SR502 w/ Taco 571's

Old setup: Transformer powers 3 zone valves/thermostats then connected to TT on old L8124C. R845A was connected to the "B" terminal on the high limit. Tstats called, B1/B2 powered up, burner fired, C1/C2 powered up, and system circ ran. R845A called, turned on burner through the high limit, only indirect circ ran.

C1/C2 stopped firing on the old L8124, so I replaced it with a L7248C we had, put on an SR502. I have the indirect circ wired in and tank's aquastat wired in, have the power on, have everything wired right, but stopped when I got to putting in the old TT from the zone valve set up, thinking the two transformers would fight each other. Do I need to disconnect the old transformer?

Thanks
 
Sponsored Links
  #2  
Old 02-08-13, 07:18 PM
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
never mind, found on an old wiring diagram of Taco's that the two transformer circuits are separated, wired it in and I have heat.
 