Will This Work

After the last power outage of 5 days, I'm going to convert my generator from Gasoline to propane. I have a 3/4" live feeding a TT solo 60 boiler, I want to know if I can also run a 16hp gen off that line too or am I going to have to upsize to a larger gas pipe, the boiler is using 13"WC pressure.
 
Sponsored Links
  #2  
Old 03-21-13, 07:57 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,145
Received 60 Votes on 52 Posts
Probably not.... How many feet from the tank? What else is on the line?

I probable would not even consider it. That 16hp engine and gen manufacturer probably suggests a separate 500 gallon tank min. Even with propane that gen will consume maybe 2.5 gallons an hour.

Whats make and model gen?

Whats this mean?

3/4" live
 
  #3  
Old 03-21-13, 11:48 AM
T
Member
Join Date: Jul 2009
Location: Toronto
Posts: 1,174
Received 0 Votes on 0 Posts
This is like asking if a car will do 200 MPH. A corvette, ya maybe a hyundia... NO.
Point is there is not enough INFO.
First, 25 HP coverts to 63610 BTU per hour, but that does not factor any effec. into this.

First question, how many BTU will the generate want in order to run ?
Second, yes a 3/4" line... how long is it from the reg to the point where you will want to branch off.

We just do not have enough info to answer the questions... it's your toys you can do it by trial and error if you wish. You should have a manometer in order to know if both will operate according to what the man. wants to see
 
  #4  
Old 03-21-13, 02:13 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 35 Votes on 27 Posts
As TO wrote, you need to supply much more information. The general rule of thumb is that for every horsepower of the engine you need 10,000 BTUs of gaseous fuel available to ensure full output. That would mean for your 16 horsepower generator you would need 160,000 BTUs available at the engine.

Add to this the 60,000 BTUs (maximum) needed by the boiler and you need a total of 220,000 BTUs supply. Standard charts state that a 3/4 inch pipe will carry 231,000 BTUs for 60 feet developed length at 11 inches water column of pressure. Developed length includes the flow restriction factor of any fittings and for 90 degree elbows figure a loss of about ten feet for every elbow.

Now this is all predicated on the tank piping and high pressure regulator having sufficient capacity in the first place.
 
  #5  
Old 03-21-13, 02:21 PM
D
Member
Thread Starter
Join Date: Feb 2008
Location: Western Va.
Posts: 28
Received 0 Votes on 0 Posts
Thanks for the replies: I'm approx 30' from my propane tank there are 2 regulators one on the tank and one just before it the gas line enters the house from that reg. approx 12 ' to where I want to tap into the line, there is nothing else on the line but my 60K boiler, Im not sure how many btu's the generator will need as I haven't converted it yet. I do have a manometer I'll check the pressure with both items running.
 
  #6  
Old 03-21-13, 04:05 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
I don't know a whole lot about LPG... so beat me up if I'm wrong... but I think these points also need to be considered:

I believe that the surface area of the LP inside the tank has to be large enough to be able to 'boil' the LIQUID into a GAS at a rate fast enough for all appliances on the circuit... I think this is one reason that LPG tanks used for high output appliances are HORIZONTAL... more surface area inside the tank, and this in ADDITION to the size of the piping.

If the tank is above ground, outdoor temperature plays a part in the rate at which the LIQ turns to GAS as well. Below ground tank, if deep enough, is not as affected by outdoor temps.
 
  #7  
Old 03-21-13, 04:18 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 35 Votes on 27 Posts
You're not wrong, Trooper and those are good points to remember. While uncommon with air-cooled engines, using a liquid feed LPG to a water heated vaporizer/zero governor is quite common on liquid-cooled engines. Some stationary installations will have a fired vaporizer to boil liquid LPG to gaseous state. These are definitely NOT DIY friendly.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: