Zero flow from one zone.
Old 10-04-13, 01:20 PM
I have a two zone hydronic boiler. I replaced the pump circulator and purged the system of air. One zone had absolutely no flow. I pressurized the system and the boiler gauge reads 15 psi. I tested the zone that had water flow with a pressure gauge and it read the samething. What baffles me is that 2nd floor zone has absolutely no flow coming when I tried to bleed it. Any ideas?
Old 10-04-13, 01:26 PM
lawrosa's Avatar
Super Moderator
Received 19 Votes on 17 Posts
Hi welcome...
Hmm, you need to perform a certain procedure to purge the air out. We need to see your purge stations to help you. Take pics of where you are doing this... Basically you need to close one side of the zone, and or open the zone valve, or flow control.
Possible there was nothing wrong with your circ and a zone valve went bad...
We can help but need a few pics.. Well lit please...
Old 10-04-13, 01:30 PM
NJT's Avatar
NJT
NJT is offline
Received 2 Votes on 2 Posts
Tell us exactly how you performed the purge procedure.
NEVER trust a boiler gauge. Look at top of forum message list for article called "How to Verify a Boiler Gauge".
If you don't have enough pressure in the system you will not get water to the top of the system. 15 PSI is enough for this, but if the gauge is wrong... well... you might not have enough pressure in the system.