Circ pump question

Almost two years ago, I installed a Tekmar 260....which is working just fine.

However, in this thread:

http://www.doityourself.com/forum/bo...ermostats.html


I mentioned that my single circ pump(a taco 007) does dead head a bit while the DHW zone valve opens up. It's been like that for two years, and it's still running fine, but I can't help but wonder if the pump is going to have an early failure due to the dead head?

So my question is....instead of installing a second pump just for the DHW, would an Alpha circ pump work in this situation? It's my understanding that it can sense the low flow, and adjust it's output to match.

Seems like I might save a bit on the electric bill as well.
 
Sponsored Links
  #2  
Old 01-03-13, 03:05 PM
Member
Join Date: Oct 2008
Location: USA
Posts: 2,925
Received 8 Votes on 8 Posts
It won't be a problem. If it operated at shutoff head for a long duration, the plastic impeller might possibly overheat with no flow through the pump. You wouldn't save any electric energy - for one reason, a centrifugal pump consumes the least power at shutoff head. Not to worry.
 
  #3  
Old 01-04-13, 07:29 AM
Member
Thread Starter
Join Date: Sep 2008
Location: USA
Posts: 140
Received 0 Votes on 0 Posts
Thanks for the info. During heating season, the two heating zone valves are usually open most of the time. The indoor sensor on the Tekmar controls the room temp, so the t-stats are set 2 above the tekmar setpoint. Dead heading is not usually an issues during heating season.

During the off season though, is when I'll have about 1 minute of dead head time while the zone valve for DHW zone is opening. The tekmar wants to run the circ pump as soon as it gets a DHW call.
 
  #4  
Old 01-04-13, 08:19 AM
Member
Join Date: Oct 2008
Location: USA
Posts: 2,925
Received 8 Votes on 8 Posts
I wouldn't worry about operating the pump at shutoff head for one minute.
 
  #5  
Old 01-04-13, 03:50 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
I wouldn't be concerned about it either...
 
  #6  
Old 01-04-13, 04:39 PM
Member
Join Date: Oct 2008
Location: USA
Posts: 2,925
Received 8 Votes on 8 Posts
Taco 00-series pumps use a polypropylene impeller, which is good for at least 275 deg F. If you ran the pump at shutoff head for long enough, much longer than a minute, the water in the volute could heat up, form steam, and possibly damage the impeller.

On general principles, I keep a replacement pump cartridge on hand - it is the only moving part, and includes the impeller. If the pump shoots craps on Super Bowl Sunday, I can replace the cartridge in a matter of minutes (since I have isolation valves on each side of the pump). I also have a spare motor capacitor and a back-up generator. Beyond that, I could jack open my two flo-control valves, and go to gravity flow, assuming I still have natural gas. I'm sure there is another gotcha out there waiting to strike that I haven't thought of.
 
  #7  
Old 01-04-13, 05:12 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
I'm sure there is another gotcha out there waiting to strike that I haven't thought of.
Don't forget what's gonna happen on Dec 21, 2012 ! Or the New Madrid fault... or Yellowstone... or Nibiru...

The water flow also cools the motor to a degree so that could be damaged in the long term as well, but 1 minute of DH won't hurt a thing.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: