Reverse Return

Is there a point where reverse return piping for the radiators on a hot water boiler system really does not make a difference like if you are over piped?
 
Sponsored Links
  #2  
Old 05-08-13, 06:13 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
Hi Ziz!

Not sure what you mean by this?

if you are over piped?
What is "over piped"?
 
  #3  
Old 05-09-13, 05:44 AM
Z
Member
Thread Starter
Join Date: Oct 2008
Location: NYC
Posts: 433
Received 0 Votes on 0 Posts
What i mean is if the rads are for 100k btu and you pipe them for 1500k btu. If you use larger than necessary pipes.
 
  #4  
Old 05-09-13, 06:41 AM
G
Member
Join Date: Oct 2008
Location: USA
Posts: 2,969
Received 10 Votes on 10 Posts
What i mean is if the rads are for 100k btu and you pipe them for 1500k btu.
I don't understand what you are talking about.
 
  #5  
Old 05-09-13, 06:57 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
I think I understand, correct me if I'm wrong Ziz...

If the Supply and Return pipes are overSIZEd from the minimum they would need to be for the attached emitters...

With reverse return, the point isn't really about 'flow', it's about 'distance' and 'balancing'.

Reverse return piping allows the total distance from the boiler to any rad and back to the boiler to be equal, thus balancing the flow through each rad.

As long as the flow is proper, there should be no 'issues'.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: