Question 1/2" Pex for radiator feeds?

I will be installing a couple of Runtal UF-3 radiators in my house, one 5' and one 6' unit. They will be about 25'-30' from the boiler and manifold, and each will be seperate home run feed and return. They will be fed with 150* water max.

Is there any reason I can't use 1/2" Oxy barrier PEX for the feed and return? The Runtals have 1/2" pipe threads on them. I know 1/2" PEX ID is less than 1/2", but will it still carry enough flow for one radiator? If its borderline suficent, I can use 3/4" PEX, but figured if its only going into a 1/2" fitting, I could use the smaller PEX.

Thanks for any advice
 
Sponsored Links
  #2  
Old 10-14-13, 02:47 PM
Member
Join Date: Oct 2008
Location: USA
Posts: 2,854
Likes Received: 3
To really know the answer, you'd need to consider the Btu/hr you need from those heat emitters, then look at their specs for flow and temperature, and figure the total pressure drop compared to the circulator head. Personally, I would just go with 3/4" pex rather than 1/2". Your maximum 150 deg water doesn't help - why so low?

Just because the connections on the heat emitters are 1/2" doesn't necessarily mean that 1/2" pipe is correct. It's the total pressure drop that governs, not the smallest sized connector.
 
  #3  
Old 10-14-13, 03:04 PM
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 26
The radiators arent needed for their full rating at 180*. They will be mounted under two large picture windows to suppliment the radiant heat on the coldest days. If I was running it at 180* I could get by with radiators half that length. System is running with a mod/con boiler so lower temp with longer radiators gives more than enough heat.
 
  #4  
Old 10-14-13, 03:35 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Likes Received: 1
With copper 1/2", we figure about 15K BTUH is the max load for that size pipe.

Yes, PEX ID is a bit smaller, so figure maybe 10-12K BTUH is the max.

As gilmorrie said, make sure the pump will do the job.
 
  #5  
Old 10-14-13, 06:23 PM
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 26
Thanks guys, the larger one will only be in the area of 4-5K BTU's so even if the PEX can only do 9K, I am still well within the scope of possibilities. And the radiators will only be about 3' above the level of the boiler and a 25' straight shot to each. I dont think there will be too much head or friction for a standard circulator to make the required gpm.

Thanks again
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes