
  #2  
Old 11-30-12, 06:48 PM
Member
Join Date: Oct 2008
Location: USA
Posts: 2,897
Received 5 Votes on 5 Posts
Michael, I sense you are in the U.K., where heating practices a quite a bit different than in the U.S., where most of us here are located. But, thermostats are the first thing suspected and replaced, becuase they are so easy and conspicuous - but a are seldom the problem.
 
  #3  
Old 11-30-12, 06:50 PM
Member
Thread Starter
Join Date: Nov 2012
Posts: 3
Received 0 Votes on 0 Posts
I'm actually in Rhode Island.
 
  #4  
Old 11-30-12, 07:03 PM
Member
Join Date: Aug 2009
Location: USA
Posts: 4,947
Received 0 Votes on 0 Posts
Why was your circulator replaced?

What is the temperature and pressure of your boiler?

What kind of radiators do you have?

the needle on the testing thing was going extremely slow
What testing thing?
 
  #5  
Old 11-30-12, 07:06 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
Michael, I've gotta run out for a few, in the meantime see if you can locate a manual for your boiler on line and drop a link here for us to look at.
 
  #6  
Old 11-30-12, 07:12 PM
Member
Thread Starter
Join Date: Nov 2012
Posts: 3
Received 0 Votes on 0 Posts
He put something next to the circulator pump that spins, it was barely spinning.

BFT is 183, PSI is reading approximately 21.

I've got baseboard radiators.

Here's the manual.

http://www.laars.com/LinkClick.aspx?...=1893&mid=6434
 
  #7  
Old 11-30-12, 07:16 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,489
Received 32 Votes on 24 Posts
Turning the power off and then back on making it work okay signifies a "soft lockout" device is causing the problem. Could be as simple as the flame detecting device is not always sensing the flame on start up.
 
  #9  
Old 11-30-12, 07:48 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,489
Received 32 Votes on 24 Posts
The user manual is of no use, I need the installation and service manual.
 
  #10  
Old 12-01-12, 09:16 AM
BillD27's Avatar
Member
Join Date: Feb 2010
Location: USA
Posts: 27
Received 0 Votes on 0 Posts
This looks like EDP Install manual:
http://www.laars.com/LinkClick.aspx?...=1892&mid=6433
 
  #11  
Old 12-01-12, 11:14 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
Thanks Bill!

Do the boiler controls show any fault codes when the problem occurs? If so, what are they?

(refer to manual for more information about fault codes)
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: