Arrow How many feet , wood floorsof Hydronic baseboard?

I'm renovating two rooms in a 230 yr old home in NH. The first is a NW facing bedroom of about 185 sq ft / 1290 cu ft, with about 25 ft of exterior wall, 35 sq ft of single-glazed windows with well-fitting exterior storms. There is no insulation in exterior walls, but blown-in insulation in the ceiling plus a 9 in attic cap. Wood floors. There are currently about 25 feet of hydronic baseboard. I recently removed about 8 ft in the renovation, and am reluctant to add more, as I am at, if not above the 67 ft guideline for 3/4 in baseboard and have had two previous boiler failures due to acid corrosion.. Will the current 25ft be sufficient?
The second room is a newly renovated bathroom of about 70 sq. ft. / 490 cu ft. About 7 ft of exterior wall and a new 11.75 sq.ft energy star window. All walls, including interior walls will be insulated, as is the ceiling, as in the other room. Electrically heated slated floor and radiant heat-lamp / fan. I am planning 10 ft of hydronic base board. Will that be sufficient?
 
Sponsored Links
  #2  
Old 06-20-13, 03:35 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
Hi Doc, download the SlantFin Heat loss package

http://www.doityourself.com/forum/bo...alculator.html

and run the numbers.
 
  #3  
Old 06-20-13, 05:12 PM
Member
Join Date: Jul 2009
Location: Toronto
Posts: 1,174
Received 0 Votes on 0 Posts
The boiler failures are not due to too much or too little baseboard. They are a function of too low of a return water temperature. You are condensing the flue gas.
A boiler bypass or some form of boiler protection is in order.
 
  #4  
Old 06-21-13, 10:15 AM
Member
Thread Starter
Join Date: Apr 2013
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
I understand that, but too many feet of baseboard is what causes the return temperature to be too low. The last boiler replacement included the addition of a boiler bypass. After I posted yesterday, I measured the baseboards on that zone, and there are 93 ft!! Although 17ft of that is enclosed in closets and under a window seat, that is still way too much!
 
  #5  
Old 06-21-13, 10:20 AM
Member
Thread Starter
Join Date: Apr 2013
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
Thank You! That is what I am looking for and I will consult it.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: