Aquastat L7224/L7248 disable for water when tankless hot water heater installed
Old 02-07-13, 05:40 PM
A
I moved into a house recently with only oil hookup. I have a Crown TZW100 boiler that heats my home baseboard radiators and also my water (sinks, showers, dishwasher, washer, etc.). The unit cycles to keep hot water available for use. This was getting expensive so I looked into a separate hot water heater. The current boiler wasn't keeping the water temp hot throughout a shower. (I figure I am putting out too much gpm). Decided to go with a tankless hot water heater. I need to know how to prevent my current boiler from trying to heat water. I will only need it during winter for heat. I have an Aquastat L7224/L7248 control connected.
Anyone know how this can be done? Thanks
Old 02-07-13, 07:23 PM
NJT's Avatar
NJT
NJT is offline
Received 3 Votes on 2 Posts
Take a look and see if this helps you out...
You need to turn the "LOW LIMIT" to OFF.
Leave the HIGH LIMIT set at 180.
https://customer.honeywell.com/resou...0s/68-0281.pdf
Your unit may be an older one and some of the features that are in this manual may not (will not) be available on your aquastat due to firmware changes made over the years.
Old 02-07-13, 07:33 PM
NJT's Avatar
NJT
NJT is offline
The newer models of the 7224 allow turning off the Low Limit, but I just scanned this manual and did not see instructions for doing so. It's possible that all you will be able to do is turn it down to 110 ... you might have to change a'stats in order to defeat the low limit on yours.
Old 02-09-13, 10:03 AM
A
Thanks...doesn't look like I can turn it off. I did lower it to 110. In the process of connecting the water heater. I'll see what happens and look into another aquastat. Again thanks for the help.
Old 02-09-13, 11:13 AM
A
Aquastat only drops to 110. Unit still turns on, but not as often. Do you think I could tie my hot water line into it? That would make it so hot water was going into the coil and the temperature wouldn't drop enough for the unit to kick on. Wondering if you have heard of this before or if you think it might damage something. Thanks
Old 02-09-13, 02:05 PM
NJT's Avatar
NJT
NJT is offline
You mean the hot water out of the new heater? Through the boiler and then to the home?
No, that makes no sense. All you would succeed in doing is cooling the hot water to the home (if the boiler is cooler than the hot water) and heating the boiler with the water heater.
I've heard and seen ALL KINDS of weird things!
Old 02-09-13, 03:18 PM
A
The way I was looking to set it up was so that there would be no cold water line going in. The hot water heated in the boiler would just cycle right back into the boiler. The water would be hot so the boiler won't need to heat it and it won't turn on.
The new tankless heater is connected after the boiler line so the hot water line out of my boiler is useless now. I just don't know how to prevent it from heating water that I don't need...thus wasting oil.
Old 02-09-13, 03:29 PM
NJT's Avatar
NJT
NJT is offline
Sorry, I'm still not following you.
You are thinking of connecting the two pipes on the boiler together? No, don't do that.
When you disconnect the pipes from the boiler, leave them OPEN, don't even cap them. If you do put caps on them, don't solder them, just slip them on and leave them.
No matter what you do, whether or not you flow water through the coil, the boiler will still fire up whenever it cools below it's LOW setpoint.
If you can't turn 'off' the low limit on your aquastat, the only thing you can do is change the aquastat.
Old 02-09-13, 03:32 PM
NJT's Avatar
NJT
NJT is offline
This one allows you to turn OFF the LOW LIMIT if not needed:
L7224U1002 - Honeywell L7224U1002 - 120 Vac Oil Electronic Aquastat
Old 02-09-13, 05:50 PM
A
Thanks for clearing things up. I'll probably just pick up that aquastat. I appreciate your help.
Old 02-09-13, 09:37 PM
G
Kinda of the same thing as you, but we just poped on a shark bite shut off on the hot side. We were pulling a lot of hot water with the tankless and old oil setup.Low limit down to 90. This also lets your boiler run every so often and if you need to you can fall back if the tankless acts up. Just open your shut off and your back to having hot water.
Old 02-09-13, 09:41 PM
G
Also don't cut your water line into the boiler. Not sure about your setup, but there might be an auto feed for the system, plus service if you ever drain it. How are you going to refill the system?