Indirect superstore tank not turning on circulator

Hi,
Woke up this morning to luke warm water. Thought maybe the oil fired boiler tripped the reset, but that wasn't the case. The 4 heating zones work fine. Turn up the thermostat, boiler fires up, circulator runs etc. The water tank however is not working properly. The zone valve for it is open, but it will not trigger the circulator pump. There are only 2 wires running from the tank , both are connected and not broken. I assume one is for the zone valve and the other the circulator?? Is there a way I can test the control unit on the tank with a multimeter? If this control is bad, are they readily available at home depot etc? Just my luck this happens on a holiday weekend!! My workaround is to turn the heat up in one zone and that will circulate water thru the hot water tank because the zone valve is open....just hate to waste oil like that. Thanks for any input. Ken
 
Sponsored Links
  #2  
Old 09-01-13, 08:33 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 1 Vote on 1 Post
Hi Ken, what it sounds like you are describing may be a bad 'endswitch' in the zone valve for the indirect.

The zone valve for it is open, but it will not trigger the circulator pump. There are only 2 wires running from the tank , both are connected and not broken. I assume one is for the zone valve and the other the circulator??
If the zone valve is open, it probably means that the control on the water heater is doing it's job.

What is the make/model of the zone valves?

Make and model of both the boiler and the indirect?

If they are Honeywell (very common), they are probably the 8043 series. Some have 2 yellow and 2 red wires coming out ( the "E" series ) and some have terminal blocks on the side of the power head (the "F" series).

Still presuming that you have 8043's, the two yellow wires operate the MOTOR in the valve that actually opens the valve. One of these yellow wires should go to one of the wires from the indirect, the other yellow wire should go to a 24VAC transformer. One of the transformer wires should go to the other yellow wire on the valve.

The two RED wires are your 'endswitch'. When the valve is fully open this endswitch CLOSES and signals the boiler to fire and the circulator to run.

I'll continue with multimeter instructions for troubleshooting once you confirm that you do have Honeywell valves. Other valves are similar, but I need to know exactly which ones you have in order to provide proper info.
 
  #3  
Old 09-01-13, 02:49 PM
Member
Thread Starter
Join Date: Sep 2013
Location: usa
Posts: 5
Received 0 Votes on 0 Posts
Thanks so much for the reply. I have Honeywell zone valves with 2 red wires and 2 yellow wires like you describe. I am going to head down now and swap out the guts from one of the heating zone valves with the indirect water heater zone valve, and I'll see if that solves my problem.
 
  #4  
Old 09-01-13, 03:15 PM
Member
Join Date: Oct 2008
Location: USA
Posts: 2,876
Received 5 Votes on 5 Posts
You could just jumper out the end-switch connections and see if the circulator starts and the boiler fires.
 
  #5  
Old 09-01-13, 03:18 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 1 Vote on 1 Post
Hang on a sec...

What do you mean "the guts" ?

You don't want to take the power head apart in anyway. You can swap the entire power head much more easily.

How old are the zone valves? If there are FOUR screws holding the power head to the valve, do NOT remove the power head without draining the system.

If there are TWO screws and two 'locating pins', the valves are the newer variety and the power head can be removed without draining the system.

But, I thought you wanted to do some diagnostic with the meter?

To me, that's much easier.

Make and model of both the boiler and the indirect?
Please answer my other question.
 
  #6  
Old 09-01-13, 03:21 PM
Member
Thread Starter
Join Date: Sep 2013
Location: usa
Posts: 5
Received 0 Votes on 0 Posts
Bingo, Now the indirect water heater is functioning properly. Just need to replace the guts from the heating zone I stole them from. Any idea where can I buy just the motor etc and not the whole zone valve? Thanks again for the help
 
  #7  
Old 09-01-13, 03:27 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 1 Vote on 1 Post
Ken, we need to get our terminology straight.

When you say 'the motor', are you actually talking about the electric motor INSIDE the zone valve power head, or are you calling the entire power head 'box' "the motor" ?

Because you CAN just replace the 'motor', but that is not likely your problem.

This is the power head:


image courtesy pexsupply.com

40003916-026 - Honeywell 40003916-026 - Replacement Head for V8043E Zone Valves

and this is the 'motor', which is inside the power head, but not likely your problem because you said that the valve was opening:


image courtesy pexsupply.com
 
  #8  
Old 09-01-13, 03:34 PM
Member
Thread Starter
Join Date: Sep 2013
Location: usa
Posts: 5
Received 0 Votes on 0 Posts
The meter was only to determine if it was the aquastat on the indirect heater or the zone valve, I wasn't sure how to troubleshoot that. I only have 2 bolts securing the head, so I swapped it with another zone. Sorry "guts" wasn't very descriptive. So now I just need to replace the head unit for a heating zone that I won't need for another month or so. Any suggestions where to buy that?
 
  #9  
Old 09-01-13, 03:39 PM
Member
Thread Starter
Join Date: Sep 2013
Location: usa
Posts: 5
Received 0 Votes on 0 Posts
I followed your link for the replacement head unit.....thanks, I'll buy it from them.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: