Low pressure on shared solar/gas DHW

Hello, thanks for doing this. I have just signed on.

I manage a combined space heating and domestic hot water system which serves four households plus the common space in our cohousing community. 160 vacuum tubes on the roof heat two 120 USG storage tanks containing potable water, and those feed into a gas boiler. The boiler is a Triangle Tube Delta. I am unable to verify the model number (doesn't seem to be written on the unit and I have temporarily misplaced the manual).

The system is 9 years old although we have made some modifications in the meantime. Two years ago I had a plumber replace the temperature control valve at the boiler, because water temperatures were fluctuating. He did not replace it with the original model.

This past week we had low temperature and low pressure on the hot water. I checked and the tempering valve was putting out only cold water, although hot water was coming to the valve. I got the same model as the one that was installed 2 years ago, and installed it. It is a Watts Series 1170C-M2. Since then, the water is hot enough but the pressure is very low at times. It seems to be fine for some hours, then low. The cold water pressure is fine. I did check, when installing the new valve for obstructions in the pipes coming in (flowed some water out to make sure it wasn't crapped up).

I have checked the pressure on city water coming into the system and it's at 40 psi.

Any suggestions as to how this problem might be caused and how to rectify it?
 
Sponsored Links
  #2  
Old 06-04-13, 11:45 AM
O
Member
Thread Starter
Join Date: Jun 2013
Location: Canada
Posts: 2
Received 0 Votes on 0 Posts
P.S. I took out the new tempering valve and ran a little water through the 3 lines connected to it, to check for obstructions. I did not find any. So far I believe it's behaving the same. Pressure OK at first, then drops.
 
  #3  
Old 06-04-13, 11:46 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,145
Received 60 Votes on 52 Posts
We probably would need a diagram to see how things are piped. Pics may help but its probably a hodge podge of stuff and pics will not tell the whole picture.

40 psi is low incoming water IMO. Possibly you have a PRV valve gone bad?? That should be near where the main comes into the home.

Posibly an old gate valve broke and is not fully open?

Just some thoughts....
 
  #4  
Old 06-04-13, 04:43 PM
T
Member
Join Date: Jul 2009
Location: Toronto
Posts: 1,174
Received 0 Votes on 0 Posts
Your delta will be a PG 25,35, or 45.
100,000 to 199,000 BTU input.
There were some modulating deltas sold just prior to the end of the model.

I seem to get the balance of the delta service in Ontario, which is a double edged sword...

If you can get some pics of the system piping we might be able to help better.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: